Hi guys,
Need a lil help understanding the mesa card.. specifically the "D" card my confusion is in the 24 volt portion ... one provides 24 volts for all the ancillary options and one provides the ground ?
maybe it was just the way it was explained to me
thanks in advance
Joe
-
Re: Mesa Card Help
Which mesa card do you have?
-
Re: Mesa Card Help
i have not purchased it yet but im looking at one of the plug and go kits possibly the 7I76-5I25 PLUG-N-GO KIT
-
Re: Mesa Card Help
im looking to outfit 2 bridgeport machines 4 axis maybe 5 with auto oiler fog buster coolant maybe spindle speed control via vfd
and a lathe 2 axis with vfd spindle speed control and fog buster coolant control
-
Re: Mesa Card Help
If you are asking about the 7I76/7I76 D difference, the only difference is that the 7I76 has sourcing field I/O outputs and the 7I76D has sinking outputs
That is the 16 7I76 field outputs source +12 or +24V to the load (so the load common is power supply common):
7I76 output --> relay coil --> common (or ground)
The 16 7I76D field outputs are sinking so load common is +12 or +24V:
+24V --> relay coil --> 7I76D output
-
Re: Mesa Card Help
thanks, yes that is what im confused about.. so the 7i76 outputs 12 or 24 volts to the relay and thats what triggers the relay to make the connection from the 12 or 24 volt main powersupply to the peripheral ?
-
Re: Mesa Card Help
Yes, if you think of the 7I76/7I76D outputs as switches, the 7I76 has a common +12/+24V for all 16 "switches" and the 7I76D has a common negative (ground) for all switches
-
Re: Mesa Card Help
thank you for that information !