OIL LUBE ALARM LOW PRESSURE
Hi all,
We have a VX500 with an Fanuc OI control.
we overfilled the lube tank and now we have been
getting a low oil pressure alarm ( even after draining, cleaning and re-filling)
Need to cycle the pump but I don't know how to do it.
Currently set at 15 min. Where do I change that? Cant find a relay or button
to activate the pump.
Manuals are useless.
Any help would be appreciated.
thanks
Jim
Re: OIL LUBE ALARM LOW PRESSURE
If you can post your ladder we can take a look and see which timer is used for the lube cycle
Re: OIL LUBE ALARM LOW PRESSURE
Your timer T000 should be the lube pause (300000) and the T002 should be the ON time (20000) In your Ladder it should be R726.3 and R726.2 respectively.
Please verify on your machine since the documentation I have is not for your model.
Best regards,
.
Re: OIL LUBE ALARM LOW PRESSURE
i think below is correct as it was changed later to T02, but difficult to tell without knowing Serial nr.
timer no.011 timer T020 R726.2 LUBRICATION ON TIME 20000
also you can try to hold standby switch, which should also turn on the lub pump.