1 Attachment(s)
Re: Spindle Drive Fault (Alarm 2) on CHNC I with Fanuc OT-B control
Rental compressor plus one california compressor still could only provide a continuous pressure of 60psi, but I also waited for the pressure to get to 120psi to turn it on and tried when the pressure at the gauge was 80psi, but same thing. The only alarm I get when the pressure drop very low (under 20psi) is related to the collet switch. So you guys don't think there is something wrong with the motor or drive? Is the pressure gauge in the attached picture supposed to show any pressure? Mine stay at 0 psi no matter what.
Thanks
Re: Spindle Drive Fault (Alarm 2) on CHNC I with Fanuc OT-B control
Never mind about the pressure gauge. It's for the spindle pin lock - bad gauge, but pin still works fine.
Re: Spindle Drive Fault (Alarm 2) on CHNC I with Fanuc OT-B control
check the sensor cable of spindle drive.
Re: Spindle Drive Fault (Alarm 2) on CHNC I with Fanuc OT-B control
Seller replaced drive, but didn't transfer parameters from old drive to new one so when an M03 command is executed, nothing happens. Anyway, after transferring parameters from old drive to new one by swapping chip, it still fault with the same error 1001 spindle drive fault with AL-2 displayed on the drive. Motor and encoder checked out fine. What else could be causing this fault? Would bad parameters in the drive cause this?
Thanks
Re: Spindle Drive Fault (Alarm 2) on CHNC I with Fanuc OT-B control
Final update on this long issue.
We replaced the spindle drive with a known good one and it works fine now. So in short, first drive is bad and so is second one. So now we just need to fix the leaky air issue.
Thank you