  1. #741
    Join Date
    Jan 2021
    Posts
    12

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    Yes, if you look through what I have posted here you will find the Parameter's you need to set for your spindle, or if you post the complete spindle motor spec's then I can post what Parameters you need to set
    Already read .. thank you mactec54 !

  2. #742
    Join Date
    Mar 2021
    Posts
    6

    Re: Huanyang Chinese VFD settings and manual here!

    I received my HY VFD a couple of days ago. It’s 2.2kw. I wanted to test as soon as possible since it will be couple of months before I complete my build. While Testing with a 2.2kw spindle I noticed that there was a motor spinning sound coming from spindle but collet nut was not spinning. I reset the vfd several times but problem persisted. Removed and reconnected wires on both sides a few times. After spending a couple of hours I decided to open the spindle from top. What I noticed was the numbers on aviation plugs were not matching with internal wiring. #4 pin was supposed to be earth or not connected but inside the spindle it was connected and pin #3 was not connected. Swapping the wires worked without any issue.

  3. #743
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Arjcnc View Post
    I received my HY VFD a couple of days ago. It’s 2.2kw. I wanted to test as soon as possible since it will be couple of months before I complete my build. While Testing with a 2.2kw spindle I noticed that there was a motor spinning sound coming from spindle but collet nut was not spinning. I reset the vfd several times but problem persisted. Removed and reconnected wires on both sides a few times. After spending a couple of hours I decided to open the spindle from top. What I noticed was the numbers on aviation plugs were not matching with internal wiring. #4 pin was supposed to be earth or not connected but inside the spindle it was connected and pin #3 was not connected. Swapping the wires worked without any issue.
    This is common that the Ground is not connected inside the spindle, you have to connect this, this is a first check everyone should do before connecting any power to the spindle, the 4th pin must be Grounded

    The correct wiring of the plugs are important when you here something like this with these spindles you have a phase missing or incorrectly wired
    Mactec54

  4. #744
    Join Date
    Mar 2021
    Posts
    2

    Question Re: Huanyang Chinese VFD settings and manual here!

    This thread is an asset to the internet and I'd like to thank Mactec54 for answering all these questions for so many years.

    I'm at a loss and nowhere else to turn so hopefully it's not too much of an imposition to ask about setting up a Hyunyang 7.5kw GT series to operate a 5hp 3 phase table saw. The settings are pretty basic according to numerous vids on youtube, but I'd like to mount the vfd on a wall away from the saw for a number of reasons. Is it possible to do this and add an on/off switch at the saw? Is there a way using the green terminals to program a remote on/off switch?


    If it isn't possible to locate the VFD remotely it seems wise to protect it from dust which in my mind means enclosing it and adding a fan and filters to remove heat. That adds another layer since there is no 12vdc power or even 120vac to power the fan at the saw unless I add that. The saw is on wheels by necessity as it must be stored in one area and used in another. so that means dragging power along with it.

  5. #745
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by justbrowsingthrough View Post
    This thread is an asset to the internet and I'd like to thank Mactec54 for answering all these questions for so many years.

    I'm at a loss and nowhere else to turn so hopefully it's not too much of an imposition to ask about setting up a Hyunyang 7.5kw GT series to operate a 5hp 3 phase table saw. The settings are pretty basic according to numerous vids on youtube, but I'd like to mount the vfd on a wall away from the saw for a number of reasons. Is it possible to do this and add an on/off switch at the saw? Is there a way using the green terminals to program a remote on/off switch?


    If it isn't possible to locate the VFD remotely it seems wise to protect it from dust which in my mind means enclosing it and adding a fan and filters to remove heat. That adds another layer since there is no 12vdc power or even 120vac to power the fan at the saw unless I add that. The saw is on wheels by necessity as it must be stored in one area and used in another. so that means dragging power along with it.
    So are you going to mount the VFD in a Metal box /cabinet on the saw or mount it some where else, seeing that you have to move it would be best is to mount it on the saw, there is a relay in the VFD Drive that can be used to switch on a Fan, there are many ways to do this, if remote is what you really want to do then it can be done with careful planning

    If your saw motor is 50Hz /60Hz then most likely there won't be much to change for the Drive setup as by default VFD Drives are set for either a 50Hz or 60Hz motor depending in what country you live

    Remote On / Off it easy to do
    Mactec54

  6. #746
    Join Date
    Mar 2021
    Posts
    2

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    So are you going to mount the VFD in a Metal box /cabinet on the saw or mount it some where else, seeing that you have to move it would be best is to mount it on the saw, there is a relay in the VFD Drive that can be used to switch on a Fan, there are many ways to do this, if remote is what you really want to do then it can be done with careful planning

    If your saw motor is 50Hz /60Hz then most likely there won't be much to change for the Drive setup as by default VFD Drives are set for either a 50Hz or 60Hz motor depending in what country you live

    Remote On / Off it easy to do
    I want to mount the VFD on a wall in a location it would not need the enclosure and I have 25' of heavy jacketed cabling to reach the saw. The motor is indeed 50/60hz and setup is pretty basic. There is a wealth of information online as to the settings for this application but I can't find any information about setting up the remote on/off.

    I'm glad to hear remote on/off is easy to do. How do I go about finding the information to set that up? I'd like to use something like a Woodstock D4151 which is just a basic switch but has a large paddle for emergency stop. When the switch is closed the vfd starts when its open it stops. I've read the manual and the answer seems close I just am not getting it.

  7. #747
    Join Date
    Jan 2021
    Posts
    12

    Re: Huanyang Chinese VFD settings and manual here!

    Hello, is it correct ?

    SPINDLE
    Power: 2.2 KW
    Voltage: 220V~250V
    Frequency: 400 Hz
    https://www.aliexpress.com/item/1005002265161177.html

    Huanyang 2,2kW input 1 phase 230V
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=220
    PD009=15
    PD010=8
    PD011=120 (Minimum Setting 120)
    PD014 Accel=10
    PD015 Deccl=10
    PD070=0
    PD072=400
    PD073=120
    PD141=220 ( Motor Rated Voltage )
    PD142=9 ( Motor Max Amps)
    PD143=2 ( Motor Number of Poles)............................................ .?!?!?
    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    Because i measure VDF output there is between ground and phase 350V .......and between phase and phase 0V ?!? Is correct ?

  8. #748
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Fiury View Post
    Hello, is it correct ?

    SPINDLE
    Power: 2.2 KW
    Voltage: 220V~250V
    Frequency: 400 Hz
    https://www.aliexpress.com/item/1005002265161177.html

    Huanyang 2,2kW input 1 phase 230V
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=220
    PD009=15
    PD010=8
    PD011=120 (Minimum Setting 120)
    PD014 Accel=10
    PD015 Deccl=10
    PD070=0
    PD072=400
    PD073=120
    PD141=220 ( Motor Rated Voltage )
    PD142=9 ( Motor Max Amps)
    PD143=2 ( Motor Number of Poles)............................................ .?!?!?
    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    Because i measure VDF output there is between ground and phase 350V .......and between phase and phase 0V ?!? Is correct ?
    They are the correct basic settings for that spindle, number of Poles =2

    You can not use a regular meter to measure the VFD Drive output voltage, unless it has a low pass filter built in, you can cause damage also if you short it out, a regular meter will also give you a false reading
    Mactec54

  9. #749
    Join Date
    Jan 2021
    Posts
    12

    Re: Huanyang Chinese VFD settings and manual here!

    I am starting to be crazy..

    I tryed all the day ..
    a) try to manual start on VDF ... not help
    - made pictures 6699,6701,6702 , that no output

    b) changed to older VDF MK100 , ... spindle runing
    https://storage.ua.prom.st/1383685_i...atelya_eng.pdf
    - pictures 6703,6704
    - but there is no posibility to engage control from Messa 7i76e to this VDF.

    c) changed cabel to spindle not help

    Looks like VDF is KO (i had one electric shock by mountnig,not to me only circuit breaker ) ...... any chance to check if is ko or not ? (but it "looks well" )

  10. #750
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Fiury View Post
    I am starting to be crazy..

    I tryed all the day ..
    a) try to manual start on VDF ... not help
    - made pictures 6699,6701,6702 , that no output

    b) changed to older VDF MK100 , ... spindle runing
    https://storage.ua.prom.st/1383685_i...atelya_eng.pdf
    - pictures 6703,6704
    - but there is no posibility to engage control from Messa 7i76e to this VDF.

    c) changed cabel to spindle not help

    Looks like VDF is KO (i had one electric shock by mountnig,not to me only circuit breaker ) ...... any chance to check if is ko or not ? (but it "looks well" )
    To start in manual mode

    PD001=0

    PD002=0

    Why would the other VFD Drive not connect to the Messa Both VFD Drives have the same output to control the speed and On / off
    Mactec54

  11. #751
    Join Date
    Jan 2021
    Posts
    12

    Re: Huanyang Chinese VFD settings and manual here!

    Manual mode - i did it PD001=0 PD002=0 .............. but not run. But VDF not looks damaged..

    Old VDF MK100
    - you try to hlep me 6 months ago.. when i start.. https://www.cnczone.com/forums/spind...ml#post2424974
    - but i was not sure with the setting of paremeters , and with my poor settings skill it works only manualy
    - i decide to buy VDF HY , because there was many informations how to setup it Dont want to bother you . Decide to use MK100 for some next project..

    Do you think that I could ask you for help with setting the VDF MK100 parameter ? To not burn next spindle ...
    Probably i will have to try again use MK100 , because i dont know if HY is ko or not..

  12. #752
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Fiury View Post
    Manual mode - i did it PD001=0 PD002=0 .............. but not run. But VDF not looks damaged..

    Old VDF MK100
    - you try to hlep me 6 months ago.. when i start.. https://www.cnczone.com/forums/spind...ml#post2424974
    - but i was not sure with the setting of paremeters , and with my poor settings skill it works only manualy
    - i decide to buy VDF HY , because there was many informations how to setup it Dont want to bother you . Decide to use MK100 for some next project..

    Do you think that I could ask you for help with setting the VDF MK100 parameter ? To not burn next spindle ...
    Probably i will have to try again use MK100 , because i dont know if HY is ko or not..
    Make the seller replace the VFD if it is not working, did you connect your supply power connect to the R and T terminals and Ground to the Ground connection

    Can you do a photo of the input power connection
    Mactec54

  13. #753
    Join Date
    Jan 2021
    Posts
    12

    Re: Huanyang Chinese VFD settings and manual here!

    Hello,

    Im in work...Input R(phase) , T (null) , ground .... output U,V,W, ground (spindle which burned works on this a few min... 2 months ago)
    I buyed this from Aliexpress , no reclamation possible.

    Probably, i will have to change to VDF MK100 ... but if i remember i think i had problem to controled by messa card..

  14. #754
    Join Date
    Jan 2021
    Posts
    12

    Re: Huanyang Chinese VFD settings and manual here!

    VDF HY was down, i ordered newone and everything working well, thank for support to all.

  15. #755
    Join Date
    Aug 2021
    Posts
    4

    Re: Huanyang Chinese VFD settings and manual here!

    Hi All, I'm really struggling with my new spindle. I had a 1.5kW spindle running fine but wanted to be able to use 1/2" mills so I upgraded to a 2.2kW ER20 spindle with the Huanyang VFD. Model Hy02D211B AC110 50Hz/60Hz+/-5Hz (that makes no sense to me, is it 50Hz or 60Hz?)
    The spindle is 2.2kW 110v 8.5A 400 Hz
    Can someone please tell me what to enter in the VFD? I've looked through almost all of this thread and can't make sense of much of it, I also didn't see any settings for 110v.
    Thanks much! Paul

  16. #756
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by PWoolson View Post
    Hi All, I'm really struggling with my new spindle. I had a 1.5kW spindle running fine but wanted to be able to use 1/2" mills so I upgraded to a 2.2kW ER20 spindle with the Huanyang VFD. Model Hy02D211B AC110 50Hz/60Hz+/-5Hz (that makes no sense to me, is it 50Hz or 60Hz?)
    The spindle is 2.2kW 110v 8.5A 400 Hz
    Can someone please tell me what to enter in the VFD? I've looked through almost all of this thread and can't make sense of much of it, I also didn't see any settings for 110v.
    Thanks much! Paul
    Set your VFD drive to all the same settings in the above posts

    The only different Parameters to set different are
    PD008=110 If this is your Spindle motor Rated voltage

    PD141=110

    You might be disappointed buying this 2.2Kw as the 1.5Kw will most likely run better on this voltage
    Mactec54

  17. #757
    Join Date
    Aug 2021
    Posts
    4

    Re: Huanyang Chinese VFD settings and manual here!

    Thanks! So here's what I'm entering. Let me know if it's not right.
    Also, this will be used totally manually, I don't hook it through the controller. Would that change PD001 and PD002?

    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=110
    PD009=15
    PD010=8
    PD011=120 (Minimum Setting 120)
    PD014 Accel=10
    PD015 Deccl=10
    PD070=0
    PD072=400
    PD073=120
    PD141=110
    PD142=8.5
    PD143=4 my motor has one of the aircraft plugs with 4 wires. One is a ground though, so should this be 4 or 3?
    PD144=3000 (Max Motor RPM) =3,000= (24,000)

  18. #758
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by PWoolson View Post
    Thanks! So here's what I'm entering. Let me know if it's not right.
    Also, this will be used totally manually, I don't hook it through the controller. Would that change PD001 and PD002?

    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=110
    PD009=15
    PD010=8
    PD011=120 (Minimum Setting 120)
    PD014 Accel=10
    PD015 Deccl=10
    PD070=0
    PD072=400
    PD073=120
    PD141=110
    PD142=8.5
    PD143=4 my motor has one of the aircraft plugs with 4 wires. One is a ground though, so should this be 4 or 3?
    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    Not quite right for manual control

    PD001=0
    PD002=0 ( if you have a pot to control the speed then this would be PD002=1 )

    J1 Jumper may need changing also

    PD002=1 These ( 2 )Parameters are for Pot / Manual Speed Control
    PD073=1

    PD143=2 ( This is the number of motor Poles this has nothing to do with wiring )

    The output from the VFD Drive to the spindle is 3Ph so you have 3 Hot wires and a Ground so 4 wires are required
    Mactec54

  19. #759
    Join Date
    Aug 2021
    Posts
    4

    Re: Huanyang Chinese VFD settings and manual here!

    Well, I got closer. I entered everything as you told me 002=1, 073=1, 143=2. Pushed the run button and dialed up the speed. I heard the high pitch of the spindle and got all excited only to see it make about one full revolution and stop with an error on the screen EoUA. Any thoughts?

  20. #760
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by PWoolson View Post
    Well, I got closer. I entered everything as you told me 002=1, 073=1, 143=2. Pushed the run button and dialed up the speed. I heard the high pitch of the spindle and got all excited only to see it make about one full revolution and stop with an error on the screen EoUA. Any thoughts?
    This is telling you you don't have enough voltage / Amps to run it, this is a common problem when someone tries to run these 2.2Kw spindles on 120v single phase, set the pot to the lowest speed and see it can start at the low speed

    So press Reset ( Stop Button ) and try at the lowest speed turning the pot right back

    I guess you are using a standard 120v 15A outlet

    How do you have the main Power supply connected to the VFD Drive this is important
    Mactec54

Page 38 of 41 283637383940

Similar Threads

  1. Car hoist 3phase settings on huanyang vfd
    By pietskiet in forum Spindles / VFD
    Replies: 1
    Last Post: 10-21-2019, 10:04 AM
  2. Replies: 4
    Last Post: 02-16-2017, 05:42 AM
  3. Huanyang SL-240EE Manual (SL Series Manual for Vector VFD)
    By Cogolith in forum Phase Converters
    Replies: 2
    Last Post: 05-24-2016, 04:19 AM
  4. Huanyang inverter PD settings
    By jamriggsy in forum Phase Converters
    Replies: 2
    Last Post: 03-15-2013, 04:54 PM
  5. Huanyang 2.2kw VFD, 0-10v 3600rpm settings?
    By EmeraldIsleforg in forum Phase Converters
    Replies: 1
    Last Post: 09-23-2012, 03:00 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •