Originally Posted by
Alan Ing
Hi Jim,
Again, thanks for the advice!
Our shop has a single phase 208V circuit protected by a 50 amp circuit breaker that we use for welding. We also have several three phase 208V circuits which are probably 20 Amp.
I was leaning towards the 65 over the 45, but it appears to me that our circuits may not be adequate for the 65. The manual for the 65 says that the Input current at 9.0 kw ouput at 208V single phase is 52 Amps and can hit 75 Amps during arc stretch. It also mentions that we should install an 80 Amp slow-blow fuse. Sounds like we won't be able to run this set up. What do you think?
For the 45, at 208V single phase, the rated output is 45 Amps, Input current at 6kw 33Amps and arc stretch at 54.5 Amps. Recommended slow-blow fuse size is 50 Amps. If our breaker is rated at 50 amps, do we still need a slow blow fuse?
if the 45 is the way to go, what would you recommend as far as model numbers and accessories. Again, we are using a Precision Plasma LLC table with water table, C and CNC AIO Dragon with DTHC and will mainly be cutting 1/8" - 1/4" aluminum as precisely as we can.
I was thinking about the 088022 which comes with the T45m machine torch. Do we need to buy the 128650 Remote Pendant and the CNC spade plug? If so which one, the 228350 (for divided arc voltage) or the 23206 (for non divided arc voltage usage). What consumable set should I buy? I don't recall seeing a finecut set.
Sorry for all the questions. I have a limited time to get this set up going before our robotics competition starts in January.
Best Regards,
Alan