How to setup Chinese VFD to 2.2KW spindle.
Picture included, as well as PDF manual.

(I dont own the product, just figured this would help EVERYone else out that does!!)

PDF file is 15.8MB (large). It actually is very easy to read and navigate, i was impressed on how informational it is. Hope this helps someone!





From: [email protected]
1. I drafed the wire picture. Please see from the link: http://www.jinlantrade.com/Stock%20files/0008.jpg
2. You can see download the inverter manual from web link:
http://www.jinlantrade.com/ebay/invertermanual.pdf
3. I just tell you how to set up VFD as following
Firstly, adjust the PD013 to 8 (set the setting to factory setting)
Secondly, adjust the PD005 to 400
Thirdly, adjust the PD004 to 400
Finally, adjust the PD003 to 400
Finally, adjust the PD144 to 3000
Note: you should set PD013, PD005, PD004,PD003, PD144 in order. It mean you should firstly set PD013, then PD005, then PD004, then set PD003, finally set PD144.
Note: after you set the all above parameter, then please recheck the PD005, PD004, PD003 value is 400 or not to confirmed that you already set it. (note: please do not check the PD013, or all the setting will go to factory setting)
The reason we let you recheck is that if you do not set it at 400, then when you run the spindle motor, the spindle motor will be over-current, then the spindle will very hot and then within 5 minutes, it will broken.