Re: NEED HELP! Fanuc O-TF
FANUC parameters will not control the buttons on the operator panel. Those will be control by PMC parameters or Diagnostics. These will not be in any FANUC manual.
Re: NEED HELP! Fanuc O-TF
Thanks I contacted the machine builder and they supplied me with a list of PMC parameters. However I can't find where to put them in on the controller?? Does anyone have the procedures for this? I have never had to replace parameters in a machine before and I'm lost as to where these ones go. I have paged through my parameters both in the parameters page and the diagnostic page and can't find anything that looks like the list I have.
Re: NEED HELP! Fanuc O-TF
What does your list look like? Most PMC parameters start in the DGNOS at 300.
Re: NEED HELP! Fanuc O-TF
The list they sent starts at N10300 and goes to N10399. I'm assuming they represent numbers 300-399. But in the control lines 310 and 311 are only 1 digit. The list has a normal 8 digit number for the bits. I can input the number in 310 and it enters leaving the preceding zeros out. (00101100 enters as 101100)However when I try to input 311 (00000001) nothing happens. It won't input the number whether I put it in as a 1 digit number or an 8 digit number.
Re: NEED HELP! Fanuc O-TF
So I can't input these by hand? All I have is a paper printout the company sent me.
Re: NEED HELP! Fanuc O-TF
You can input by hand. But you need to convert binary to decimal.
Re: NEED HELP! Fanuc O-TF
You need to change parameter 19 bit 7 1xxxxxxx (x = don't care). This bit select binary/decimal
1 In the diagnosis display, the timer counter
data is displayed in decimal.
0 The diagnosis display is displayed in
binary as usual.