  1. Re: Need tech help interfacing 6047 amps to 0MA control

    Check Parameter 37 bits 0-3 0=1st axis, etc. This tells the machine if there is a separate pulse coder that detects movement. WARNING: Disconnecting this may cause the axis to not move as expected....
  2. Re: Kel-Vista UR 175/1000 - "INV. LOW VOLT DC LINK"

    If this happens at power on, it could be the unit with the "5" on the LED.(That unit is a servo amplifier.) Could be an issue with the servo amplifier of the power supply module next to it.
  3. Replies
    2
    Views
    1,298

    Re: FANUC SERIES O-T not ready

    F148.6 "SA" is the servo ready bit from the control to the PMC. Your servo's are not ready. The machine could be in Emergency Stop, or an axis could be on a hard limit switch, or there could be a...
  4. Re: Fanuc servo drive mystery battery location

    Have you recently had service on the machine? or did it lose memory? If the machine is older (90's) it might not have batteries. Compare parameter 1815. If bit 5 is OFF on the good machine, then you...
  5. Replies
    9
    Views
    2,563

    Re: Tsugami with a fanuc LH1 control

    the software operators panel is under the OFFSET/SETTING screen. Hit right arrow, should be labeled OPR.
  6. Replies
    9
    Views
    2,563

    Re: Tsugami with a fanuc LH1 control

    FANUC LH1 is not a valid control type. what year what the machine/control made?
  7. Re: Fanuc 15M limiting number of files in directory

    it is an option parameter. if you have the original data sheets or parameter list, it can be reinstalled by FANUC. you can most likely find the option bit by searching online. No one will post it on...
  8. Thread: need help

    by STLMachinist
    Replies
    2
    Views
    791

    Re: need help

    Check your servos. Your 3rd axis servo has multiple alarms. Overload(overheat), Low Voltage, High Current. Most likely the servo PCB on that drive is damaged.
  9. Replies
    4
    Views
    3,887

    Re: 1000 sequence alarm

    A bits are alarm bits on PMC side. If any are on, then trace in ladder to find why it is on. Or consult MTB. I believe alarms in the 1000 range are MTB alarms, not FANUC alarms.
  10. Replies
    6
    Views
    2,496

    Re: NC AUTOMATIC MODE BLOCKED

    stupid question: are all doors closed properly?
    How about G8.0=1? This is interlock signal. Trace in ladder and find cause if it's a 0.
  11. Replies
    4
    Views
    3,887

    Re: 1000 sequence alarm

    Check A bits in status in PMC. Trace in ladder.
  12. Replies
    6
    Views
    2,496

    Re: NC AUTOMATIC MODE BLOCKED

    Check FEEDHOLD.G8.5. It should be a 1. IF G8.5=0, check ladder to find out why
  13. Re: 96 Harrison Alpha 400 Spindle Fault detected!!!

    Flashing 9 on spindle? What kind of spindle amplifier is it? (Alpha, Analog, Digital) Which FANUC control is on the machine?
  14. Re: Alarm 414 Servo Alarm : Y axis detect error

    That normally indicates a bad servo module on the main PCB.
  15. Re: fanuc 31i b alarm sv0417 ill dig servo parameters x, y, z

    Parameter 1815 bit 1 tells the control your axes have scales. That needs to be on for the axes with scales, or the control will not move properly.
  16. Replies
    6
    Views
    3,154

    Re: 915 SRAM PARITY - SISTEM ALARM

    That's not a configuration issue. That's a corrupt memory issue. While swapping, your good control's memory has been corrupted. Most likely by being disconnected from the battery for extended period....
  17. Replies
    2
    Views
    948

    Re: no graphics fanuc 0t

    either display hardware issue.. or corrupt memory. If you have parameters backed up, you can try to clear memory to see if the screen fixes itself.
  18. Replies
    9
    Views
    12,179

    Re: Fanuc battery

    The encoders are the APC... 6Vdc? Unless each drive had a battery, these are most likely on the door.
  19. Replies
    2
    Views
    1,345

    Re: amada pega 344 fanuc w 6m control

    C31= X axis (X)
    C34 = Y axis (Y/Z)
    C37= T axis (Z/P

    The 4 cable wires are the motor power. Should connect to 5,6,7,8 on the drives there. I imagine X to X, Y to Y, the other to T. 5=Red,...
  20. Replies
    2
    Views
    1,144

    Re: Amada Vipros Mystery Fault

    There is a switch, and if it comes off, it will lose that LED.

    Change parameter 85 for 4th axis home position.
  21. Re: Systen Alarm 926 FSSB Alarm (please help)

    post a picture of your screen. The NMIC information points you towards the problem.

    When does the alarm happen?
  22. Replies
    2
    Views
    1,177

    Re: Fanuc .Lad file

    ladders vary upon machine, not upon FANUC model.
  23. Replies
    3
    Views
    1,189

    Re: Setup Drive A06b-6069-H203 on Fanuc 21

    If they same issue is happening with the new drive... Then it's not the drive. Measure the resistance of the motor power U/V/W to GND with an insulation tester. It should measure above 200Megaohms....
  24. Replies
    1
    Views
    1,015

    Re: Power Supply Module Alarm A0

    A0? Are you sure this is on the Power Supply? Or is it on the Spindle Amplifier?

    If this is on the Spindle Amplifier, the software has gotten corrupt and needs reprogrammed.
  25. Replies
    10
    Views
    4,807

    Re: FANUC 18i ERROR CODE 2025

    Are you looking at parameters?... or Diagnostics?
  26. Replies
    2
    Views
    985

    Re: fanuc521 on a mori frontier

    Same control as a FANUC 21. The MSC521 is just a FANUC control, with a Mori custom side that they install.
  27. Replies
    2
    Views
    1,495

    Re: 4th axis compatibility with my Fanuc

    What kind of control is on the machine? Although the drive may be there, an option may need to be added in order for it to work properly. PLUS, the servo parameters will need to be set up.
  28. Replies
    5
    Views
    2,682

    Re: E44 hdlc response time-out error

    Most likely one of the MMC boards next to the CRT inside the cabinet.

    E44 HDLC RESPONSE TIME-OUT ERROR
    COMMUNICATION TO CNC WAS INTERRUPTED DURING COMMUNICATION INITIALIZATION
    CHECK CNC POWER...
  29. Re: FANUC 18M not booting up CPU won´t start. Black screen

    That is a machine side alarm. Check for an A address on in the ladder, then trace it back to the cause. If you have a manual for this machine, it should tell you what 1002 means.
  30. Replies
    2
    Views
    1,677

    Re: Fanuc Retrofit - Read ladder logic?

    Unless you have a hard copy, or a special device that only the MTB has. You won't be able to read the ladder. The ladder is either on the ROM board or PC board.