    Fanuc Power supply module fault

    Hello guys.
    I am looking for a bit of guidance on a problem with an A06B-6120-H045 power supply module.Sometimes when I switch on the power isolator the power supply does not switch on (no led on)..Am I right to think that if the 240v input is there the led should light up and when the control is switched on the drives should enable.If this is the case what area of the PS should I be looking at for a fault
    Thanks
    Dean.

  2. #2
    Join Date
    Feb 2006
    Posts
    58
    There should be two breakers feeding your power supply, one is single phase, the other is 3 phase.
    Check the magnetic contactor first (sits between the 3 phase breaker switch and AC reactor).

    The manual below covers the full diagnostic steps that you should try, anything past that is usually a repair of IGBT transistors or something that should be done by a service tech.

    http://fanuc.pennineuk.com/library/pdf/AIMANUAL.pdf

  3. #3
    Join Date
    Aug 2011
    Posts
    33
    Thanks for your help.All voltages are present.I believe the PSM is faulty and will send for repair.
    Thanks again.

Similar Threads

  1. FANUC Alpha Series power supply input power limits
    By tcom-frazzled in forum Uncategorised MetalWorking Machines
    Replies: 0
    Last Post: 01-17-2012, 06:07 PM
  2. Alarms at power up, 320v power supply fault?
    By locash in forum Haas Lathes
    Replies: 5
    Last Post: 01-10-2012, 06:35 AM
  3. Fanuc Power Failure Module
    By w_kane in forum Fanuc
    Replies: 0
    Last Post: 07-15-2011, 02:04 PM
  4. Power Supply module for Colchester Tornado 200
    By egayzam in forum RFQ (Request for Quote)
    Replies: 0
    Last Post: 03-26-2011, 06:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •