    DISabling servo drive power on a DX/SX system

    Anyone ever find/figure out/come up with a method of DISabling power to the servos on a DX or SX system? Like many, I've toyed with the idea of handwheels on my V2XT, and installing them is a trivial affair, but having the DRO on the controller's screen would be handy to say the least. Hitting the E-Stop disables the DRO as well as the servos, so no love going that way. Would it be as easy as simply using a mechanical/electronic switch to interrupt the power to the servos? Has anyone ACTUALLY done this? Would love to hear ideas on how it could be done.

  2. #2
    Join Date
    Aug 2010
    Posts
    109
    I'm not sure about your particular machine but on my Bridgeport EZ-TRAK SX it uses a weld proof contactor to break one wire of each dc servo to disable the servos but it still reads out the position.

  3. #3
    Join Date
    Feb 2009
    Posts
    19
    Quote Originally Posted by dreammstr6 View Post
    I'm not sure about your particular machine but on my Bridgeport EZ-TRAK SX it uses a weld proof contactor to break one wire of each dc servo to disable the servos but it still reads out the position.
    Excellent. Thank you for letting me know. Any chance you know WHICH wire it interrupts? I don't know what a weld proof contactor is, but I'll be looking it up, shortly. If you have the time, could you tell me what wire it interrupts, or any label the wire might have on it that I might be able to suss it out myself? Thank you.

    EDIT - If you could take a picture of this contactor that might help, too. Maybe a part number... Not having too much luck Googling it...

  4. #4
    Join Date
    Aug 2010
    Posts
    109
    on my mill it uses a motion science power amplifier. on the x axis the wires going to the contactor is 36 and 41 which is the positive wire for the motor. and on y the wires are 40 and 22 which is positive for y. the weld proof contactor is a interesting design. it uses a external solenoid to ingage the contacts which are spring loaded riding on a plastic shaft.

  5. #5
    Join Date
    Feb 2009
    Posts
    19
    Thank you very much for checking that for me. I have the MSI drives in my V2, as well, so will be going to check it shortly. I've built a few things in my life, but I'm not overly knowledgeable about electrical components. EDIT - I'm wondering if this can be something as simple as just interrupting the continuity of this wire for each axis... like using a mushroom switch with multi stage connectors on the back. (one for each axis)

  6. #6
    Join Date
    Aug 2010
    Posts
    109
    yvw. the relay is 2 parts 31918156 relay pole ac m and 31918154 magnetic relay. i don't see why a heavy duty double pole single throw relay wouldn't work. all that happens on my mill is anytime you take the machine out of manual mode by opening a program or selecting jog or such is that the contactor pulls in closing the circuit between the 2 power amplifiers and the motors.

  7. #7
    Join Date
    Feb 2009
    Posts
    19
    Awesome news. Thank you again! I'm going out to the shop to do some poking around. I'll let you know how it goes... I'm thinking that a mushroom switch, some wiring, a few gib locks, a quill lock, and some handwheels might add some functionality to my old girl.

  8. #8
    Join Date
    Aug 2010
    Posts
    109
    as long as the mushroom switch can maintain it's position and handle the amps should do the job. a quick and dirty test i did on a EZ-Trak DX was to pull the positive wire on the output of each amp and tape them up. i was testing for the readout change on screen when we had a bad bmdc card. maybe you will be lucky and be able to do the same

  9. #9
    Join Date
    Feb 2009
    Posts
    19
    Quote Originally Posted by dreammstr6 View Post
    as long as the mushroom switch can maintain it's position and handle the amps should do the job. a quick and dirty test i did on a EZ-Trak DX was to pull the positive wire on the output of each amp and tape them up. i was testing for the readout change on screen when we had a bad bmdc card. maybe you will be lucky and be able to do the same
    Just came back inside from the shop. What you propose is exactly what I am thinking to try, tomorrow. (little too exhausted to do it tonight) Checking my MSI drives and the machine's schematics, it looks like I have wire numbers 331/332 , 333/334 , 335/336 for the motor wires coming from each drive. I'll do a continuity and voltage check to determine which is positive and which is ground and then isolate the positive lead as you say yours does through the switch/contactor. I'm thinking I'd like a slightly more graceful approach than basically a light switch for this because as you point out - it has to handle the amperage... I'll have to ask of and rely on the helpfulness of others for that.

    Other than that, looks very straight forward for gib locks. Quill lock will be another story. The boss it usually exists in does not exist, so I'll peek inside the mechanism's cover for some ideas in there.

    Looking forward to doing this as I've always thought it was one of the three shortcomings of my V2.

    Thank you for your help. I appreciate it.

    Edit -

    Maybe I could use a SPST rocker or toggle, utilizing the 24V circuit within the cabinet, to trigger a relay (or 3 relays) for this and label it accordingly. (Manual/CNC)

  10. #10
    Join Date
    Aug 2010
    Posts
    109
    yvw. i'll help anyway i can. i would suggest a 110 contactor and a 2 position switch to break the wires. one contactor if 3 pole could do all 3 axis's and would be a simple circuit

  11. #11
    Join Date
    Feb 2009
    Posts
    19
    Quote Originally Posted by dreammstr6 View Post
    yvw. i'll help anyway i can. i would suggest a 110 contactor and a 2 position switch to break the wires. one contactor if 3 pole could do all 3 axis's and would be a simple circuit
    Just making sure I understand correctly -

    Are you suggesting a 110VAC contactor because the servos peak at 90VDC? Also, what's yvw? I'll go look up a contactor to see what they cost. Thanks!

  12. #12
    Join Date
    Aug 2010
    Posts
    109
    yvw. short for your very welcome. and why i suggested a 110 contactor most machines i have worked on use 110 for the control power for the spindle contactors. so would be easy to borrow power from that circuit to energize your extra contactor for the axis interuption

  13. #13
    Join Date
    Feb 2009
    Posts
    19
    Ah! I see. I see I also have to learn about contactors are described, as there are a vast range of results returned from my searches. I'm thinking that I use the 110VAC to "power" the contactor, and use the toggle to interrupt that power over the positive wire. Correct? Thanks!

  14. #14
    Join Date
    Aug 2010
    Posts
    109
    correct. you can use a simple 2 position off and on switch to turn the contactor off and on. your spindle probably uses 2 contactors for reversing the direction. u can use a single contactor similar to it just rated for the right amps. what part of the country you from? i might be able to lookup a suitable contactor in your area

  15. #15
    Join Date
    Nov 2004
    Posts
    3028
    There may be a little more to this.
    Example: The EZTRAK will put 12 VDC to the drives on the drive enable line to turn them OFF. I know this because I pull the green connector out of the AUXBOB to kill this 12VDC to turn the drives ON and see which one is generating the axis drive fault.

    So I believe the V2XT, Boss 8 and 9, and such do have those large contactors isolating the motors from the drives and a drive enable signal going to the drive boards.

    George
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  16. #16
    Join Date
    Aug 2010
    Posts
    109
    on my particular EZ-Trak the green connector you refer to hooks to cr1 which is a cube relay which energizes the bigger weld proof contactor which just breaks the possitive output going to the motors. there is nothing that turns the power amplifier itself off. now on my other mill it doesn't have the contactor. it does turn the amp itself off. i was just thinking if it works for my mill with the weld proof contactor it might be the easiest solution. i could be wrong though.

  17. #17
    Join Date
    Feb 2009
    Posts
    19
    Quote Originally Posted by dreammstr6 View Post
    correct. you can use a simple 2 position off and on switch to turn the contactor off and on. your spindle probably uses 2 contactors for reversing the direction. u can use a single contactor similar to it just rated for the right amps. what part of the country you from? i might be able to lookup a suitable contactor in your area
    I'm in Milwaukee. I got to thinking about this contactor theory, and an idea/question occurred to me. Then I saw George's reply, and got to thinking ... see below, please...

    Quote Originally Posted by machintek View Post
    There may be a little more to this.
    Example: The EZTRAK will put 12 VDC to the drives on the drive enable line to turn them OFF. I know this because I pull the green connector out of the AUXBOB to kill this 12VDC to turn the drives ON and see which one is generating the axis drive fault. So I believe the V2XT, Boss 8 and 9, and such do have those large contactors isolating the motors from the drives and a drive enable signal going to the drive boards. George
    Yes, I do have a contactor like that, and as just thinking about that kind of thing...

    When I traced those power wires coming from my MSI cards, they go through a 3 pole contactor located at the bottom left of the control cabinet, right below where the hard drive mounts. That's no longer there since I moved things around after upgrading the PC side of things to a 2Ghz AMD processor a few years back, so I can get to it rather easily to do this if it will work...

    Thanks, guys.

  18. #18
    Join Date
    Aug 2010
    Posts
    109
    then maybe it will be a easy fix for you

  19. #19
    Join Date
    Feb 2009
    Posts
    19
    You guys are getting my hopes and interest up! Gonna go limp into the shop again and verify the wires on that contactor... back in a few...

    EDIT - Back. Yep, I'm thinking this might just work out sweetly. Indeed the servo power wires go to a contactor down there. The contactor has two wires that I presume are the power wires for it, labeled 23 and 24, and being Red and White. They head back to the servo drive power supply, and into J19. I'm loathe to do something that might let any magic smoke out, but I'm very tempted to remove a drive cover to gain access to a table screw, remove one of those wires to the contactor and see what happens...

  20. #20
    Join Date
    Feb 2009
    Posts
    19
    Either of you wanna warn me away from doing such a thing...?

Page 1 of 2 12

Similar Threads

  1. Servo drive GME-system
    By Jan-Willem in forum Servo Motors / Drives
    Replies: 3
    Last Post: 04-06-2011, 08:40 PM
  2. please need guidance on servo system n drive
    By 15mgtar in forum Servo Motors / Drives
    Replies: 9
    Last Post: 07-25-2010, 09:12 PM
  3. Dynapath 10 replace servo drive & power supply??
    By ken fedirko in forum DNC Problems and Solutions
    Replies: 3
    Last Post: 01-13-2008, 12:30 AM
  4. Help w/ power supply for a 3-axis servo system
    By yantra3d in forum CNC Machine Related Electronics
    Replies: 2
    Last Post: 07-25-2007, 08:41 PM
  5. Disabling drive when not in use
    By rkonnen in forum Servo Drives
    Replies: 9
    Last Post: 09-12-2006, 11:48 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •