    Unhappy 24Vdc Solid State Relay not the same as mechanical relay??

    Hello Guys.
    I have this 2 brand new Solid State relays
    (Salsar, SSR-10DA)
    SSR Relay (SSR-10DA) - China Solid state relay,ssr,relays in Relay & Contactor

    which I am currently use to close NO contact with 24Vdc input from CNC controller manual buttons (spindle CW and spindle CCW).
    The LED is is lid when push on/off...but the contact (Load Voltage: 24-380VAC) doesn't seem to close......

    Question is...this type of solid state is no good to close the contact?? Or am I just having bad Solid State?
    Alternatively....mechanical relay works just fine....
    I thought it works just the same?

  2. #2
    Join Date
    Dec 2003
    Posts
    24216
    I see no reason why it shouldn't work?
    I assume you are switching the AC to spindle direct, what type of spindle?
    how are you achieving the reverse (CW/CCW)?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Oct 2006
    Posts
    142
    Al,
    I was pretty confident that should work too.
    I connect the 2 SSR to FWD/REV/COM on the inverter to drive spindle CW/CCW.
    Normal relay works. Perhaps just bad solid state relay?

  4. #4
    Join Date
    Dec 2003
    Posts
    24216
    I am still not clear as to what you are controlling, those particular SSR's are intended to switch an AC load directly.
    If you are using them on a VFD type controller using theVFD logic inputs you are using the wrong device, they will not switch the low voltage low impedance input of a VFD.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Oct 2006
    Posts
    142
    I think you are right.
    I am using those LOGIC for the contact VFD, not the load itself. I thought it could be used similarly to the normal relay.

  6. #6
    Join Date
    Oct 2006
    Posts
    142
    But I am wondering why can't the logic contact be connected? it is just the contact open/close?

  7. #7
    Join Date
    Dec 2003
    Posts
    24216
    NO, the SSR has to see a compatible load and voltage type, the CW/CCW inputs are low level logic DC, the SSR's are high voltage AC output type, you may be able to use a low level logic output type such as 24vdc in and low level DC output, but in this case it seems hardly worth using SSR when a small simple mechanical relay would do it.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    Oct 2006
    Posts
    142
    Thanks Al
    very clear explanation.

Similar Threads

  1. Using a solid state relay as a main stop relay
    By garagefela in forum CNC Machine Related Electronics
    Replies: 4
    Last Post: 02-26-2010, 11:27 PM
  2. Expert on solid state relay needed.....
    By planekrazie in forum CNC Machine Related Electronics
    Replies: 7
    Last Post: 04-13-2009, 04:04 PM
  3. Router 0/1 with solid state relay
    By bigz1 in forum CNC Machine Related Electronics
    Replies: 6
    Last Post: 04-25-2008, 02:37 AM
  4. solid state relay question
    By aegfurn in forum CNC Machine Related Electronics
    Replies: 9
    Last Post: 02-24-2007, 04:09 AM
  5. Solid state relay
    By N4NV in forum CNC Machine Related Electronics
    Replies: 13
    Last Post: 05-07-2006, 06:19 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •