    Re: Huanyang Chinese VFD settings and manual here!

    You can control speed(frequency) via Modbus by assigning each its own modus id.

  2. #662
    Join Date
    Apr 2005
    Posts
    23

    Re: Huanyang Chinese VFD settings and manual here!

    Posting an update on my situation.

    First great thread. I got very nice help from mactec54 on a new VFD running my lathe project. Found out a big mistake was to start the motor then put clutch on and had faults. Now starting with the clutch on it works fine.

    I had a VFD on my mill and had a problem with the VFD faulting half the time when I switched it on. Attempted to change to a different VFD and was asking for help on that. THEN I got to thinking about what was wrong with the VFD on my mill. It was that I was starting the VFD first then switching the power on with a switch between the VFD and the motor. Took out the switch and let the VFD run the motor itself and it works fine. Goes to show the VFD should have full control of the motor with no switching between the VFD and motor.

    I am shelving the new VFD for another day, don't need it.

    I know it was dumb to have a switch between the VFD and the motor but that was the problem. Wouldn't have figured that out without this forum and this thread.

    Thank You mactec54

  3. #663
    Join Date
    Dec 2008
    Posts
    3

    Re: Huanyang Chinese VFD settings and manual here!

    Looking for some advice I have ordered a Huanyang HY04D023B 4.0kw VFD.
    Would like to make sure the setting i have put together from this very helpful thread look correct.
    My motor is a 2HP 230 volt 3 phase 5.2 amps 60HZ 3480 RPM Supply voltage is 240 single phase.
    PD000= 0
    PD001= 0
    PD002= 0
    PD003= 60
    PD004= 60
    PD005= 60
    PD006= 2.5
    PD007= 10
    PD008= 230
    PD009= 20
    PD010= 8
    PD011= 40
    PD013= 8 for reset only
    PD014= 15
    PD015= 15
    PD141= 230
    PD142= 5.2
    PD143= 4 poles
    PD144= 3000
    PD072= 60
    PD073= 60

    Any advise is welcome
    Thank you for your time
    Dan

  4. #664
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by DanPoynter View Post
    Looking for some advice I have ordered a Huanyang HY04D023B 4.0kw VFD.
    Would like to make sure the setting i have put together from this very helpful thread look correct.
    My motor is a 2HP 230 volt 3 phase 5.2 amps 60HZ 3480 RPM Supply voltage is 240 single phase.
    PD000= 0
    PD001= 0
    PD002= 0
    PD003= 60
    PD004= 60
    PD005= 60
    PD006= 2.5
    PD007= 10
    PD008= 230
    PD009= 20
    PD010= 8
    PD011= 40
    PD013= 8 for reset only
    PD014= 15
    PD015= 15
    PD141= 230
    PD142= 5.2
    PD143= 4 poles
    PD144= 3000
    PD072= 60
    PD073= 60

    Any advise is welcome
    Thank you for your time
    Dan
    Your numbers look Ok when using a VFD you can have a higher and lower Hz range if you need it, this will depend on what you are using your motor for, you have it set for a lower HZ RPM

    You have PD011=40 minimum speed

    PD073=60 should be 40 also
    Mactec54

  5. #665
    Join Date
    Dec 2008
    Posts
    3

    Re: Huanyang Chinese VFD settings and manual here!

    Mactec54 thank you for your reply, the motor is on a mill i will change PD073 to 40

  6. #666

    Re: Huanyang Chinese VFD settings and manual here!

    Good afternoon. I have Model HY02D211B. I have successfully run the spindle via onboard controls and onboard POT. I have connected wires from PlanetCNC output board as follows:
    Signal and common from PlanetCNC relay to FOR and DCM
    Signal and common from PlanetCNC 0-10v variable to V1 and ACM

    My relating VFD settings are as follows:
    PD001 set to 1
    PD002 set to 1
    PD070 set to 0

    With this setup and settings, I am able to start and stop the spindle via CNC controller. However, I am unable to control the frequency via CNC controller. The onboard POT will work, but only to half speed due to PD070. I have checked with meter to V1 screw terminal that the voltage changes appropriately dependent on speed command to CNC controller. What am I missing? Do I have a bad VFD?

  7. #667
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by iBigNTastyi View Post
    Good afternoon. I have Model HY02D211B. I have successfully run the spindle via onboard controls and onboard POT. I have connected wires from PlanetCNC output board as follows:
    Signal and common from PlanetCNC relay to FOR and DCM
    Signal and common from PlanetCNC 0-10v variable to V1 and ACM

    My relating VFD settings are as follows:
    PD001 set to 1
    PD002 set to 1
    PD070 set to 0

    With this setup and settings, I am able to start and stop the spindle via CNC controller. However, I am unable to control the frequency via CNC controller. The onboard POT will work, but only to half speed due to PD070. I have checked with meter to V1 screw terminal that the voltage changes appropriately dependent on speed command to CNC controller. What am I missing? Do I have a bad VFD?
    Check the Jumper is on 1-2 , if the pot is active then you don't have Parameters set or the Jumper is incorrect, the pot is not active when using remote control
    Mactec54

  8. #668

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    Check the Jumper is on 1-2 , if the pot is active then you don't have Parameters set or the Jumper is incorrect, the pot is not active when using remote control
    Wait... there's a jumper too? Man, I feel like an idiot. Can you describe the location of said jumper?

  9. #669

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by iBigNTastyi View Post
    Wait... there's a jumper too? Man, I feel like an idiot. Can you describe the location of said jumper?
    Never mind. Reviewing the picture I took of the wiring at the VFD terminals, I can see the jumper off to the right. Can't believe I didn't notice that before...

  10. #670
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by iBigNTastyi View Post
    Wait... there's a jumper too? Man, I feel like an idiot. Can you describe the location of said jumper?
    No unless you know about these VFD Drives, many have the same problem with this Jumper, and other settings, but somewhere in this thread it would of been posted, there are so many posts things like this get lost
    Mactec54

  11. #671
    Join Date
    Apr 2007
    Posts
    42

    Re: Huanyang Chinese VFD settings and manual here!

    Hi. I have not read this whole tread, so it may have been answered before, but:

    Is there any way to "reverse" specific inputs so i can use NC switches in stead of the NO switches that is in the wiring example?
    I want to set up one input as Stop and one as E-Stop and want both of these to be NC inputs. (and the rest as NO)

  12. #672
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by flesvik View Post
    Hi. I have not read this whole tread, so it may have been answered before, but:

    Is there any way to "reverse" specific inputs so i can use NC switches in stead of the NO switches that is in the wiring example?
    I want to set up one input as Stop and one as E-Stop and want both of these to be NC inputs. (and the rest as NO)
    Depends on what VFD Drive you have but if you have the Huanyang then you use RST and DCM for your Estop circuit and For and DCM for your Stop

    Both are switched with external Relays and are N/0 Relays they are closed to activate open for a Fault or Stop which you don't want it to be any other way
    Mactec54

  13. #673
    Join Date
    Apr 2007
    Posts
    42

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    Depends on what VFD Drive you have but if you have the Huanyang then you use RST and DCM for your Estop circuit and For and DCM for your Stop

    Both are switched with external Relays and are N/0 Relays they are closed to activate open for a Fault or Stop which you don't want it to be any other way
    Yes it is the Huanyang drive

    Ok. So multi-input 1 and 3 is NC inputs by default?

    So i can set the following:
    - PD044: Stop (4)
    - PD045: Run (1)
    - PD046: E-stop (13)
    - PD047: Reversed (15)
    - PD048: NA
    - PD049: NA

    And then the Stop and E-Stop will be NC inputs?

  14. #674
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by flesvik View Post
    Yes it is the Huanyang drive

    Ok. So multi-input 1 and 3 is NC inputs by default?

    So i can set the following:
    - PD044: Stop (4)
    - PD045: Run (1)
    - PD046: E-stop (13)
    - PD047: Reversed (15)
    - PD048: NA
    - PD049: NA

    And then the Stop and E-Stop will be NC inputs?
    To make the system work yes, they open to stop or for a fault, the E stop circuit will be closed only after Reset in your Control is set so the Relay is No until Reset

    The same for the stop that will be open until it has a signal to close from the control to close

    If you have trouble ( some do ) with the RST connection you should use DRV and DCM connection

    DRV and DCM
    PD050 Parameter to set
    Mactec54

  15. #675
    Join Date
    Mar 2016
    Posts
    1
    Good evening,

    I have an HY01D511B Huanyang VFD (110V 1.5kw) and a KL-800A Spingle (220V 400Hz).

    I have it working for the most part but am having some issues with the spindle not responding to the M3 S0 or M5 commands.

    The spindle is responding correctly to the SXXX part of the M3 commands when SX is greater than 0. Meaning as long as I'm not trying to stop it the speed control command is working as expected, but if I enter the M3 S0 or M5 command I the spindle just keeps spinning at the minimum defined value (7200 RPM or 120 Hz)

    Could someone confirm the correct parameters for this VFD and spindle combination.

  16. #676
    Join Date
    Jan 2013
    Posts
    0
    Quote Originally Posted by mactec54 View Post
    This is not new we all know that you can jumper this connection,( I have posted that before, for testing use only) the reason you need a relay is it is not safe to use without it

    The Parameters are also what has been posted hundreds of times

    So for anyone reading this post, this does not eliminate the use of a relay, when using PWM control, a Relay must be used for safety reasons
    I plan to use a hardwired switch rather than a relay for safety purposes, so when needing to change a tool or interact with the spindle I will use the switch to ensure it cannot turn on, but I still want the ability to shut off the spindle when idle using just gcode commands. The problem I'm running into is I cannot get the spindle to stop with a M3S0 or M5 command.

    Which parameters should I be looking at.

  17. #677

    Re: Huanyang Chinese VFD settings and manual here!

    Hello,

    Great thread. I have a 2.2kw spindle and the 3hp Hyuang VFD for it.

    I am running an Acorn board and controlling the spindle with the software. I have controllable voltage from the board from 0 to 10 v. I have p001 set at 1 for remote control and p002 set at 1 for remote freq control.

    When I run a program the spindle turns on and runs up to 400hz when the s16000 is what was called in the g code?

    Is the remote considered a “pot” and do I need to configure p070, p 071 and p 072?

    Thank you

    Phil

  18. #678
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Firepilot View Post
    Hello,

    Great thread. I have a 2.2kw spindle and the 3hp Hyuang VFD for it.

    I am running an Acorn board and controlling the spindle with the software. I have controllable voltage from the board from 0 to 10 v. I have p001 set at 1 for remote control and p002 set at 1 for remote freq control.

    When I run a program the spindle turns on and runs up to 400hz when the s16000 is what was called in the g code?

    Is the remote considered a “pot” and do I need to configure p070, p 071 and p 072?

    Thank you

    Phil
    Cut and paste what Parameters you have set as they all have to be correct for the speed to work correctly

    J1 Jumper also has to be set for Remote Control

    PD070=0 for 0-10v ( 1 ) for 0-5v

    PD072=400

    PD073=120

    PD071 is not used leave at the default of 20
    Mactec54

  19. #679
    Join Date
    Jun 2012
    Posts
    153

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    Cut and paste what Parameters you have set as they all have to be correct for the speed to work correctly

    J1 Jumper also has to be set for Remote Control

    PD070=0 for 0-10v ( 1 ) for 0-5v

    PD072=400

    PD073=120

    PD071 is not used leave at the default of 20
    I think you have 72 and 73 backwards. PD072 is shown as meaning lower "analog" frequency. Default is 50 since motors will heat up badly at low rpm. because there's little back EMF from the windings.

    PD073 is max "analog" frequency with default of zero, which I guess mean no limit, so effectively 400Hz = 24000 rpm for these units.

    You also need PD002 =1 to set "external" input for frequency control. PD001=1 if you want remote on/off ie M3/M5

    Then set PD044 ( or 45,46 ) =1 to set D1 ( or D2,D3 ) input terminal to use for on/off input . See p37 for more on that.



    I used the following opto-isolator cct to interface to my controller CPU's GPIO lines:

    Attachment 433498

    Many thanks to OP for post the link to the doc. I have mislaid my paper manual and this is a life-saver.

  20. #680
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by reg.miller View Post
    I think you have 72 and 73 backwards. PD072 is shown as meaning lower "analog" frequency. Default is 50 since motors will heat up badly at low rpm. because there's little back EMF from the windings.

    PD073 is max "analog" frequency with default of zero, which I guess mean no limit, so effectively 400Hz = 24000 rpm for these units.

    You also need PD002 =1 to set "external" input for frequency control. PD001=1 if you want remote on/off ie M3/M5

    Then set PD044 ( or 45,46 ) =1 to set D1 ( or D2,D3 ) input terminal to use for on/off input . See p37 for more on that.



    I used the following opto-isolator cct to interface to my controller CPU's GPIO lines:

    Attachment 433498

    Many thanks to OP for post the link to the doc. I have mislaid my paper manual and this is a life-saver.
    No they are correct as per manual and have not changed in the last 10 years

    From the manual

    PD072 Higher Analog Frequency

    PD073 Lower Analog Frequency
    Mactec54

Page 34 of 41 243233343536

Similar Threads

  1. Car hoist 3phase settings on huanyang vfd
    By pietskiet in forum Spindles / VFD
    Replies: 1
    Last Post: 10-21-2019, 10:04 AM
  2. Replies: 4
    Last Post: 02-16-2017, 05:42 AM
  3. Huanyang SL-240EE Manual (SL Series Manual for Vector VFD)
    By Cogolith in forum Phase Converters
    Replies: 2
    Last Post: 05-24-2016, 04:19 AM
  4. Huanyang inverter PD settings
    By jamriggsy in forum Phase Converters
    Replies: 2
    Last Post: 03-15-2013, 04:54 PM
  5. Huanyang 2.2kw VFD, 0-10v 3600rpm settings?
    By EmeraldIsleforg in forum Phase Converters
    Replies: 1
    Last Post: 09-23-2012, 03:00 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •