    3 phase 208 to 110 single transformer question.

    Hey guys I have another project Im working on in which I what to use the machines current 110V transformer to supply voltage to a DC PSU. The current transformer takes 2 legs off of 208V 3 phase and is wired to the terminals labeled "0" and "200" on primary side. On the secondary side is the wire are connected to "0" and "100". Now this transformer has 4 terminals on each side.

    Primary equals 0,20,200,240 and the secondary side has 0,10,100,120. Now the machine is using the 0 and 100 which I am assuming is 110V due to the +/- 10% tolerance. But my questions are:

    1. Is the terminal labeled "0" the Neutral/L2 for my signle phase circuits?

    2. Is there a way to find the nuetral verse hot using a multimeter with AC?>

    3. On this transformer with the machine using the "100" could I tap into the 120 for my 120VAc -24VDC power supply at the same time or are these type of transformer an either or deal?

  2. #2
    Join Date
    Sep 2010
    Posts
    1765
    1) sure
    2) there is not one
    3) confusing question but sounds like u r asking if u can power something requiring 120vac from the 100v side. sure

    there is no nuetral when u have 2 wires coming out of a transformer; just 2 wires. u can call one nuetral if u want, call it L1 or L2. whatever.

    reread and it sounds like u r not going to remove this xfmr from ur machine; just want to tap into it for 120v to feed a 24vdc power supply. so yes, just wire across the 100v side with 2 wires that go to the 120v input of your power supply. dont ground either, just hook them up and dont worry about n vs L noemclature.

    sometimes msch builders tie one side of 120v to machien ground, so if u care, yes, put ur meter from machine case or ground to each side of the 100v and see if one is 0 volts; if so it is the 'neutral' side. other would show 100 v to ground.

  3. #3
    Join Date
    May 2011
    Posts
    0
    Quote Originally Posted by mike_Kilroy View Post
    1)
    reread and it sounds like u r not going to remove this xfmr from ur machine; just want to tap into it for 120v to feed a 24vdc power supply. so yes, just wire across the 100v side with 2 wires that go to the 120v input of your power supply. dont ground either, just hook them up and dont worry about n vs L noemclature.

    sometimes msch builders tie one side of 120v to machien ground, so if u care, yes, put ur meter from machine case or ground to each side of the 100v and see if one is 0 volts; if so it is the 'neutral' side. other would show 100 v to ground.
    Thank you. But the question above was refering to the fact that the machine's transformer is using the 100V for its 110V devices,but this transformer obviously has the ability to output 10V,100V or 120V. I was asking if I left the transformer in the machine as is with the 100V wired, could I also tap into the 120V terminal as well or is this transformer such that you can only choose one voltage to use on the primary at a time. In other words could I tap 10,100 and 120V all at the same time without making the transformer off balance?And is it no problem with wiring a 120V devive to the transformer terminals rated at 100V?This is why I am asking this question to know if I need to use the 120V side and if I even can use it with the 100V wired up already at the same time?

    Also I have recently seen an instance where the nuetral was tied to equipment ground and it puzzled me coming from a DC world. DC is straight foward but with AC changing polarity I would think tying anything to it like a piece of equipment would fry you? Now I know the equipment is bonded to earth ground but lets say the earth ground connection in the plug came undone. Would you be getting zapped everytime you touched the machine? I mean I wouldnt stick a screw driver in a outlet but this is making me think I can as long as its in the nuetral side.Just Kidding.

  4. #4
    Join Date
    Sep 2010
    Posts
    1765
    now i get it, sorry. YES absolutely u can wire ur 120v load from 0 to 120 terminals while the 0 & 100v terminals are being used by the machine. there would only be 2 possible limitations:
    1) u cannot exceed the rated kva of the xfmr: so if the mach uses 80% of the rated kva for the 100v, then u can only pull ant=other 20% of its kva rating for your load; i assume ur 24vdc psu is small enough to not matter much?? maybe u should say what the xfmr kva rating is, what the 24v psu rating is, and maybe see if u can figure out the load on the 100v already - u can do this by a clamp on ac ammeter around one of its 2 output wires, or if less than 10 amps unhook on and put it thru ur dgital meter set to 10 amp ac current scale.
    2)if one side is grounded make sure ur 24v psu dont care.

  5. #5
    Join Date
    Sep 2010
    Posts
    1765
    didnt have time to finish my comment... no, if u loose ur grnd connection on machine plug, it does mean u will get shocked

    u need current to flow to get shocked. means u need to put urself in series with the voltage source; the ONE sire from the 100vac going to ground, then on to plug ground as u say, is NOT in series with the voltage. so if that ground wire at plug goes away, and u put urself in place of it by touching the machine whilst standing in puddle of water in barefeet, u are still not in series with the voltage; the voltage is from the 100vac terminal to the 0 v terminal, not from the 0 terminal to ground. to put voltage across u, u wud have to touch the 100v terminal and 0 terminal at the same time; altho u dont want to experiment and try to prove it, u could touch that 100v terminal whilst standing in the puddle and not get shocked IF that ground wire from machine to ground WAS off since there would (should) be no path for the voltage to flow current thru u (dont try this at home)

  6. #6
    Join Date
    Dec 2003
    Posts
    24216
    Just to expand on the grounded neutral, it is optional in the code that if you have a isolated control transformer, that it sounds like you have, it is optional whether you setup a grounded neutral, IOW re-reference the secondary to ground.
    When choosing which conductor you ground is purely optional as at that point they are totally identical.
    The conductor chosen to be earth grounded should be done right at the transformer and no where else.
    This terminal will be secured to chassis and a ground wire and a neutral conductor will be taken from this point and be the ONLY place where the neutral and ground conductor connection is made.
    As to using it without grounded neutral it is possible but there should be fusing in both secondary conductors as opposed to just one with grounded neutral.
    But if you are using the 100 and 120v tap then the '0' conductor would be the one to ground in that case.
    BTW, all ground and machine bonding conductors together with shields should go to a central ground 'star' point where the service ground should also be terminated.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  7. #7
    Join Date
    May 2011
    Posts
    0
    Thankx guys. Like I said Im from the DC world. Well amatuer DC world, where polarity is constant. AC with changing polarity like in this situation confuses me. In DC negative is ground ,period. But the term nuetral I never under stood because AC constantly changes polarity. So too me earth ground is negative. This may be incorrect but when I think ground I think negative. So with an AC circuit changing polarity I was thinking any connection of the AC circuit(hot or nuetral) to a grounded machine would cause a short because I thought even the nuetral changes polarity from negative to positive. This is what I thought with AC. You see my logic of why I thought I would get shocked? But your syaing nuetral does carry voltage at all untill the hot side(potential voltage source)is connected to ground or am I see looking at this all wrong?

    But are you guys saying there is no voltage on the nuetral wire? If I stand in a puddle and stick a fork in the nuetral side of an outlet I am okay,but its not untill I stick the fork in the hot side and become the nuetral(aka path to ground or least path of resistance) that I will get shocked,correct?

  8. #8
    Join Date
    Sep 2010
    Posts
    1765
    c ur logic but u r telling ur age....

    my first vw beetle was 6 volt POSITIVE ground!

    my ford 8N tractor was 6v POSITIVE ground up till 2009 when I changed it to 12v negative ground

  9. #9
    Join Date
    Feb 2007
    Posts
    505

    Cool

    Quote Originally Posted by Skiroy View Post
    Thankx guys. Like I said Im from the DC world. Well amatuer DC world, where polarity is constant. AC with changing polarity like in this situation confuses me. In DC negative is ground ,period. But the term nuetral I never under stood because AC constantly changes polarity. So too me earth ground is negative. This may be incorrect but when I think ground I think negative. So with an AC circuit changing polarity I was thinking any connection of the AC circuit(hot or nuetral) to a grounded machine would cause a short because I thought even the nuetral changes polarity from negative to positive. This is what I thought with AC. You see my logic of why I thought I would get shocked? But your syaing nuetral does carry voltage at all untill the hot side(potential voltage source)is connected to ground or am I see looking at this all wrong?

    But are you guys saying there is no voltage on the nuetral wire? If I stand in a puddle and stick a fork in the nuetral side of an outlet I am okay,but its not untill I stick the fork in the hot side and become the nuetral(aka path to ground or least path of resistance) that I will get shocked,correct?
    Be very carefull with the neutral, althought it is normally connected to ground ,if the neutral circuit is open you will get zapped if touching the neutral and ground.
    As far as your DC analogy, think of it as the neutral connected to ground , while L1 is going from 0 volts to +169volt peak to 0volt to -169 volts peak. (peak to peak values for 120vac )

    The neutral is carrying the same current as the L1 line as they are connected to both side of the transformer secondary.

    The number on your transformer primary and secondary are turns ratio more than voltage. If you use the 200 primary tap with 200volts you get 100v on the 100 secondary tap.In your case you are using 208volt on the 200 primary tap so you should get 104volt on the 100 secondary tap.

    hope this help.

  10. #10
    Join Date
    Dec 2003
    Posts
    24216
    Quote Originally Posted by Skiroy View Post
    AC with changing polarity like in this situation confuses me. In DC negative is ground ,period. But the term nuetral I never under stood because AC constantly changes polarity. So too me earth ground is negative. This may be incorrect but when I think ground I think negative. So with an AC circuit changing polarity I was thinking any connection of the AC circuit(hot or nuetral) to a grounded machine would cause a short because I thought even the nuetral changes polarity from negative to positive.?
    But are you guys saying there is no voltage on the nuetral wire? If I stand in a puddle and stick a fork in the nuetral side of an outlet I am okay,but its not untill I stick the fork in the hot side and become the nuetral(aka path to ground or least path of resistance) that I will get shocked,correct?
    The secondary of your 120v transformer Alternates in voltage polarity (AC) the current also reverses direction at a frequency of the supply, if you earth ground one of these conductors, nothing changes except the conductor that is grounded becomes, ideally, at the same potential as the planet earth and You, hence you do not sense anything when touching the neutral in spite of this 'alternating' voltage because there is (hopefully) zero potential between you and mother earth.
    The theory is that the earth consists of an homogenous mass that has zero resistance anywhere in its total area.
    The big problem I have with modern notation is that commons & grounds are used interchangeably without due indication as to what respective supply system it applies to and whether or not it is actual Earth Ground referred to??
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  11. #11
    Join Date
    May 2011
    Posts
    0
    I have read where there can sometimes be low voltage up to 40V on a nuetral but that depends on the substation. So is this why you can only tie your nuetral to ground at an "isolated transformer" to clean any stray voltage off the nuetral?


    Also I see a flaw in my fork in the nuetral side of the outlet scenerio. Assuming that the nuetral side is a clean 0V I see you wont get shocked because no voltage can make it to the nuetral as it is physically disconnected from the voltage source. But in my scenerio with the machine transformer is a loop because the machine's devices are in series with the transformer. So it makes the connection from the hot side of the transformer to the device as the conduit and back to the neutral side so I would expect electron to be present at the nuetral side of the transformer, meaning there should be electrons flowing into the machines metal casing because its tied to the casing. I dont know why Im having such a hard time with this.

    This to me would be like connecting a lightbulb to L1 and L2 and then touching the Neutral side(L2) on the lightbulb. Im still going to get shock because there is a load connecting L1 and L2 so the nuetral no longer is dead,voltage is now flowing through it and you will get shocked regardless of if you touch the nuetral or hot side at the bulb or at the voltage generator(this is of course assuming you are standing in a puddle and are grounded). PLEASE HELP THE FUZZY GO AWAY!:drowning:

  12. #12
    Join Date
    Dec 2003
    Posts
    24216
    Quote Originally Posted by Skiroy View Post
    I have read where there can sometimes be low voltage up to 40V on a nuetral but that depends on the substation. So is this why you can only tie your nuetral to ground at an "isolated transformer" to clean any stray voltage off the nuetral?
    See post #10.
    There should NEVER be any potential between neutral and earth ground. when the substation or supply transformer is grounded, in N.A. the neutral is re-referenced to ground at the service supply entrance, therefore if done correctly the neutral ground path should ideally have low ground path resistance back to the substation ground.
    The method of re-referencing an isolated control transformer is to re-establish a grounded neutral which otherwise would not be present due to the isolation effect of the transformer.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  13. #13
    Join Date
    Sep 2010
    Posts
    1765
    u r ready for the library! go take out a couple basic electricity books since u r ready to understand what they say! enjoy it.

    try this:

    SCENARIO 1
    ---------------
    define L1='hot', L2=neutral TIED TO GROUND IN YOUR CB PANEL AS IT SHOULD BE. Lite bulb from L1 to L2.

    A) u, grounded in puddle on feet, touch L1: shock. cuz it is 120v above ground.
    B) u, grounded in puddle on feet, touch L2: NO shock cuz it is 0v above ground.

    SCENARIO 2
    ---------------
    define L1='hot', L2=neutral **NOT** TIED TO GROUND IN YOUR CB PANEL AS IT SHOULD BE. Lite bulb from L1 to L2.

    A) u, grounded in puddle on feet, touch L1: shock. cuz it is 120v above ground Probably at your neighbors CB panel!
    B) u, grounded in puddle on feet, touch L2: NO shock cuz it is 0v above ground.

    SCENARIO 3
    ---------------
    define L1='hot' from isolation transformer (ur 100v secondary), L2=neutral of same xfmr and you did **NOT** TIE TO GROUND IN YOUR achine. Lite bulb from L1 to L2.

    A) u, grounded in puddle on feet, touch L1: no shock. cuz it is not referenced to ground so is 0v above ground.
    B) u, grounded in puddle on feet, touch L2: NO shock cuz it is not referenced to ground so is 0v above ground.


    SCENARIO 4
    ---------------
    define L1='hot' from isolation transformer (ur 100v secondary), L2=neutral of same xfmr and you did TIE TO GROUND IN YOUR achine. Lite bulb from L1 to L2.

    A) u, grounded in puddle on feet, touch L1: shock. cuz it is referenced to ground so is 100v above ground.
    B) u, grounded in puddle on feet, touch L2: NO shock cuz it is referenced to ground so is 0v above ground.


    ****OF COURSE THESE ARE ALL FOR THOUGHT -- DO NOT TRY THIS AT HOME!!!!!!!!!! *************

  14. #14
    Join Date
    Sep 2010
    Posts
    1765
    FOR kicks to get u to go get those books and start learning this fun stuff, what do you think would happen if you tie one side of your 60 watt lite bulb to HOT socket pin of 120v and other to ground rod? Would it light up? full or partial brightness?

    FOR kicks too, to get u to go get those books and start learning this fun stuff, what do you think would happen if you tie one side of your 60 watt lite bulb to plus terminal on car battery or even 100vdc power source, and other to ground rod, then tie the other side of the power supply to the earth ground of your wall socket? Would it light up? full or partial brightness?

    You'd be mighty surprised about these....

  15. #15
    Join Date
    Dec 2003
    Posts
    24216
    Quote Originally Posted by Skiroy View Post
    I have read where there can sometimes be low voltage up to 40V on a neutral but that depends on the substation.
    That aspect of grounding is where there is poor or unacceptable ground resistance, in this case a ELT Earth Leakage trip or Ground Fault Interrupter is used, the neutral is connected to ground rod or other means at the panel, the live and neutral are then taken through the ELT to the rest of the installation, now if a ground leakage occurs on the live conductor that because of poor conditions would not be sufficient to blow a fuse etc, the small unbalance or difference in current flow between live and the neutral is detected by the ELT and a trip occurs.
    This is a way of increasing the sensitivity of the ground detection.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  16. #16
    Join Date
    May 2011
    Posts
    0
    thankx guys. I love this forum. Very helpfull. Now what is the solution for humanity when this years solar storm hits?

  17. #17
    Join Date
    Feb 2007
    Posts
    505
    Quote Originally Posted by Al_The_Man View Post
    See post #10.
    There should NEVER be any potential between neutral and earth ground. when the substation or supply transformer is grounded, in N.A. the neutral is re-referenced to ground at the service supply entrance, therefore if done correctly the neutral ground path should ideally have low ground path resistance back to the substation ground.
    The method of re-referencing an isolated control transformer is to re-establish a grounded neutral which otherwise would not be present due to the isolation effect of the transformer.
    Al.
    A few years back , before the ground fault breaker became the norm, they had those small isolation transformer in the bathroom marked razor only (because of their low power capacity)
    They were safer than a normal outlet, you could touch either side of the lines and ground and be ok.
    The only way to get a hair rising experience was to touch both line at the same time.

    Grounding practice is mainly for safety reasons.

Similar Threads

  1. Replies: 12
    Last Post: 05-18-2015, 02:29 AM
  2. Convert three phase transformer to single phase?
    By jimjovan in forum CNC Machine Related Electronics
    Replies: 5
    Last Post: 09-16-2013, 11:32 PM
  3. Changing the transformer from single to three phase
    By carbidecraters in forum Fadal
    Replies: 1
    Last Post: 09-20-2007, 01:15 AM
  4. 3 phase transformer - on single phase?
    By zcases in forum CNC Machine Related Electronics
    Replies: 3
    Last Post: 10-21-2005, 04:22 PM
  5. 3 phase transformer on single phase?
    By jevs in forum CNC Machine Related Electronics
    Replies: 4
    Last Post: 03-19-2005, 06:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •