3 Attachment(s)
Getting C11/Mach3 to control 2.2kw Spindle
Hi, I have some issues on connecting the C11 BOB to VFD (YP-C please see YP-C PDF INVERTER.doc) and getting the C11/Mach3 control my spindle.
Given the image below I made the following connectios (the symbols in red are the C11 terminals):
Attachment 211520
VFD -> C11 :
S1 -> PIN 1 (NO)
S2 -> PIN 2 (NO)
COM -> VIN2 (PIN1) & VIN1 (PIN16)
FU -> 10V (PIN 14)
COM -> GND (PIN 14)
Also, I attach some screenshots from Mach3 settings (Mach3 Screenshot Settings.zip), as you may understand better my case.
Using a multimeter:
I verified that variable speed control gets 12vdc isolated from a 12v power supply.
I checked that the 0-10vdc analog output does not give any indication or changes according to pot turning.
In Mach3, I tried to "Spindle Toggle" but my spindle does not start.
Any ideas would be bery helpful,
Thanks in advance,
Kostas.
Finally managed to get it working!!!
Hi again, finally I managed to get the spindle turning by C11/Mach3 combination following the steps below:
1) Wiring from VFD to C11 (please see the YP-C document attachment in my 1st post):
VFD -> C11
S1 -> PIN 1 (NO)
S2 -> PIN 2 (NO)
COM -> VIN2 (PIN1) & VIN1 (PIN16)
FU -> 10V (PIN 14)
COM -> GND (PIN 14)
2) Set the YP-C VFD parameteres for controlling it from outside:
P0000 -> 1
P0001 -> 1
3) In Mach3 Port & Pins, I put the following settings:
a) Motor Outputs -> Spindle [step pin:14, dir pin:8, step port:1, dir port:1] (didn't understand the 8 in dir pin but it worked)
b) Output Signals -> Enable Output #1 [port:1, pin:1], Output #2 [port:1, pin:16] and Charge Pump [port:1, pin:17]
c) Spindle Setup -> Relay Control -> Uncheck 'Disable Spindle Relays', M3 Output #1:1, M4 Output #2:2
d) Spindle Setup -> Motor Control -> Check 'Use spindle motor output' and 'Step/Dir Motor'
e) Motor tuning and Setup -> Spindle -> Steps Per:1000, Step Pulse:5, Dir Pulse:1
4) I fine tuned the C11 pot by setting the Step Pulse to 5 and managed to get 10.02V in multimeter, so I started the testing from Mach3 MDI screen.
My testing started by typing in MDI command prompt the following: m3 s12000. I noticed that Mach3 warned me about 'Too fast for puley - Using Max'
and then I noticed that the max spindle speed was set to 8000 in Mach3 main screen. So, I assumed that I had to increase this to 24000 as this is my spindle max RPM. I found a setting under Config -> Spindle Pulleys and I selected the Pulley Number 5 and set it to 24000 instead of its default value (25000). Is this OK to be changed?
So, returning to MDI screen, I typed m3 s24000 and took a voltage measure of 10.02V, then set it to s12000 and got 4.9V (not 5V). Is this OK?
Also, please check the following video and noticed the frequency in VFD's screen. In s24000 I get 400Hz but in s12000 I get ~195Hz. Is this OK?
Also please notice that in s200 (my last test in the video), it actually does not turn but it is considered as 'started' in Mach3 screen.
Getting the Mach3 / C11 control the Chinese 2.2kw Spindle through VFD - YouTube
Thank you very much for your help Bill !!!