Should be: system -> PMM (power mate mng) -> Parameter
Type: Posts; User: Pucas
Should be: system -> PMM (power mate mng) -> Parameter
Hi, controller type, alarm no. and machine production year would help a lot.
Anyways if you still have the issue, give me the information and I will help you.
Hi! Normaly there should be an operating panel of sub spindle. Can you share a picture of your operation panel?
487911
Hi there! You can try to change nc parameters as below:
- 3100 bit 2: 0->1
- 14705 bit 0 and 6: 0->1
Hi,
try to set D10.1 to 0
Hi,
You can check parameter:
- 0577 Spindle speed command offset (always set to 0)
- 0516 Spindle speed command gain adjustment (always set to 1000)
Which spindle motor do you have?
Hi!!!
My questions would be:
- are the y, x and b axis in reference position (zero return position) when you command the tool change? check signals F94.0 (x), F94.2 (y 1st zero return)/ F96.2...
Hi!!! I think you already solve it. but in case if not you can check some points as follows....
- Check the parameter 1321. You should have a blue folder in electric cabinet. Find the 1321 in data...
Hi, I don't know the machine but it sounds like solenoid valve problem.
Hi,
Give me your email address.
Thanks
Please write me your email address I will send it to you.
I don't think that you will find the Manuals online... but maybe I can help you. I will check what can I find for you tomorrow.
Sorry my mistake. Should be M124 \ M125.
Hi,
it's M123 (Sub sp. center rigid tap mode on) and M124 (Sub sp. center rigid tap mode off)
E.G.
G80
G28U0
T0900
G00X0
amp alarms:
211552
2060 TURRET AMP ALARM
Cause:
- In case that alarm is issued on the turret AMP.
Actions: /Procedures:
- Take measures by means of reviewing the maintenance manual of FANUC I/O Link ...
Does it have PMM? If yes, set the turret to pos. 1, PMM parameter 11#0 to 0 to 1, power off/on.