COLCHESTER TORNADO 80 alarm 1007
Hello!
We have COLCHESTER TORNADO 80 with GE-FANUC 21-t
At each attempt to rotate the spindle gives an alarm 1007 monitoring hardware fault.
We read about the recovery procedure, but we do not have such a supplementary board.
We will be grateful if anyone can help.
Thanks!
Re: COLCHESTER TORNADO 80 alarm 1007
Hi, If your tornado is equipped in SSM Board, you need to use procedure as bellow
If, with the link, LK2, in the right hand position, +5A, the push button on the SSM is held down while the main isolator is switched on as described above to delete the Alarm History, but then is
held longer, the SSM display cycles around the available maximum spindle speed settings
When the required maximum speed is displayed releasing the push button writes this value to the SSM memory.
The main isolator must now be switched off and the link restored to its normal position
Good Luck:)
In case SSM failure I can offer to repair it.
Re: COLCHESTER TORNADO 80 alarm 1007
Quote:
Originally Posted by
AndyM23
Hi, If your tornado is equipped in SSM Board, you need to use procedure as bellow
If, with the link, LK2, in the right hand position, +5A, the push button on the SSM is held down while the main isolator is switched on as described above to delete the Alarm History, but then is
held longer, the SSM display cycles around the available maximum spindle speed settings
When the required maximum speed is displayed releasing the push button writes this value to the SSM memory.
The main isolator must now be switched off and the link restored to its normal position
Good Luck:)
In case SSM failure I can offer to repair it.
Can you please specify what is the main isolator?
I am facing a problem with my tornado 110 with fanuc 21i-t but whenever the machine boots it gives an emergency stop alarm and then 1001 spindle speed monitoring -no response
1 Attachment(s)
Re: COLCHESTER TORNADO 80 alarm 1007
A photo for the error ladder
Re: COLCHESTER TORNADO 80 alarm 1007
Board is located either to the left of main A3 board or alternatively on right hand side panel
Private message me your email and I will send you procedure
Re: COLCHESTER TORNADO 80 alarm 1007
Hello,
@AndyM23. You mentioned that you can repair SSM, It seems i have faulty SSM on my colchester tornado 110 but i am not sure. Would you be able to check it out or give me some ideas what to try?
Best regards