    Q regarding line reactors

    So, I have a teknomotor spindle with a Hitachi WJ200 VFD and in conversations with the tekno rep, he was always pushing me to add a line reactor to the system saying that it will extend the longevity of the spindle by quite a bit and that just everything would be better. They don't distribute line reactors so I'm assuming he was being honest. A line reactor was only $100 so I picked one up.

    Question is on the wiring and mounting. I currently have the thing bolted to my work bench and it is not grounded. There is no separate ground lug on the transformer.

    Is this a disaster waiting to happen or am I ok with this setup? Do I need to make a grounded metal box for this and tie it to the chassis of the reactor or anything?

    TIA,
    -Andy B.
    http://www.birkonium.com CNC for Luthiers and Industry http://banduramaker.blogspot.com

  2. #2
    Join Date
    Dec 2003
    Posts
    24220
    I am assuming he recommended using it between VFD and motor?
    You should bolt it to a grounded chassis or enclosure or run a ground wire to it if you are leaving it bolted to your bench, which doesn't sound very safe?
    The ideal is close to the motor.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Dec 2010
    Posts
    634
    The upload photo thing wasn't working but here's a (lousy) picture of the setup.



    I could shorten the run to the spindle by about 3' maximum. I could also throw a ground wire from the wirenut to the reactor without too much difficulty. Finding an enclosure would be a bit more difficult but possible.
    -Andy B.
    http://www.birkonium.com CNC for Luthiers and Industry http://banduramaker.blogspot.com

  4. #4
    Join Date
    Dec 2003
    Posts
    24220
    The enclosure is up to how safe you feel, it does not affect the operation but your VFD and motor frame should have a ground conductor, the one you should have to the VFD would be closest to hook up to.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Dec 2010
    Posts
    634
    Yes, the motor and the VFD do indeed have a ground. You can see the green wire with the yellow wire nut next to the reactor - that comes from the 220 plug that feeds the VFD.

    I'll probably enclose it at some point.
    -Andy B.
    http://www.birkonium.com CNC for Luthiers and Industry http://banduramaker.blogspot.com

  6. #6
    Join Date
    Sep 2010
    Posts
    1765
    Quote Originally Posted by Al_The_Man View Post
    I am assuming he recommended using it between VFD and motor?
    Al.
    I can't tell from the pix if it is between the motor and vfd or on the 3ph input to the vfd..... would be good to know which it is....

    PS: wow, your website showing ur bandura's is neat!

  7. #7
    Join Date
    Dec 2003
    Posts
    24220
    I wondered, but when Andy mentioned shortening the run to the motor I assumed it was on the motor side.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    Dec 2010
    Posts
    634
    Yes, I'm running single phase 220v into the VFD. VFD 3phase out goes to the line reactor then to the spindle. I highly doubt that the 3 feet of length I can get rid of between the reactor and the spindle is going to make much difference at all.
    -Andy B.
    http://www.birkonium.com CNC for Luthiers and Industry http://banduramaker.blogspot.com

  9. #9
    Join Date
    Sep 2010
    Posts
    1765
    good enough. yes, 3' less length out of like 13 total will make no difference to anything.

    BTW, ur decision to add this inductor wasd good one; the spindle motor mfgr was 100% correct it will help cool ur spindle motor at any given load and it should extend the life of your motors insulation too. we use output reactors like this when we need to squeeze every ounce of power out of a given spindle motor. there is plenty of scope picture docs as well as temperature measurements that prove this helps - prob gets u another 8% power out the motor compared to same system w/o the output choke.

  10. #10
    Join Date
    Dec 2010
    Posts
    634
    I ran a couple hour job today and the spindle was noticeably cooler. Not that it got super hot before but, I have a stick on thermometer on there and it barely got off the second temp after several hours of running.

    I'm thinking it was $100 well spent.
    -Andy B.
    http://www.birkonium.com CNC for Luthiers and Industry http://banduramaker.blogspot.com

  11. #11
    Join Date
    Sep 2010
    Posts
    1765
    andy, please give us the rest of the data to complete the picture!!!!!!!!!!!!

    when we generally use an output choke, we get about 8% more (maybe 8% cooler motor than w/o it) - but we start with a vfd that has probably 100% smoother output current than these small vfds like u used!!!

    so how MUCH did it help on YOUR low cost wj200 vfd?? PLEASE give us the **BEFORE** temp from a similar job so we can the whole improvement!

  12. #12
    Join Date
    Dec 2010
    Posts
    634
    Hi Mike,

    I don't really have quantitative data on this but I do have a stick on thermometer on my spindle. When running a long job, my spindle temp sticker would start at around 40o C after 15 to 20 min and creep up from there hitting a maximum of around 50o C. Yesterday, It didn't make it past 45.

    Mind you, I'm not really loading the spindle too hard though either - I think if I was more aggressive with my cuts, it would probably make a bigger difference.
    -Andy B.
    http://www.birkonium.com CNC for Luthiers and Industry http://banduramaker.blogspot.com

  13. #13
    Join Date
    Sep 2010
    Posts
    1765
    andy, tnx a LOT for the feedback!

    keep in mind higher load should give similar PERCENTAGE improvement so ur data is GOOD!

    hmmm..... 45 vs 50 sounds like 45/50= 10% cooler! I know, I know, I am stretching it here with the data at hand.... but my past experience said like 8% cooler on really clean output pwm drive.... u r saying maybe 10% cooler gut feel on Hitachi XJ200 not as clean drive..... maybe it is really 12 or 15% cooler if you duplicated really close - or not... but in any case, it is all coming together than that output choke prob got u 10-ish% cooler motor performance and maybe added another few hours insulation life to it (lets see, 3 hours every 4 days x 20,000 nominal hour life plus another 1000 hours - not much to take to the bank probably).... everyone knows that a few degrees cooler on a thing will increase its life SLIGHTLY; there are definitive studies that will show the exact life increase of insulation based on x degrees cooler running - not much if small! so bottom line seems to me is 2 fold:

    1) adding inductor will increase ur motor life 0.00000001% or 20 minutes more out of 20,000 hour life design.
    2) it WILL let u cut with 10% more HP than before!

    Now which is more significant? Perhaps if u r still in contact with that mfgr u may want to relay ur experience back to them THIS way so they stop telling customers their spindle will last significantly longer if they put a choke on the output, but instead tell their customers they can get more torque out of it at a given cut!!!!!..............

    I apologize for my excitement, but as an engineer in this field I get mighty upset with mfgrs who spout nonsense.

  14. #14
    Join Date
    Dec 2003
    Posts
    24220
    The other advantage that you are going to get, and probably what your supplier was referring to but it is not immediately detectable, is the effect of reducing the high frequency harmonics imposed on the motor, which can reach fairly high voltages, this is often the cause of motor failure, vector rated motors are meant to alleviate the risk of winding damage also, but I would hazard a guess that most induction motors of any quality use same winding insulation.
    The inductive reactance of a choke increases with frequency, so that the lower operating frequencies pass through unsuppressed to a large degree. and the high frequencies fall under the effect of the higher inductive reactance.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  15. #15
    Join Date
    Jan 2006
    Posts
    2985
    A related line reactor question:

    I am in the process of hooking up a 25HP 460V VFD and motor. I am using a transformer to step up the available 230V to 460. Do I still want a line reactor on the line side of the VFD or does the transformer fill that role?

    Thanks
    Matt

  16. #16
    Join Date
    Sep 2010
    Posts
    1765
    the xfmr fills that role

  17. #17
    Join Date
    Dec 2003
    Posts
    24220
    You may want to consider one on the motor side, the input choke is generally used where the supply transformer is some remote distance away and other machinery is fed from it.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  18. #18
    Join Date
    Jan 2006
    Posts
    2985
    I plan to use one on the motor side as I'm not using an "inverter duty" motor. The transformer secondary goes straight to the drive with about 15-20ft of wire. The majority of the other loads are powered from the 230V prior to the transformer.

    Thanks for the help
    Matt

Similar Threads

  1. Replies: 3
    Last Post: 04-08-2011, 01:48 AM
  2. Line conditioners for CNC Equipment and poor line conditions
    By WSS in forum Waterjet General Topics
    Replies: 0
    Last Post: 01-14-2011, 03:07 AM
  3. Dm2400 Line By Line Execution????
    By andrewtub in forum Benchtop Machines
    Replies: 6
    Last Post: 01-26-2010, 05:28 AM
  4. Line Smoothing, point /line no identification
    By dz1 in forum Visual Basic
    Replies: 8
    Last Post: 12-15-2007, 12:03 PM
  5. line arc line
    By THE GREAT ONE in forum MetalWork Discussion
    Replies: 3
    Last Post: 01-23-2006, 09:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •