    Simodrive 611

    I have a BP Discovery 308 with a Simodrive 611. If I give a speed higher than 2500 rpm on the spindle the drive faults out. I can step up to 6k with no problem. Also when I run the machine for more than a few hours the drive will fault out when rapiding the Z back to home position. Some have suggested the caps in the drive power section need to be changed. Googling I find a gaggle of places that fix Siemens drives. Has anyone had some experience with any of the drive repair places? Or can you recommend a place to send the drive to?

    I'm in the midwest USA.

    Thanks
    John

  2. #2
    Join Date
    Oct 2008
    Posts
    44
    Open the cabinet door and check the fault code displayed on the spindle drive when spindle faults out.

    Before sending your Z drive for repair, I will suggest you to confirm whether it is the drive's problem, as Z ballscew bearing might cause the same. Again, check the code number displayed on Z drive when the alarm occurs. Also, you can swap Y, Z drive to confirm whether there's a problem with the drive. Swapping the drives doesn't need you to change any setting or parameter.

  3. #3
    Join Date
    Sep 2010
    Posts
    84
    Actually I don't suspect any problems with any of the axis drives but rather the AC to DC converter part.

    John

  4. #4
    Join Date
    Oct 2008
    Posts
    44
    if you mean the ER-module, i don't think it causes the problem.

  5. #5
    Join Date
    Nov 2006
    Posts
    925
    The ER module is the biggest problem with these drives,especially the early ones.If an early model loses a phase while enabled it will destroy it.
    Usually if the ER unit is a gonner nothing works.
    Check the dc link voltage on the busbars it should be about 660 dc.Get someone to monitor the voltage while you ramp the speed up.

  6. #6
    Join Date
    Oct 2008
    Posts
    44
    Quote Originally Posted by gridley51 View Post
    Check the dc link voltage on the busbars it should be about 660 dc.Get someone to monitor the voltage while you ramp the speed up.
    Should be around 600V, when you have 400-415V input voltage.

  7. #7
    Join Date
    Sep 2010
    Posts
    84
    Yes, I suspect the E/R module as the core problem. It seems the capacitors get old and you experience problems with a drop in power. Heck if I could source the capacitors I'd replace them myself. I think I checked the voltage but not under a load.

    Just checked and under normal conditions the DC buss was 601v at an overload jumped to 668v then fell down to 575v after enabling the drive it went back to 601v.

    I have 240vac mains and run off of a well balanced phase converter. My simodrive 611 in the lathe has no problems running at 0-6k spindle speeds and both run off of the same phase converter.

    John

  8. #8
    Join Date
    Nov 2006
    Posts
    925
    Quote Originally Posted by gridley51 View Post
    Check the dc link voltage on the busbars it should be about 660 dc.
    Apologies,pressed the wrong key twice.

Similar Threads

  1. Wanted,for Simodrive 610
    By Roberto1759 in forum Servo Drives
    Replies: 2
    Last Post: 02-10-2011, 09:51 AM
  2. Simodrive 611 Replacement
    By xclr82xtc in forum CNC Machine Related Electronics
    Replies: 0
    Last Post: 07-10-2010, 07:25 PM
  3. simodrive 610
    By Roberto1759 in forum Servo Motors / Drives
    Replies: 0
    Last Post: 02-10-2010, 11:06 PM
  4. simodrive 611
    By mixalisxat in forum Servo Motors / Drives
    Replies: 2
    Last Post: 04-02-2008, 07:37 AM
  5. Simodrive Problem
    By wanchai101 in forum Servo Motors / Drives
    Replies: 5
    Last Post: 07-25-2007, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •