    Alarm 300 APC on Colchester Storm A-50 Fanuc 21i-T

    Hello all. I also posted in the colchester lathe section but notice a bit more activity in here.
    My lathe used to tell me when the batteries were low. But I converted from Lithium expensive to D cell affordable and I just lost the ref. positions.... Guess I'll just change the batteries every year from now on.
    Can anyone help me with the procedure to manual reference position return the axis?? Any help would be greatly appreciated.

    The controller


    Thanks in advance.

    Claude

  2. #2
    Join Date
    Apr 2008
    Posts
    211
    Ok, made some progress.
    I need to go to parameter #1815 and turn off the apc switch by entering 0 as a value in each axis.
    But it won't let me because it's write protected.... How do I turn off the write protected??

  3. #3
    Join Date
    Apr 2008
    Posts
    211
    Found how to get the write protect off.I found a procedure scribbled on the machine manual I got with the machine. Here is how it goes.
    Turn the write protect of by going into MDI mode and hitting the offset setting key until the setting soft key appears. Turn off by entering 1 as a value.
    Next, press systems key to get to the parameters screen, scroll to line #1815 and change values from 1 to 0 in both the x and z axis, turn off machine.
    Once turned on again, jog turret to soft stop on pos. z and pos. x. change paramater #1815 to 0 again and write protect on with the 0 value. Turn off machine.
    But I still get the 300 Alarm.(chair)
    Help!

  4. #4
    Join Date
    Apr 2005
    Posts
    79
    This may help

    Attachment 189566

  5. #5
    Join Date
    Apr 2008
    Posts
    211
    That looks great Bill! Thank you so much. I shall try that right now.

  6. #6
    Join Date
    Apr 2008
    Posts
    211
    WooHoo! I had to tweek a few things for it to work, but it worked! Am in production again!
    Thank you again Bill, you da man!
    :cheers:

  7. #7
    Join Date
    Jul 2015
    Posts
    1

    Re: Alarm 300 APC on Colchester Storm A-50 Fanuc 21i-T

    I have a Storm A50 and tried to use that pdf posted with this thread. What things did you tweek? When I enter the 00110000 into parameter 1815 it doesn't change the parameter even if I cycle the power off and back on. And when I used the suggested 1 000 000 (added spaces for readablity) as the overtravel values, I get a 309 APC ALARM: X Axis ZRN Impossible alarm. When I re-turned the write protect parameter back to 0 as the pdf instructed it didn't change the 1320 parameter to the new suggested value of 1 000 000.

Similar Threads

  1. colchester 2000l CNC not ready alarm
    By Hakam in forum Fanuc
    Replies: 10
    Last Post: 02-09-2017, 05:50 AM
  2. Colchester 2000L APC 310 and 320 Alarm
    By rjhzxc in forum Colchester Tornado lathes
    Replies: 2
    Last Post: 04-23-2014, 02:38 PM
  3. Alarm 300 APC on Colchester Storm A-50 Fanuc 21i-T
    By Nastyzen in forum Colchester Tornado lathes
    Replies: 1
    Last Post: 06-26-2013, 10:35 PM
  4. Replies: 2
    Last Post: 06-12-2013, 09:08 PM
  5. Clausing Colchester Storm CNC 100
    By CNC BOSS in forum Colchester Tornado lathes
    Replies: 2
    Last Post: 06-02-2012, 04:39 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •