    Re: M96 problem on NexGen ST20 lathe

    Solved by adding G103 P1 before the M96 line, and G103 after M96 on both branches. The G103 P1 stops the look ahead feature so it will poll the input on the M96 line.
  2. Re: Non Haas bar feed interface to Haas NexGen

    Correction to program. Add G103 P1 before the M96 line, and G103 after M96 on both branches. The G103 P1 stops the look ahead feature so it will poll the input on the M96 line.
  3. Re: M96 problem on NexGen ST20 lathe, Posted in the Lathe Forum this time.

    Correction the G103 P1 does fix it. Thank you very much!!!!!
  4. Re: M96 problem on NexGen ST20 lathe, Posted in the Lathe Forum this time.

    Good thought, but I don't think so. I had considered lookahead, so after changing the input, I let the test program run for 5 minutes which would have run the M96 line about 150 time along with 4...
  5. Non Haas bar feed interface to Haas NexGen

    Other then trouble with the M96 the attached document shows how to interface to the new Haas NexGen lathe. I hope they will fix the M96 problem, so it will work. You will also need plugs to attach to...
  6. M96 problem on NexGen ST20 lathe, Posted in the Lathe Forum this time.

    I am trying to use the M96 command to poll the spare input that I am using for End of Bar from the bar feed. This is the way we have always done end of bar on the Haas lathes. However, on this new...
  7. Replies
    1
    Views
    762

    M96 problem on NexGen ST20 lathe

    I am trying to use the M96 command to poll the spare input that I am using for End of Bar from the bar feed. This is the way we have always done end of bar on the Haas lathes. However, on this new...
  8. Replies
    1
    Views
    1,036

    Re: plc on alpine bar feeder

    Alpine Automation is gone! I have finally had some luck with these Alpine barfeeds. As the battery in the PLC starts to go dead it will sometimes forget that the program is password protected. So I...