    Panasonic 3 phase driver running on 1 phase?

    Hi,

    I have some panasonic servo drivers model number MSDA043A1A

    I would like to wire them using a single phase supply, but from the model number I can tell these are meant for 3 phase supply. Panasonic tell me it is possible to use a single phase supply but will not tell me how to. I don't have the knowledge to work it out so I was interested to know if anyone has done this before and how do I go about it.

    I am in the UK and I have a 230-240v single phase supply.

    My servo has the connections L1, L2, L3 and ground.

    Many thanks

    Gav

  2. #2
    Join Date
    Jan 2006
    Posts
    2985
    If it is like most servo drives, the 3 phase is fed directly into a 3 phase bridge rectifier, where it gets turned into DC. If you simply connect your single phase to two of the wires, it should work fine. Some manufacturers recommend connecting one wire to L1 and the other wire to both L2 and L3. The paralleled paths lower losses a little bit so it will be a tad bit more efficient. Also on single phase you should reduce your max current a bit as single phase supply will have a much higher ripple voltage than three phase, with the same DC bus capacitance. I'd be surprised if the manual doesn't explain how to do it, most I have seen do.

    Matt

  3. #3
    Thanks Matt thats great info.

    How would I reduce the max current is this something I set within the drive (software)?

    Cheers

    Gav

  4. #4
    Join Date
    Jan 2006
    Posts
    2985
    I'm not sure how familiar you are with electricity. The AC is a sine wave that gets rectified into dc. You need capacitors to store energy so that in between the peaks of the AC sine wave, you still have DC power. The larger the current is, the faster these capacitors will discharge between peaks of the sine wave. If the capacitors discharge too much, it could actually fault the drive due to undervoltage. This should not harm the drive but might spoil whatever you are working on at the time. I think the manufacturers recommend going up something like 50% on rated current if you plan to use single phase. Capacitors cost money so they only put in enough capacitance to keep everything in spec with 3 phase power. The higher current rated drive has more capacitance so it handles the single phase power better.

    In reality I would say just use what you have and if you have no problems then smile. The drives I have used can monitor the DC bus voltage. If you can do this, you should be able to get a good idea of how you are doing.

    To answer your question, you can probably set the current limit in the drive. If you set it too low, you will loose torque on your motor, which could make the position error exceed limits and fault the drive. If you set it too high, the motor can draw too much current, cause the DC bus voltage to sag, and fault the drive. So either way if you push it too hard, you will fault the drive.

    What is the rated current of the motor and of the drive?

    Matt

  5. #5
    Join Date
    Jan 2005
    Posts
    15362
    gavztheouch

    For main Power Supply only use L1 & L3 for single phase

    You will have to wire the control power as well L1C & L2C
    Mactec54

  6. #6
    Join Date
    Nov 2008
    Posts
    147

    Re: Panasonic 3 phase driver running on 1 phase?

    so basically a 1 phase input should run a 10 amp motor with 15 amp rated driver?

  7. #7
    Join Date
    Jan 2005
    Posts
    15362

    Re: Panasonic 3 phase driver running on 1 phase?

    Quote Originally Posted by Johns tool room View Post
    so basically a 1 phase input should run a 10 amp motor with 15 amp rated driver?
    If the encoder plays niece that can work, if you have a phase lose alarm there is a way around that as well.
    Mactec54

  8. #8
    Join Date
    Jan 2013
    Posts
    474
    Quote Originally Posted by Johns tool room View Post
    so basically a 1 phase input should run a 10 amp motor with 15 amp rated driver?
    Possibly, but you need a big enough single phase supply and cable gauge size. The current draw may make the cable get hot or even fry supply wire insulation.

  9. #9
    Join Date
    Nov 2008
    Posts
    147

    Re: Panasonic 3 phase driver running on 1 phase?

    Quote Originally Posted by servtech View Post
    Possibly, but you need a big enough single phase supply and cable gauge size. The current draw may make the cable get hot or even fry supply wire insulation.
    3^.5 times bigger.

  10. #10
    Join Date
    Nov 2008
    Posts
    147

    Re: Panasonic 3 phase driver running on 1 phase?

    Quote Originally Posted by mactec54 View Post
    If the encoder plays niece that can work, if you have a phase lose alarm there is a way around that as well.
    what the relation between the encoder and power input to the driver? I'm not getting that. Please explain

  11. #11
    Join Date
    Jan 2005
    Posts
    15362

    Re: Panasonic 3 phase driver running on 1 phase?

    Quote Originally Posted by Johns tool room View Post
    what the relation between the encoder and power input to the driver? I'm not getting that. Please explain
    Some Servo Motor / Encoder has to recognize the drive they are being connected too, so if the motor size does not match the Servo Drive, they will not work, this is with most quality Servo Drives Motor combo, in your case it should work,

    As for cable the size is related to the Amps being used only so if the max amps is 10A, the correct wire size would be rated at 12.5A this is what code would require.
    Mactec54

Similar Threads

  1. 2 phase driver & 4 phase 6 wire stepper HELP!
    By mark in aus in forum Stepper Motors / Drives
    Replies: 2
    Last Post: 06-02-2009, 06:31 PM
  2. ? about vm-16 or vm-17 running single phase?
    By dccamp in forum Milltronics
    Replies: 3
    Last Post: 02-28-2009, 11:01 PM
  3. running off rotary phase converter
    By Joe Miranda in forum Milltronics
    Replies: 3
    Last Post: 04-14-2008, 03:19 PM
  4. Somewhat OT. running a three phase motor from DC?
    By fyffe555 in forum Phase Converters
    Replies: 9
    Last Post: 12-06-2006, 04:42 AM
  5. Running a VF-4 on a phase converter??
    By ZR Machine in forum Haas Mills
    Replies: 6
    Last Post: 11-02-2005, 02:04 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •