Good afternoon,
Recently, we acquired a second hand Gildemeister TWIN 65 machine from France. We had DMG check the machine out on site in France and their report came back all good.
Unfortunately, no-one at our firm has any idea how to get this thing to play, and neither do any of the engineers we have had to look at it.
We can get it switched on and referenced but the alarms ask for the turrets to be positioned, which i cant do.
The system is Siemens SINUMERIC 840c.
I have asked Gildemeister uk for help but they have told me that nobody in the uk has any knowledge on this machine!
Can anyone suggest anybody, or anywhere i can get a good manual or even just how to reference turrets?
Thanks in advance.
Re: Help with Gildemeister/siemens
hi i have the same problem with turret in lathe dmg twin sinumerik 840c
error tool holder position unknown and clamp position not defined
do you ripear this PLEASE HELP
do you have procedure
4 Attachment(s)
Re: Help with Gildemeister/siemens
Hi Guys,
let's see if I can help.
All I can tell you is how we reference our turret on our CTX310 lathe with Sinumerik Guildermeister 840 controller.
I've also found the Siemens manuals to be rather crap. If my boss had not shown me the way around the controller, I'd have had a hard time using only the Siemens books.
Anyway, referencing turret:
1). Go to TSM window.
2). Press the Turret button (panel button, NOT a soft screen button).
3). A new window should pop up.
4). On this window you should see a Reference Turret (i.e. on the screen itself, a "soft" button). Press the "real" physical button next to it.
5). Turret should start referencing, and a message will be displayed at the top of the screen, indicating the turret is in the process of referencing. Wait for this message to disappear then hopefully your turret is referenced.
I've attached images showing the TSM screen, Turret button, and screen Reference Turret button.
Attachment 388996
TSM window.
Attachment 388998
Turret button.
Attachment 388994
Sorry about this Reference Turret button sketch, it's all I have with me, but you should recognise it easy enough on the screen.
wojtekthx,
every time I turn on our lathe, I have to press the chuck open pedal until the chuck icon on the screen turns yellow. After that I press reset then it's ready.
Something else I have to do regularly is calibrate the chuck clamping. Our hydraulic chuck has a short range of movement from open to closed. First thing I do is position the jaws roughly in the middle of their range of motion, then I adjust the bolt on jaw position to suit the part diameter. Unfortunately I don't have a photo of the chuck calibration window but I'll try and explain the procedure to calibrate the chuck:
1). Go to TSM window.
2). Press chuck button and the chuck calibration window should pop up.
3). There should be a "soft" screen button (New File I think) showing a yellow folder - press it.
4). Open chuck jaws FULLY - press the TEACH IN UNCLAMPED soft button on the screen.
5). Close the chuck jaws FULLY with NO PART in the chuck - press the TEACH IN WITHOUT PART soft button on the screen.
6). Open the jaws and put your part in then close the jaws on the part - press the TEACH IN WITH PART soft button on the screen.
7). Press the CLEAR button on the panel (the real button with 2 slanting parallel lines).
8). Press the SAVE soft button on the screen.
9). Now press the chuck close foot pedal, and on the screen you should see the ACTUAL VALUE number turn green.
10). Go back to the TSM window and your chuck icon should now be green (clamped on part).
Attachment 389000
Chuck button.
Hope that helps,
Keith
Re: Help with Gildemeister/siemens
I’ve been having a similar issue I wonder if you can help I keep getting this alarm 701505 check shuttle data. I’ve tried all sorts still no joy
the machine is a CTX gamma 3000 TC