I just bought this VFD
3KW 110V VARIABLE FREQUENCY DRIVE INVERTER VFD 4HP 13A HUANYANG CNC | eBay and it maxes out on PD 142 at 12 and the seller is telling me that I do not need to change pd 142 "
technical.jrs:
Dear Friend,
Thanks for your message!
The current depends on the working condition of the motor, the rated current is 13A for this inverter, but just like drving a car, the current will be changed when the inverter works, so you don't need to set PD142, you just set as this video:
http://vid1199.photobucket.com/album...ing18/--_0.mp4, and below steps:Step 1: Set PD005 =400
Step 2: Set PD004 =400
Step 3: Set PD003 =400
Step 4: Set PD072 =400
If you motor is 0-60HZ, then you need to change the above values to 60. As the orginal factory value setting is 50, so please change the the above parameters according to your motor.
Pls don't set PD142."
This is this biggest VFD I could find, I may return this but need a VFD that can actually give me 13 amps