I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
It is rated for 24,000 rpm. I cannot achieve more 7,999 rpm any suggestions?
Any Help is appreciated
When running HZ registers 133.33 It is set to 400 hz 1.7 Amps
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mpresti8
It is rated for 24,000 rpm. I cannot achieve more 7,999 rpm any suggestions?
Any Help is appreciated
When running HZ registers 133.33 It is set to 400 hz 1.7 Amps
1.7Ax3=5.1A at the spindle 8.8A at the supply.
You did not say what spindle you have; it sounds like your Parameters are not set correctly.
How many Amps is your AC supply??
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
20 Amp circut
This unit was running at Max revolution until this happened
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
I have the GDZ-80-1.5B 24000 rpm 1.5 KW 110V 400Hz 5ASpindle water cooled
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mpresti8
20 Amp circut
This unit was running at Max revolution until this happened
Until what happened, did it overload or stall, is this being used from the KeyPad or by remote 0-10v??
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Run by the keypad on the front of the inverter no problems other than I wanted to slow it down because I believe it was running too fast for the surfacing blade i had on it. I was checking settings and the VI VR pin that you move the jumper on to change from the keypad operation to the Mach 3 software operation That is when i could not get it to work properly at this time it is shorted across the VR pins
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Did you check if this Parameter PD144: Max Motor RPM is set to 3000
https://www.automationtechnologiesin...5-110vac-input
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
let me check that real fast
PD144 = 3000
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
automationtechinc
PD144 is set to 3000
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mpresti8
let me check that real fast
PD144 = 3000
This Parameter PD144 is related to the Max RPM only.
This is the Parameters you need for KeyPad / Pot use.
Pot Control
PD001=0
PD002=1
PD070=1
JI Jumper 2-3=VI Position. You can try either position as some of these drives can be either for Pot use, these Parameters are important as well to make it run also for Pot control
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mactec54
This Parameter PD144 is related to the Max RPM only.
This is the Parameters you need for KeyPad / Pot use.
Pot Control
PD001=0
PD002=1
PD070=1
JI Jumper 2-3=VI Position. You can try either position as some of these drives can be either for Pot use, these Parameters are important as well to make it run also for Pot control
Those settings are correct still no luck
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mpresti8
Those settings are correct still no luck
Check the Jumper is not damaged.
What are the Parameters you have set in the Drive
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mactec54
Check the Jumper is not damaged.
What are the Parameters you have set in the Drive
Curent settings are as follows
https://en.industryarena.com/forum/i...AASUVORK5CYII=
PD001=0
PD002=0
PD003=400
PD005=400
PD004=400
PD007=.0.50
PD009=15
PD010=8
PD011=133.33
PD013=8 FACTORY RESET
PD014=10
PD015=10
PD025=1
PD027=0.80
PD141=110
PD142=5
PD143=2
PD144=3000
Jumper is fine
https://en.industryarena.com/forum/i...AASUVORK5CYII=
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mpresti8
PD002=1 this needs to be 1 not 0
PD070=1 also for the Pot to work
PD007=20
PD025=0 Default
PD027=10 this is normally left at the default, if you want to use it than it should be set at the max of 10
You also may need these 2 Parameters set also
PD072=400
PD073=133 Your Minimum Speed
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mactec54
PD002=1 this needs to be 1 not 0
PD070=1 also for the Pot to work
PD007=20
PD025=0 Default
PD027=10 this is normally left at the default, if you want to use it than it should be set at the max of 10
You also may need these 2 Parameters set also
PD072=400
PD073=133 Your Minimum Speed
i made those inputs and still max rpm is7999 I think this thing is haunted
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mpresti8
i made those inputs and still max rpm is7999 I think this thing is haunted
There is another Parameter that is not set correct then, as that is sitting at your minimum speed setting, is there any others that you may have changed.
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mactec54
There is another Parameter that is not set correct then, as that is sitting at your minimum speed setting, is there any others that you may have changed.
Are you trying to run from the KeyPad or from Mach3 if from Mach3 then you need a 0-10v Analog output from the Breakout Board, for this to work, if still only working from the KeyPad do the Arrow keys up /down change the speed.
What Breakout Board are you using.
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
I am running from the VFD not the computer or Mach 3
Honestly this thing is driving me nuts.. One thing that I have seen on these YouTube videos is that when they change a value and press set the screen displays END mine does not display that
Re: I have a huanyang hy02d211b VFD . 110 VAC water cooled spindle
Quote:
Originally Posted by
mpresti8
I am running from the VFD not the computer or Mach 3
Honestly this thing is driving me nuts.. One thing that I have seen on these YouTube videos is that when they change a value and press set the screen displays END mine does not display that
Give me a call, I will help you to check to find the problem
The phone number is on our website:
https://www.automationtechnologiesin...ucts-page/vfds