VFD setup for H.S.D 6.8kw spindle
I have aquired a few of these spindles and I would like to hook one of these up to my own CNC.
In order to do this I need a VFD for this, and I have got 2 different ones to try out.
I have a Control techniques Unidrive UNI2402 and a Hitachi WJ200-150HFE drive to play with.
I'm trying to test it out on the bench, with a speed potmeter attached, to the Hitachi drive, and it keeps going into overload.
I have set these paramters for now
A001 - 00
A002 - 2
A003 - 50Hz
A004 - 400Hz
A044 - 1
A082 - 380v
B012 - 16A
H003 - 7,5kw (goes in speciel increments so 7,5kw was the closest)
H004 - 2 poles
Am I missing something??
The Unidrive VFD was the one that was placd on the Biesse machine the spindles came of, I cannot get into controlling the speed manually with a Speedpot..
I have tried most anything already, and I'm looking for some serious help now.
So if anyone is really good at the one or the other, then please help me out. :)
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
IN-WondeR
I have aquired a few of these spindles and I would like to hook one of these up to my own CNC.
In order to do this I need a VFD for this, and I have got 2 different ones to try out.
I have a Control techniques Unidrive UNI2402 and a Hitachi WJ200-150HFE drive to play with.
I'm trying to test it out on the bench, with a speed potmeter attached, to the Hitachi drive, and it keeps going into overload.
I have set these paramters for now
A001 - 00
A002 - 2
A003 - 50Hz
A004 - 400Hz
A044 - 1
A082 - 380v
B012 - 16A
H003 - 7,5kw (goes in speciel increments so 7,5kw was the closest)
H004 - 2 poles
Am I missing something??
The Unidrive VFD was the one that was placd on the Biesse machine the spindles came of, I cannot get into controlling the speed manually with a Speedpot..
I have tried most anything already, and I'm looking for some serious help now.
So if anyone is really good at the one or the other, then please help me out. :)
There would be nothing about your spindle that would be using 50Hz so you have something incorrect with that parameter, what are your motor spec's??
A003=400Hz at 50Hz you have a good chance of damaging your spindle
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
mactec54
There would be nothing about your spindle that would be using 50Hz so you have something incorrect with that parameter, what are your motor spec's??
A003=400Hz at 50Hz you have a good chance of damaging your spindle
A003 is the base frequency of the spindle, as I'm in the EU we run a 50 cycle electricity grid
Motor specs is as follow
Voltage: 380v
Amp: 16A
RPM @ 200Hz is 12000
Max RPM @ 400Hz is 24000
cos: 0,8
2 pole motor, 3 phase
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
IN-WondeR
A003 is the base frequency of the spindle, as I'm in the EU we run a 50 cycle electricity grid
Motor specs is as follow
Voltage: 380v
Amp: 16A
RPM @ 200Hz is 12000
Max RPM @ 400Hz is 24000
cos: 0,8
2 pole motor, 3 phase
The base frequency of the spindle is 400Hz look at your spindle spec's you just posted, it has nothing to do with 50Hz electrical grid , unless you are running a 50Hz Ac 3 phase motor and you are not
You need these ( 2 ) set as well
A061=400
A062=200
Re: VFD setup for H.S.D 6.8kw spindle
Good god man, you are a genious... It never occured to me to run the basefrequency as 400..
But why would I want to set lower to 200Hz??
Not it trips the Over Voltage on Decelleration... So I need to play with things, but now the spindle spins up..
Re: VFD setup for H.S.D 6.8kw spindle
Typically you have to decelerate slower unless you have external braking resistors. Some drives have bigger internal resistors than others for a given HP, not sure about yours
Sent from my iPhone using Tapatalk Pro
Re: VFD setup for H.S.D 6.8kw spindle
I haven’t mounted a braking resistor yet. I have it on the shelf. Right now it was just a test to get the spindle running. So right now I’m one step closer at getting ATC on my machine.
Re: VFD setup for H.S.D 6.8kw spindle
Braking resistor mounted. Now it can stop in 2 secs flat. :)
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
IN-WondeR
Good god man, you are a genious... It never occured to me to run the basefrequency as 400..
But why would I want to set lower to 200Hz??
Not it trips the Over Voltage on Decelleration... So I need to play with things, but now the spindle spins up..
Just going off what you posted, you posted 200Hz in the spec's, if it is air cooled then this is normal, you can try lower but watch for over heating, all these Spindles have a minimum speed they can safely run at
Trips on Deceleration because you have not set the deceleration time correct
Large spindles you need a Braking Resistor if you want to stop fast, if not you would have to adjust the Deceleration Time
F003=10 By default you would have to make this number larger, without a Braking resistor
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
mactec54
Just going off what you posted, you posted 200Hz in the spec's, if it is air cooled then this is normal, you can try lower but watch for over heating, all these Spindles have a minimum speed they can safely run at
Trips on Deceleration because you have not set the deceleration time correct
Large spindles you need a Braking Resistor if you want to stop fast, if not you would have to adjust the Deceleration Time
F003=10 By default you would have to make this number larger, without a Braking resistor
Even without the braking resistor I could stop it with F003 set at 10.
And yes the spindle is aircooled, but it's an electric fan, so it will not be dependant on the rotation of the spindle.
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
IN-WondeR
Even without the braking resistor I could stop it with F003 set at 10. And yes the spindle is air cooled, but it's an electric fan, so it will not be dependent on the rotation of the spindle.
So what was your problem then on Deceleration, you posted this, Not it trips the Over Voltage on Deceleration... So I need to play with things, but now the spindle spins up..
6000 RPM is most likely your limit, use what the manufacture recommends for the minimum speed, you have the spindle motor spec's
If you post the model number I will give you what the minimum speed is, it has nothing to do with the fan unless you know better than the manufacture of your spindle motor
There spindles have a minimum speed regardless of the fan, some are 12,000 RPM some are 6,000 RPM this depends on what model spindle you have
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
mactec54
So what was your problem then on Deceleration, you posted this, Not it trips the Over Voltage on Deceleration... So I need to play with things, but now the spindle spins up..
6000 RPM is most likely your limit, use what the manufacture recommends for the minimum speed, you have the spindle motor spec's
If you post the model number I will give you what the minimum speed is, it has nothing to do with the fan unless you know better than the manufacture of your spindle motor
There spindles have a minimum speed regardless of the fan, some are 12,000 RPM some are 6,000 RPM this depends on what model spindle you have
The problem was that I have decel set at 6 second, that tripped it.
I only have the specs on the motor,. not the exact modelnumber, as it's not imprinted on the spindle itself. They are marked Biesse iso30 but that's a wide variety. :) So you see it's difficult for me to find a spec sheet with minimum speed since I do not have the full modelnumber. :)
Re: VFD setup for H.S.D 6.8kw spindle
Quote:
Originally Posted by
IN-WondeR
The problem was that I have decel set at 6 second, that tripped it.
I only have the specs on the motor,. not the exact modelnumber, as it's not imprinted on the spindle itself. They are marked Biesse iso30 but that's a wide variety. :) So you see it's difficult for me to find a spec sheet with minimum speed since I do not have the full modelnumber. :)
Post a photo then I may be able to match it up from that, they have many models, 6000 RPM should be safe, just watch for over heating when you are using it that would be
A062=100