    Need Help! 5HP motor 460V to 230V?!

    I just bought a huge air distributer. 2000CFM driven by a 5HP electric motor 3450RPM. The motor is like new and must have been recently replaced!

    It comes with a really nice filter. My plan was to swap out the 2" thick filter for a really nice HEPA filter to keep my shop dust free. (i dont cut wood or grind/sand).

    The unit is actually in mint condition and works perfectly. It came with all the documentation and even the electric schematic for the allen bradely box.

    Its wired for 3 phase 460Volt.

    On the 5HP motor is clearly states 460V/230V. My shop only has 240V and i want to use it. How do i go about rewiring this thing?

    Later today i will go out there with a flashlight since night is coming and try and get pictures of the plaque on the motor.

    Thanks guys!
    Attached Thumbnails Attached Thumbnails 88287201014101130121837061494.jpg   88287201014101130121837061343.jpg   88287201014101130121837061182.jpg   88287201014101130121837061021.jpg  

    88287201014101130121837061495.jpg   IMAG0479.jpg   IMAG0480.jpg   IMAG0481.jpg  

    IMAG0482.jpg   IMAG0483.jpg  

  2. #2
    Join Date
    May 2010
    Posts
    0
    You cant just rewire the motor. You would have to make sure everything else in the air distributer can take 240V. Depending on how many amps it draws. It may be easier to get transformer to bump your voltage up.

  3. #3
    Join Date
    Dec 2003
    Posts
    24220
    If you take the terminal cover off, there is generally connection instructions on a label attached.
    If not post the present connections and terminal designations as they are often standard.
    Keep in mind you may have to increase the fuse and overloads size accordingly, hopefully the wire and contactor size is sufficient for the higher current.
    Also check the control transformer to see if the primary can be changed.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  4. #4
    Join Date
    Feb 2010
    Posts
    3447
    Quote Originally Posted by Al_The_Man View Post
    If you take the terminal cover off, there is generally connection instructions on a label attached.
    If not post the present connections and terminal designations as they are often standard.
    Keep in mind you may have to increase the fuse and overloads size accordingly, hopefully the wire and contactor size is sufficient for the higher current.
    Also check the control transformer to see if the primary can be changed.
    Al.
    Well by rewire i meant "just make it run" lol.

    I will take some really nice pictures of the inside of the box.
    Also have a few pictures of the motor as well. I will load them up later tonight!

    I'm excited!

  5. #5
    Join Date
    Feb 2010
    Posts
    3447

    Talking

    Here are the motor pictures. The angle which i had the camera is extremely tight, and i couldnt flash the center or it would blow out the text so sorry for the bad pictures, but all the information is there
    Attached Thumbnails Attached Thumbnails IMG_2771.jpg   IMG_2772.jpg   IMG_2774.jpg   9999.jpg  

    8888.jpg  

  6. #6
    Join Date
    Feb 2010
    Posts
    3447
    Inside of unit Allen-Bradley:



    Extra information i found:
    Uses a 13" direct drive chicago blower corportation blower 2000cfm.

    Calculated unit shipping weight 782 pounds.
    manufactured in 1997.
    Pretty sure its a new motor and not the original.
    Attached Thumbnails Attached Thumbnails IMG_7332.jpg   IMG_7333.jpg   IMG_7334.JPG   IMG_7335.JPG  

    IMG_7336.JPG   IMG_7337.jpg   IMG_7338.jpg   IMG_7339.JPG  


  7. #7
    Join Date
    Jan 2006
    Posts
    738
    Nice unit... Although I consider this a "small" blower, once you get up to about 100 HP I call em large. I do balance work on industrial blowers, some of them are up in the 800 - 1000 HP range.

    As Al suggested... Check the current rating of the breaker... when you go from 460 to 230 your current will increase (about drouble), so you may have to replace the breaker. Also check the contactor rating rating. Looks like the control transformer has dual primary, probably in series now, putting in in parallel may allow you to run it on 230 (240).

    Steve

  8. #8
    Join Date
    Jul 2006
    Posts
    1256
    You need 230 3 phase.Does your shop have 3 ph 230?
    L GALILEO THE EPOXY SURFACE PLATE IS FLAT

  9. #9
    Join Date
    Dec 2003
    Posts
    24220
    According to the print it shows a dedicated 460/120v 75va transformers, but looking at the actual transformer it appears to have primary taps.
    Check the actual txfr itself.
    Also on the motor change, the terminals are usually laid out as per the diagram #'s so all you do is change the links over.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  10. #10
    Join Date
    Feb 2010
    Posts
    3447
    Quote Originally Posted by lgalla View Post
    You need 230 3 phase.Does your shop have 3 ph 230?
    240V single phase

  11. #11
    Join Date
    Feb 2010
    Posts
    3447
    Quote Originally Posted by vger View Post
    Nice unit... Although I consider this a "small" blower, once you get up to about 100 HP I call em large. I do balance work on industrial blowers, some of them are up in the 800 - 1000 HP range.

    As Al suggested... Check the current rating of the breaker... when you go from 460 to 230 your current will increase (about drouble), so you may have to replace the breaker. Also check the contactor rating rating. Looks like the control transformer has dual primary, probably in series now, putting in in parallel may allow you to run it on 230 (240).

    Steve
    lol! 1000HP blower holy crap. That must be the size of a house!

    I will check breaker rating, and transformer out and report back.

  12. #12
    Join Date
    Dec 2003
    Posts
    24220
    Quote Originally Posted by diyengineer View Post
    240V single phase
    You could use a 1 ph in VFD just for 3ph for the motor and feed 240 1 ph directly into the control transformer.
    The contactor would go on the input side of the VFD.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  13. #13
    Join Date
    Feb 2010
    Posts
    3447
    Quote Originally Posted by Al_The_Man View Post
    You could use a 1 ph in VFD just for 3ph for the motor and feed 240 1 ph directly into the control transformer.
    The contactor would go on the input side of the VFD.
    Al.
    So the motor is unable to be ran via single phase alone? (damnit! haha)

    Whats the cheapest 5HP 240V single phase input with 3 phase output that you know of?

    Would this be able to help me out?
    G5842 Static Phase Converter - 2 to 5 HP

  14. #14
    Join Date
    Feb 2010
    Posts
    3447
    I know those solid state phase converters are no where as good as a rotary converters, but for the price its dirt cheap to get 3 phase power...

    A VFD would be better i guess but may cost hundreds more?

  15. #15
    Join Date
    Dec 2003
    Posts
    24220
    Never used on of those, Phase Perfect is the only other static phase convertor I know of, but that is made in the USA otherwise if it had been R.O.C. I would have said stay away.
    I have built a rotary version, but if viable, I prefer a VFD.
    That one is only rated at 70% of full load in continuous. A lot less for 90%.
    Try Driveswharehouse.com. http://www.driveswarehouse.com/Drives/AC+Drives.htm
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  16. #16
    Join Date
    Feb 2010
    Posts
    3447

    Talking Video of inside.

    [nomedia="http://www.youtube.com/watch?v=JdiLrP_urAI"]YouTube - Haakon Air Handler Need help converting to single phase operation.[/nomedia]
    Video should help a lot!

    As for a single phase input VFD to 3 phase output (5HP capacity), this seems to be my only option at a very steep $599.
    http://www.driveswarehouse.com/Drive...FD/PC1-50.html

  17. #17
    Join Date
    Dec 2003
    Posts
    24220
    Quote Originally Posted by diyengineer View Post
    As for a single phase input VFD to 3 phase output (5HP capacity), this seems to be my only option at a very steep $599.
    On the other hand, you got the whole unit for the price of the Cab tire cable hanging on the cable carrier!
    Al.

    A single phase motor would probably run fairly close, but may be cheaper. If you could sell the 3 phase one.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  18. #18
    Join Date
    Feb 2010
    Posts
    3447
    Quote Originally Posted by Al_The_Man View Post
    On the other hand, you got the whole unit for the price of the Cab tire cable hanging on the cable carrier!
    Al.

    A single phase motor would probably run fairly close, but may be cheaper. If you could sell the 3 phase one.
    Later today i will rip out the 5HP motor and load up some pictures.

    I looked and the motor is worth a pretty good chunk of change!

  19. #19
    Join Date
    Dec 2003
    Posts
    24220
    If looking for a 1phase replacement, you will need a 2 pole motor.
    3480rpm +.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  20. #20
    Join Date
    Jan 2006
    Posts
    738
    You might luck out by calling around to some local motor rebuild shops. Tell em what motor you have, and what you are needing. One of them may be willing to do an exchange for you for very little...

    Steve

Page 1 of 2 12

Similar Threads

  1. controller power supply 115/230v OK for Australian power?
    By Momill in forum Australia, New Zealand Club House
    Replies: 8
    Last Post: 07-07-2011, 05:06 PM
  2. Rewiring Transformer for 230V Input
    By keebler303 in forum CNC Machine Related Electronics
    Replies: 3
    Last Post: 05-27-2010, 05:24 PM
  3. 2M2280N 230V AC, high performance stepper driver
    By Zappautomation in forum News Announcements
    Replies: 0
    Last Post: 11-08-2009, 01:28 PM
  4. I need 3Phase 230V off 1Phase 110V, can I get help?
    By idtkid in forum CNC Machine Related Electronics
    Replies: 11
    Last Post: 07-14-2009, 02:56 PM
  5. Need help wiring 230V AC spindle motor
    By Heavy D in forum Knee Vertical Mills
    Replies: 4
    Last Post: 05-07-2006, 05:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •