DGN parameters Nakamura Tome TMC15M Fanuc OTC PMC-M how to enter PMC parameters?
Good Day.
We are seeking help from those expert and experience user of Fanuc controls. We would like to know how to enter DGN parameters for Nakamura tome TMC15M Fanuc OTC PMC-M. We can't enter those value by hand or via RS232.. Is there any special key combination need to turn on?
Machine History:
*Low battery all parameters has been lost.
Machine Status:
*Mode selector Locked on MDI
*Interlock Key act as Mode selector Switching from MDI - HNDL.
*Hardware Condition: PSM "00" SPM "--" SVM"00"
*Alarms" 310,320 APC alarm need ZRN" no control are responding...
Any help and advice would be really appreciated..
[email protected]
Re: DGN parameters Nakamura Tome TMC15M Fanuc OTC PMC-M how to enter PMC parameters?
I have the GE fanuc error
Which is system alarm 910(ram parity). How it can be removed
Re: DGN parameters Nakamura Tome TMC15M Fanuc OTC PMC-M how to enter PMC parameters?
Quote:
Originally Posted by
Bilal166
I have the GE fanuc error
Which is system alarm 910(ram parity). How it can be removed
Press and hold RESET & DELETE buttons while powering up. All memory will be wiped out and have to be reloaded.