    Problems with a 480V three phase rotary air compressor

    Hi Guys,

    I’m having some problems with a 480V three phase rotary air compressor, the compressor keeps blowing a single time delayed fuse. I was performing a quick and dirty ohm test on the motor not sure what the coil windings resistance should be. Basically I tested each leg to earth ground my readings were, L1 and L2 were 1.5 ohms and L3 was 65 ohms. Does anyone know where I could find motor technical specifications?

    I know the resistance will be relative to horse power ratting voltage exedra.

    Also if a motor is rated 40 amps 480 volts does that mean 40 amps is the total draw of all three legs combined? So would the 40 amps be divided in to each leg? Knowing voltage and current draw per leg I could figure out the resistance with ohms law or somthing close.

    Thanks Eric,

  2. #2
    Join Date
    Dec 2003
    Posts
    24221
    You cannot get a meaningful resistance measurement between phases of a 3ph induction motor, the winding resistance will be very low, if you are getting any kind of resistance to ground then the motor has a problem, it should be very high or open circuit?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Apr 2010
    Posts
    294
    I'd expect each leg to run 40 amps.

  4. #4
    Join Date
    Dec 2003
    Posts
    24221
    And generally this is FLA , Full Load Amps so off load would be considerably less.
    The difference between each phase should be no more than a couple of %.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Feb 2006
    Posts
    338
    Sounds like you have to replace that motor.

    Something I found to help you determine if a motor is ok or what is wrong with it.

    How to check the Windings of a 3-Phase AC motor with an Ohmmeter
    http://www.aemc.com/techinfo/techwor...ech_megohm.pdf

    I havn't found a good referance for the actual values you should measure. I know it is partly because what is acceptable can vary a bit for different motors and motor types.

    I think you can usually use any isolated coil should read 0.1-9 ohms
    Any isolated coil to ground or another coil 500,000 to 1,000,000+ ohms

  6. #6
    Join Date
    Aug 2011
    Posts
    79
    On a three phrase motor usually there is a motor nameplate. That should give you some basic electrical info. What is the rating of the time delay fuse that keeps tripping? Also normally each phrase should be fused. Normally those fuses (3 ea) should have the same rating. FanFan

Similar Threads

  1. Rotary Compressor
    By slatern44 in forum Uncategorised MetalWorking Machines
    Replies: 3
    Last Post: 08-21-2018, 03:05 PM
  2. Phase Converter Sizing & Compressor
    By TravisR100 in forum Haas Mills
    Replies: 20
    Last Post: 08-03-2009, 02:01 PM
  3. CONVERT SINGLE 240/480V POWER TO THREE PHASE 415V OUTPUT
    By PhaseChangeConv in forum News Announcements
    Replies: 0
    Last Post: 09-03-2008, 05:45 AM
  4. rotary air compressor
    By omegaghost in forum I.C. Engines
    Replies: 5
    Last Post: 01-15-2007, 01:19 AM
  5. Rotary Phase converter problems
    By Gnome in forum Phase Converters
    Replies: 5
    Last Post: 06-15-2005, 03:43 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •