1 Attachment(s)
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
nwrepair1
My God Mactec54. Same pics, same wording ,same admonishment, same irritating crap every time. Why do you bother? It's getting old. I am also a retired industrial electrician and can attest that not all machines are EMI compliant. Example would be the ShopSaber SS 23 I bought new last year. No shielded wire except on limits and emergency stops. Control box not UL Listed or approved. Most cnc routers built in US in the 1990s didn't have shielded either. In fact most mfg resisted use of shielded until Europe made it mandatory. Get a life.
The industry is a whole lot more torrent to EMI that a Home Hobby shop
You are obvious just another mouth piece with no substance, you need to add to what I post to help people who are struggling to do this if you can't add help to those that need it then don't criticize those that are helping
Nobody cares if you brought a machine that is not wired to electrical standards, that shows your poor judgment as an electrician
So if you think this wiring is Ok let us know
Re: Chinese 2.2kw spindle burned out?
Wmgeorge suggested using a tester that can read up to 400 hz. The reader we used to measure the 150v didn’t have a frequency reading option. Does that invalidate the reading, or does that tell me that the VFD is compromised for sure?
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
justCNCit
Wmgeorge suggested using a tester that can read up to 400 hz. The reader we used to measure the 150v didn’t have a frequency reading option. Does that invalidate the reading, or does that tell me that the VFD is compromised for sure?
You where only reading Voltage, but you must read from Phase to Phase not Phase to Ground, at the worst the meter will not read the correct reading, his meter only needs to have a low pass filter and he will be fine
If he has Dc voltage up to 400v then he can check the DC Bus Voltage which will give me a good idea of what is going on
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
justCNCit
Wmgeorge suggested using a tester that can read up to 400 hz. The reader we used to measure the 150v didn’t have a frequency reading option. Does that invalidate the reading, or does that tell me that the VFD is compromised for sure?
If the wire from the VFD to the motor is long, it can cause high voltage reflections in the VFD and motor. it can burn through the insulation of the motor and maybe burn out the VFD output devices. You can insert some reactors in between them to knock down some of the high voltage. VFD rated motors can handle higher voltages than single frequency motors. setting the chopping frequency too high will make the motor quieter but run hotter. I use the default chopping frequency, its noisy but cooler. Does your vacuum cause airflow problems for the motor cooling?
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
mactec54
You where only reading Voltage, but you must read from Phase to Phase not Phase to Ground, at the worst the meter will not read the correct reading, his meter only needs to have a low pass filter and he will be fine
If he has Dc voltage up to 400v then he can check the DC Bus Voltage which will give me a good idea of what is going on
When you measure the voltage, measure phase-to-phase (U to V, U to W, V to W), not phase to ground. Any voltmeter will do. For measuring the phase currents, the meter needs to be able to be able to handle the applicable frequency range (because the current pick-up is inductive).
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
Gerry_H
When you measure the voltage, measure phase-to-phase (U to V, U to W, V to W), not phase to ground. Any voltmeter will do. For measuring the phase currents, the meter needs to be able to be able to handle the applicable frequency range (because the current pick-up is inductive).
No not any meter, it will not measure with any accuracy the VFD Drive PWM output most of these VFD Drive installs, we are talking about are running at 400Hz to have full voltage not a regular 50Hz / 60hz so a regular 50Hz / 60Hz meter is not going to work with any accuracy, if work at all, that is why they make meters like Fluke that can measure a VFD Drive output, the meter needs to have a low pass filter to be able to read the VFD Drive output with any accuracy and normally if you are doing this on as a job, you want a good meter that can do the Dc Bus
Re: Chinese 2.2kw spindle burned out?
My 2 pennoth worth if applicable...…….to test it, could you wire the apparent faulty VFD in question to a common 50/60 Hz 3 phase motor and see if it will run and speed up and down?…..just asking.
BTW.....Mac does have an enormous capacity of patience...…...I don't think many on here have be so helpful with VFD's like he has been.
Ian.
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
handlewanker
My 2 pennoth worth if applicable...…….to test it, could you wire the apparent faulty VFD in question to a common 50/60 Hz 3 phase motor and see if it will run and speed up and down?…..just asking.
BTW.....Mac does have an enormous capacity of patience...…...I don't think many on here have be so helpful with VFD's like he has been.
Ian.
Here is a good explanation what is happening and why a regular meter has trouble reading the output, they are just not designed for these kind of measurements, meters that have a low pass filter can do quite a good job, there are some cheap Chinese meters that can do it all, so you don't have to have an expensive meter like a Fluke to do the job
VFD PWM Waveform
Re: Chinese 2.2kw spindle burned out?
In that link it states that an analogue meter can read the VFD voltage because it doesn't move quick enough to dip when the voltage goes low during the ramp up to full voltage etc, so for the test all you need is to measure the voltage across 2 of the wires with an oldie needle type meter and you're good to go if you get a reading......as I see it.
Question 1..…...does this apply to all VFD's like the ones sold on EBAY, Bangood, Amazon etc.
Question 2…….is it OK to run a VFD straight out of the box with the settings they come with if you don't require any exotic settings for special purposes etc?
Ian.
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
handlewanker
In that link it states that an analogue meter can read the VFD voltage because it doesn't move quick enough to dip when the voltage goes low during the ramp up to full voltage etc, so for the test all you need is to measure the voltage across 2 of the wires with an oldie needle type meter and you're good to go if you get a reading......as I see it.
Question 1..…...does this apply to all VFD's like the ones sold on EBAY, Bangood, Amazon etc.
Question 2…….is it OK to run a VFD straight out of the box with the settings they come with if you don't require any exotic settings for special purposes etc?
Ian.
I would not count on a analogue meter as it would not be an accurate reading either
Yes all VFD Drives, there are some that have a different number of output stages but you would not be buying any of those Drives because of cost
Yes you can run a VFD Drive straight out of the box with no motor wired to it most come configured for either 50Hz or 60Hz , also if you had a regular 3Ph 50Hz Ac motor of the right size you could wire it to the VFD's output U V W and Ground and run it also
I should of worded some of my posts better as to the use of a meter, the meter it's self will not damage the VFD Drive it is the user using the meter that can damage the IGBT's of these cheap VFD Drives
Re: Chinese 2.2kw spindle burned out?
Tank you..…...just bought one of "those" drives to go with a Deckel D bit grinder that I sold on Gumtree to make it more saleable for running on single phase......2.2Kw 3Hp etc, A$80 on Amazon.
There's a brilliant video by Clough42 in 2 parts on UTUBE on wiring up and setting all the parameters, and why you would want to, for a Westinghouse VFD, but I suppose it applies to practically all FVD's.....really makes sense of the handbook after it's explained in infinite detail.
The ability to house the VFD in a separate enclosure and have the controls on the machine of choice is quite handy.
One thing he did show and that is how/where to wire in a separate computer fan for when the motor is running slow....there's so much concise information in that video, especially for someone like myself who wants to just use one without the huge read-up and finger crossing exercise before switch on.
Ian.
Re: Chinese 2.2kw spindle burned out?
Quote:
Originally Posted by
handlewanker
Tank you..…...just bought one of "those" drives to go with a Deckel D bit grinder that I sold on Gumtree to make it more saleable for running on single phase......2.2Kw 3Hp etc, A$80 on Amazon.
There's a brilliant video by Clough42 in 2 parts on UTUBE on wiring up and setting all the parameters, and why you would want to, for a Westinghouse VFD, but I suppose it applies to practically all FVD's.....really makes sense of the handbook after it's explained in infinite detail.
The ability to house the VFD in a separate enclosure and have the controls on the machine of choice is quite handy.
One thing he did show and that is how/where to wire in a separate computer fan for when the motor is running slow....there's so much concise information in that video, especially for someone like myself who wants to just use one without the huge read-up and finger crossing exercise before switch on.
Ian.
Did the D bit Grinder have a 3 Ph motor on it, you can only use a VFD Drive with a 3Ph motor
No all VFD Drives are different to wire and Program the principle is the same
If you see something on YouTube you have to be careful as most of the posters are the same as you with no real experience in setting up a VFD Drive, so what you think is really good can be very wrong also