    Phoenix Phase Converter Question

    Hi All
    I have a Bridgeport V2XT milling machine being fed by a Phoenix 10 hp RPC, the milling machine is operating eractily and part of the troubleshooting process is to check various voltages.

    L1 to L2 241 volts
    L2 to L3 251 volts
    L3 to L1 257 volts

    L1 to Ground 120 volts
    L2 to Ground 120 volts
    L3 to Ground 228 volts

    These readings were taken inside the milling machine electrical box. The milling machine has two transformers (T1 and T2) that feed various electronic controls and a 3 phase spindle motor . The milling machine is wired so the spindle motor gets L1,L2 and L3 and each transformer gets two legs. So T1 is fed from L1 and L2 and T2 is fed from T2 and T3. So the question is is the phase to phase balance out of spec and why is the L3 to ground so far out. Any advice ???

  2. #2
    Join Date
    Dec 2003
    Posts
    24216

    Re: Phoenix Phase Converter Question

    I Assume L1-L2 are the 240v single phase supply to the RPC, these are carried through to the 3ph termination to provide two of the phases.
    The readings to ground are normal and are meaningless, but any 1ph control transformer or supply fed from Anything but the two 240v 1ph input conductors can/will cause problems.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3

    Re: Phoenix Phase Converter Question

    I now see what you are talking about. I wonder if I could put both transformers on L1 and L2 , is there any downside to wiring it that way? I don't want to let any smoke out of the wires !!!!!

  4. #4
    Join Date
    Dec 2003
    Posts
    24216

    Re: Phoenix Phase Converter Question

    If the transformers offer complete isolation I don't see why you could not?
    Ensure that the source of the 240v 1ph (L1-L2) have adequate protection/fusing, wire size etc.
    Usually the only reason on the original equipment was to balance the 3 phases.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5

    Re: Phoenix Phase Converter Question

    1.What do you mean by isolation? 2. I will review the fuses,wire size etc and I agree with what you say about being balanced 3. I have had another crazy idea as well. What do you think if I just plugged the transformers directly into the 240Vac and arrange it so the spindle motor was wired to the Rotary Phase Converter. As I understand the wiring diagram the transformers are using 240ac any how and the control for the spindle motor is 24vdc. Thanks for the advice.

  6. #6
    Join Date
    Dec 2003
    Posts
    24216

    Re: Phoenix Phase Converter Question

    That is what I meant to place all the single phase transformers across the main L1-L2 240v (1ph) supply pair.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  7. #7
    Join Date
    Oct 2014
    Posts
    4

    Re: Phoenix Phase Converter Question

    you are having better luck then me but after contacting Phoenix I found out they have CNC balanced unite. PS don't do digital on a CNC .

  8. #8
    Join Date
    Jan 2005
    Posts
    15362

    Re: Phoenix Phase Converter Question

    Quote Originally Posted by sansushi View Post
    you are having better luck then me but after contacting Phoenix I found out they have CNC balanced unite. PS don't do digital on a CNC .

    What do you mean, Don't do Digital on a CNC
    Mactec54

  9. #9
    Join Date
    Oct 2014
    Posts
    4

    Re: Phoenix Phase Converter Question

    I meant stay away from static phase converters because when they fail it will burn up your motor .Phoenix is sending me a state of the art all new designed unite , when I get it next week ill let you know.Now they told me your voltage issue is normal and will work fine on a plane motor.

Similar Threads

  1. Replies: 24
    Last Post: 12-13-2017, 06:45 PM
  2. question...digital phase converter
    By magnum500sw in forum Phase Converters
    Replies: 2
    Last Post: 02-13-2013, 12:27 AM
  3. Hurco and phase converter question
    By jgr69ca in forum HURCO
    Replies: 2
    Last Post: 01-25-2009, 02:01 AM
  4. wtb: 20 or 30 hp phase perfect phase converter
    By gaugemate in forum Want To Buy...Need help!
    Replies: 0
    Last Post: 10-23-2008, 06:06 PM
  5. Phase Converter Question
    By bherr in forum Phase Converters
    Replies: 11
    Last Post: 11-02-2006, 07:02 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •