Originally Posted by
i_r_machinist
Straight from Bob Campbell:
Try this. Make sure that the jumper JP1 is on both pins. Jp1 jumper makes a connection between the NO connection on the run relay to the center screw terminal on the dir relay.
For the connection to the VFD run a wire from the center screw terminal on the run relay to the common pin 11 on the VFD. Then run a wire from NC screw terminal on the Dir relay to terminal 1 on the VFD. Then run a wire from the NO screw terminal on the Dir relay to terminal 2 on the VFD.
To me, unless you have a Stop connection the VFD will always be in run?
Unless we are not getting the full picture on the VFD?
The contact is labelled RUN/Stop which implies that you open it to stop?
Originally Posted by
i_r_machinist
ps. Com doesn't always mean "ground" in electronics?
I've been trying to get that across for years!
Al.