fanuc ot-a pmc parameters wont enter
I am sure i am missing something here.
i need to put in my pmc data parm. in the machine and it just wont do it. is there a parm you need to turn on 1st?
i can enter all the other parms just pmc data ones arent inputting.
tried the eob trick e stop trick, pretty much everything i read that may work.
i am guessing there is a parameter i need to activate before i can succesfully input them?
yes write protect is off and the pwe is enabled. also tried MDI and edit
manual says call up number
have in mdi
type in data
press input.
nothing happens. these are my 310-350 pmc parameters, i do not have any 900's mine stops at 828
Thank you
Delw
Re: fanuc ot-a pmc parameters wont enter
Use your PMC parameter backup file that you get from punching out, edit the values that need to be edited there, then load it back. Procedure should be:
To backup PMC parameters:
Step 2: Save the PMC Parameters:
These are also sometimes unofficially referred to as
Re: fanuc ot-a pmc parameters wont enter
Sorry I should have put this in. I need to do it manually
Machine just hit the floor, we have no disks
I have all the paperwork on parms and pmc parms etc etc all the other parms I put in, just having a problem with the pmc's aka diagnostic ones
entering them manually only takes a few mins.
Re: fanuc ot-a pmc parameters wont enter
I see. Well probably you could work your way around it by making a PMC parameters text file yourself that would be in the format:
Quote:
&HE:%
N10300 P 00000110
N10301 P .....
....
N10499 P .... OR N10549 P ..... (depends on the 0 control, you should be able to tell which is your last one from your paper printed backup)
%
%
You would just input your values that you have on printed paper in this file and then just load it back normally.
Cheers.
Re: fanuc ot-a pmc parameters wont enter
Got it figured out, talked to fanuc this morning and they helped me through the whole thing( guy was pretty cool)
what happened my parm list has 2 blocks of 900 numbers one shows then has a x on them the other block shows and has a OK on them so I went with the set that said OK
turns out it wasn't ok so to speak that's what prevented me from editing my diag parameters. Thanks for your help.
1 Attachment(s)
Re: fanuc ot-a pmc parameters wont enter
The 900's are the machine options.
The ones they charge a fee to turn on to a 1!
Al.
Re: fanuc ot-a pmc parameters wont enter
Al
thanks for that file
The 900 parm needed to be installed to turn on menus so we could actually insert the diag parms.
once we did that we had a few kinks, got pretty much everything working except one weird issue that I will post in another thread.
Re: fanuc ot-a pmc parameters wont enter
I got the same proplem. I can in put parameter but can not input diagnostic. Can you show me how to input diagnostic, please. Thanks!
Quote:
Originally Posted by
Delw
Sorry I should have put this in. I need to do it manually
Machine just hit the floor, we have no disks
I have all the paperwork on parms and pmc parms etc etc all the other parms I put in, just having a problem with the pmc's aka diagnostic ones
entering them manually only takes a few mins.
Re: fanuc ot-a pmc parameters wont enter
Quote:
Originally Posted by
Delw
Got it figured out, talked to fanuc this morning and they helped me through the whole thing( guy was pretty cool)
what happened my parm list has 2 blocks of 900 numbers one shows then has a x on them the other block shows and has a OK on them so I went with the set that said OK
turns out it wasn't ok so to speak that's what prevented me from editing my diag parameters. Thanks for your help.
Dear DELW
Pl. Help I am Facing same Problem What is the Parameters to enable.
Re: fanuc ot-a pmc parameters wont enter
Quote:
Originally Posted by
Pak_Pa_Fee
I got the same proplem. I can in put parameter but can not input diagnostic. Can you show me how to input diagnostic, please. Thanks!
Hello Sir,
could you inform, how to input diagnostic?