    160V DC 12 Amps from 240V AC single phase supply

    I have a brushed DC motor rated at 160VDC 12 Amps (2.3hp). I want to control it with a Granite Devices controller, or similar. What is the best way to provide the 160V DC to the controller from 240V AC single phase? (and cheaply)

    I assume this could be done with a transformer, bridge rectifier and capacitors, but I have never seen a transformer of this size at my local electronics shop (500VA max).

    I already have a couple of amplifiers for AC servos which take the 240v AC and have a 340VDC bus. I assume they just rectify the 240vac into 340vdc.

    Are their off the shelve products to do this?

    Thanks,
    Frank

  2. #2
    Join Date
    Dec 2003
    Posts
    24220
    Not sure what is available in Australia, but do you have 'construction Site' transformers that are 240-120 as they do in the UK?
    The 120vac will give you the DC you are looking for if the VA is there.
    Alternatively try the local Electrical Suppliers for a similar 240/120 version.
    Just a couple of options to look at.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Feb 2006
    Posts
    101
    Thanks for the tips.

    On ebay (Australia) there are lots of 240 to 120 step down transformers, they say to run items from the US. Up to 2000VA, for $A195. (Like this one, item #180496483937, http://cgi.ebay.com.au/240V-TO-110V-...item2a066dc661)

    I assume these are just a transformer in a box. Are these suitable, if I gut out the transformer? Anything to watch out for in terms of quality?

  4. #4
    Join Date
    Dec 2003
    Posts
    24220
    The seller seems legit, 100% F.B. rating.
    There is not alot to a transformer to check, as long as it is copper winding and the Kva rated properly it should be OK.
    You could send a question to through ebay to one of the recent buyers to get an opinion.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. Can I convert single phase motor to three phase?
    By Jim Estes in forum Phase Converters
    Replies: 34
    Last Post: 06-04-2020, 02:52 PM
  2. Replies: 12
    Last Post: 10-13-2009, 03:53 AM
  3. Wiring Slo-Syn 240V 1 Phase Motors
    By PerPlexed in forum Servo Motors / Drives
    Replies: 7
    Last Post: 06-17-2009, 04:24 AM
  4. 240v supply and 208v motor
    By isu19151@verizo in forum Bridgeport / Hardinge Mills
    Replies: 8
    Last Post: 11-29-2007, 08:23 AM
  5. 2.5 amps per phase drive - 2.8 amps per phase bipolar motor ...
    By kochevnik in forum Stepper Motors / Drives
    Replies: 6
    Last Post: 10-23-2006, 04:48 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •