    Hitachi X200 to G540 - PWM speed control and run

    Needing a little reassurance on PWM speed control for a Hitachi X200 and a G540.

    The way I read this I can connect:
    G540 pin7 (ground) to terminal L on the VFD (Analog Ground)
    G540 Pin 8 (VFD Output) to terminal "O" on teh VFD (voltage Input)
    G540 Pin9 (VFD +10VDC) to terminal H on the VFD (10V Referance)
    set A001=01 (analog input as freq source)

    Plus I will use a G540 output and a relay to switch P24 and a programable input for Run.

    Am I close??

    Here are the diagrams.








    OUTPUTS: The G540 has two general purpose outputs called OUTPUT 1 and OUTPUT 2 on the MAIN TERMINAL BLOCK. They are at Pos 5 and Pos 6 respectively on the terminal block. These outputs may be used to drive relay coils or for any other purpose. The outputs are rated at 1A and 50VDC maximum. Connect one end of the load to the output and connect the other end of the load to a positive DC voltage. This voltage may be the G540 power supply or it may be a separate power supply having a different voltage.


    ANALOG OUTPUT: This is a 0V to +10V opto-isolated analog output intended for use with VFD drives. VFD OUT goes to 0VDC while the G540 is disabled. Connect VFD GND, VFD OUT and VFD +10V to the VFD drive inputs. Make sure the VFD drive positive voltage does not exceed +12VDC. Do not short VFD OUT to any other terminal. Do not reverse polarity to VFD GND and VFD +10V or the G540 may be damaged







    Please and Thank you
    Mikie

  2. #2
    Join Date
    Sep 2012
    Posts
    108
    can anyone confirm this is correct. I want to control my x200 fvd with gecko540/mach 3

  3. #3
    Join Date
    Sep 2010
    Posts
    1765

    none

    Quote Originally Posted by BloomingtonMike View Post
    Needing a little reassurance on PWM speed control for a Hitachi X200 and a G540.

    The way I read this I can connect:
    G540 pin7 (ground) to terminal L on the VFD (Analog Ground)
    G540 Pin 8 (VFD Output) to terminal "O" on teh VFD (voltage Input)




    set A001=01 (analog input as freq source)

    Plus I will use a G540 output and a relay to switch P24 and a programable input for Run.

    Am I close??


    Mikie
    NO -- DO NOT WIRE ANYTHING TO ETHEIR OF THESE PINS - NOT NEEDED AND IT WILL SHORT OUT THE HITACHI INTERNAL AND G540 THINGS +10V SUPPLIES TOGETEHR.. G540 Pin9 (VFD +10VDC) to terminal H on the VFD (10V Referance)

    MIKE you are very close, yes. i assume g540 has some kind of output that can supply +24v or sink it so you should not need a relay in between for the run command. but I know nothing of this g540 thing.

  4. #4
    Join Date
    Dec 2003
    Posts
    24220
    It looks OK to me, the VFD +10v analogue supply is used to supply the Gecko isolated PWM to Analogue convertor, H,O, & L).
    The relay Contact closure is used to switch P24 to the run input terminal.
    Presumably BloomingtonMike got it right as that was a year ago!
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Aug 2011
    Posts
    73
    Hi Mikie,

    Were your 3 connections b/w G540 & Hitachi inverter correct in the end?

    I have a WJ200 which is nearly identical and wanted to confirm before I power up.

    Cheers,

    Richard (Melbourne, Australia)

  6. #6
    Join Date
    May 2013
    Posts
    5

    Re: Hitachi X200 to G540 - PWM speed control and run

    I have a couple of questions. I have a copy of the wiring diagram above with the vfd drive wired to the G540. I have the two relays as shown, but I have no idea what the unit that is referred to in the diagram as Relay Power Supply is. Is it a relay, a power supply or what?. Also I have a KL 48v power supply in my G540 Control box ans a Separate vfd with its own power supply. Is it possible to run the inverter/vfd from the KL Power supply already in my G540 control box?

  7. #7
    Join Date
    Dec 2003
    Posts
    24220

    Re: Hitachi X200 to G540 - PWM speed control and run

    What do you mean by 'run the inverter/VFD from the G540/KL?
    What make of VFD?
    In most cases you can eliminate the VFD Run relay, I have a separate post on it.
    Al.
    .
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    May 2013
    Posts
    5

    Re: Hitachi X200 to G540 - PWM speed control and run

    Quote Originally Posted by lyjcncnuser View Post
    I have a couple of questions. I have a copy of the wiring diagram above with the vfd drive wired to the G540. I have the two relays as shown, but I have no idea what the unit that is referred to in the diagram as Relay Power Supply is. Is it a relay, a power supply or what?. Also I have a KL 48v power supply in my G540 Control box ans a Separate vfd with its own power supply. Is it possible to run the inverter/vfd from the KL Power supply already in my G540 control box?
    .

    To clarify, by "KL", I was referring to the 48v power supply in my G540 controller box. It is actually a Mean Well NES-350-48 7.3 amp supply.

    The VFD is a Dema:
    Model: D5M-1.5S2-1A
    Input voltage: Single-phase 220V/110V 50Hz
    Power (KW): 1.5KW
    Capacity of driver (KVA): 2.8
    Output current (A): 7.0
    Applicable motor (KW): 1.5

    VFD is using a RS485 communication interface.

    The VFD came with the Chinese 6040 CNC. As well as the VFD, the Chinese controller box also contained cheap stepper controllers. I bought the better G540, pre-wired in a controller box with a 48v power supply and E-Stop.

    What I would like to do is move the VFD from the old controller box to the G540 controller box and run the G540 and the VFD using a single power supply .

    My first question is "in the diagram the unit that is labelled "Relay Power Supply". Is it a relay or a power supply; or is it something else altogether"

    Question 2 is can I move the VFD to my G540 controller box and just use a single power supply.

  9. #9
    Join Date
    Dec 2003
    Posts
    24220

    Re: Hitachi X200 to G540 - PWM speed control and run

    You generally do not need any relay supply if using RS485 as all the control features are done via this method.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  10. #10
    Join Date
    Mar 2003
    Posts
    35538

    Re: Hitachi X200 to G540 - PWM speed control and run

    The G540 runs from the 48V power supply.
    The VFD needs 220V AC.
    You may be able to power the 48v supply from the same AC as the VFD.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  11. #11
    Join Date
    May 2013
    Posts
    5

    Re: Hitachi X200 to G540 - PWM speed control and run

    Quote Originally Posted by ger21 View Post
    The G540 runs from the 48V power supply.
    The VFD needs 220V AC.
    You may be able to power the 48v supply from the same AC as the VFD.
    My VFD is 110v/220v switchable; I have it set up to run from 110v.

    Also thanks to both you and Al_The_Man for your help.

Similar Threads

  1. HITACHI X200 settings
    By 15mgtar in forum DIY CNC Router Table Machines
    Replies: 99
    Last Post: 03-29-2015, 12:48 AM
  2. possible Problem with Hitachi x200 vfd
    By jayty97 in forum DIY CNC Router Table Machines
    Replies: 9
    Last Post: 09-18-2012, 08:08 PM
  3. Hitachi X200-022-NFU
    By kolias in forum Open Source CNC Machine Designs
    Replies: 0
    Last Post: 05-13-2012, 02:26 AM
  4. Hitachi X200 VFD Questoins
    By crane550 in forum DIY CNC Router Table Machines
    Replies: 1
    Last Post: 04-21-2012, 05:41 PM
  5. Hitachi X200?
    By fritts in forum Phase Converters
    Replies: 2
    Last Post: 12-27-2008, 04:06 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •