Hello to all;
I have been testing again. I hope this info will help someone in the future trying to figure out the series / parallel wiring on the Vexta PH series 8 wire stepper. I think the doc is self explained, if you require help, or have any corrections, please tell me.
The following is also attached as a file for your downloading pleasure.
Wire diagram for the VEXTA PH268M-E1.5B by Ron Boeser, 07-12-2005.
General disclaimer; I tested these wire configurations using a ZETA4 drive (compumotor). All configurations listed were succesfull for a short run time. I would confirm by testing for many hours to confirm operation and overheating/ amp draw concerns. Please use at your own risk, I do not want to hear about burned up steppers or drives, it is YOUR choice to use this guide.
These are 8 wire steppers with the following wire colors:
Phase A:
Black ----
]coil
Black/White ----
Orange/White ----
]coil
Orange ----
Phase B:
Red ----
]coil
Red/White ----
Yellow/White ----
]coil
Yellow ----
Series configuration:
A+ = Black
A- = Orange
A Center tap = Blk/Wht + Org/Wht
B+ = Red
B- = Yellow
B Center tap = Red/Wht + Yel/Wht
Parallel configuration:
A+ = Black + Org/Wht
A- = Blk/Wht + Orange
B+ = Red = Yel/Wht
B- = Red/Wht + Yellow
All info contained herein was taken from the ZETA4 manual and a VEXTA diagram I scrounged from the web. Please copy and pass this info freely to help others along the CNC path.