mactec54
Most run a 25A / 30A circuit for their whole machine, other than that they use a 1.5Kw spindle if they don't have an option with a larger power circuit.
The input Power to the VFD Drive should be connected to R Hot T Neutral and Ground to the VFD Drive Ground Terminal, for this VFD Drive if you have a Ground Bus then all your Grounds will connect to this one Point, (Yes it can run like you have it, the correct way for this VFD Drive is R / T for the input Power connection)
If you have noise and can see the effects on your computer, then you have done something wrong with the Grounding or Shield Termination.
So, we need focus on the Grounding, establish a Ground Bus Bar this attaches to the Ground Plane (the metal Plate you have everything mounted on)
Then we have to look at the Shield Termination how have you done this, as this needs to be a direct clamp to the Ground Plane.
The EMI Power Filter needs to be as close as possible to the VFD Drives Input Power, Not all EMI Power Filters are suitable for VFD Drive use this is what I recommend, TDK Lambda
TDK Part # RSEN-2030L
I see the Spindle Cable, you want the Shield to go up to the VFD Drive, so to keep the exposed wired as short as possible, then you can clamp the Shield directly to the Ground Plane, ( Your metal Cabinet,) you can't attach a tail to the Shield, this acts as an antenna if this is what you have done, this needs to be corrected, here are some snips on Shield Grounding / Termination, Both ends have to be Clamped, Ground / Earth wire connection must be separate from a Shield Termination
If you are using the USB for any connections to your machine, you most likely will need a USB Isolator you can find them on Amazon Ebay, you most likely are using an Ethernet connection so this does not apply.
Twist all your wire Pairs wherever you can, using a Tight Twist! No Ground / Earth wires with the Twisted Power wires