I am trying to DNC a large program at 19200 baud rate and the buffer fills. At that point the handshake between machine and computer loses information and a error is the result. I am using a RS232 cable about 20' long. Anybody seen this?
I am trying to DNC a large program at 19200 baud rate and the buffer fills. At that point the handshake between machine and computer loses information and a error is the result. I am using a RS232 cable about 20' long. Anybody seen this?
slow your baud rate down so the machine can stay ahead of the data flow.
mmodeler,
I have a 1996 Feeler FV-800 with Mitsubishi Meldas 520 AM control and have no problem drip feeding at 19 200 Baud with a 20' serial cable between my PC and the front panel. Remember that there is also a 22' internal intermediate cable from the front panel to the control at the back. Total L=42' !
I have the CNC parameters set to Hardware (RTS/CTS) handshake:
PARAMETER 1
#. Parameter input (value)
2. Baud rate: 0 (19200 Baud)
3. Stop Bit: 3 (2 stop bits)
3. Parity Effective: 0 (No Parity bit during I/O)
5. Even Parity: 0 (Odd Parity)
6. Chr Length: 3 (8 data bits) this is a little special with Mitsubishi controls.
7. Terminator Type: 3 (EOR is fixed no matter what you choose)
11. Hand Shake: 1 (RTS/CTS Hardware)
12. DC Code Parity: 0 (No DC code parity)
PARAMETER 2
#. Parameter Input (value)
1. DC2/DC4 Output: 0 (Without DC2, without DC4)
2. CR output: 1 (On)
3. EIA Output: 0 (ISO)
4. Title Feed out: 0 (Off)
5. Feed Chr:0 (0 Characters)
6. Parity V:0 (Off)
7. Time Out:0 (0 seconds)
8. RST Ignore:0 (RST valid)
PC parameters for COM1 serial port
Baud rate: 19200
Data Bits: 7
Parity: Even
Stop Bits: 2
Flow control: Hardware
FIFO buffers in "Advanced" are set to "LOW".
DNC program parameters
Com port: COM1
Baud rate: 19200
Flow control: RTS/CTS
Code system: ISO
Data bits: 7
Parity: Even
Stop bits: 2
Serial cable pinout (20' Belden 8104 shielded low capacitance cable):
PC side 9-pin Dsub female <---> CNC side 25 pin Dsub male
2 RxD <---> 2 TxD
3 TxD <---> 3 RxD
5 Signal Ground <---> 7 Signal Ground
7 RTS <---> 5 CTS
8 CTS <---> 4 RTS
Pins 4 DTR & 6 DSR are jumpered at PC side's 9-pin Dsub female
Pins 6 DSR & 20 DTR are jumpered at CNC side's 25-pin Dsub male
Pin 8 is not used at my CNC side's 25-pin Dsub male, but may need be jumpered to 6 & 20 for your CNC. Please check this.
/ Peter
Are you wired to a com port on the PC or are you using a USB to serial adapter? Hardware handshake?
I'm also wondering if the buffer is loading so much information that the PC thinks the connection was lost after a certain amount of time (waiting for the machine to respond back). Is there a time-out setting on the communication software?
Greg
I am using a com port.
Lines are being lost. the computer does not send the information fast enough I think.
Drop the baud rate to 9600 on both the pc and the haas and see if the trouble continues
Eagle
Also make sure you disable the FIFO on the local comm port. You could also try using RTS/CTS (hardware flow control) if you have a cable that is wired this way. If you need help still, feel free to give us a call. We have lots of experience in connecting this machine and cabling.
Greg Mercurio -Shop Floor Automations
www.shopfloorautomations.com /619-461-4000