    Hurco Hawk 30 - "Way lube oil low" error message

    Can anyone suggest any ideas!!!

    I have a Hurco Hawk 30 that has sat idle throughout the xmas break. On returning yesterday there is now an error message
    coming up on the console "Way Lube Oil Low; Enter machine diagnostics". The machine will run for a few minutes and then
    this message appears and locks up the console. Then we reboot and the same happens again. We thought we had resolved this
    by cleaning out the oil pump and bleeding the pipes, but it ran for 30mins and then same error message? The oil is topped up and
    there appears to be oil going into the tubes?

    If anyone knows how to bypass this error or if you have experienced this before and have a solution that would be much appreciated.

    Kind Regards

    Mark Newton

  2. #2
    Join Date
    Jun 2008
    Posts
    1103
    Is that NPE as in Wales NPE?
    Pop the old cabinet open and locate the card rack. Re-seat the board(s) that sit edge on with the big grey plugs on. You'll need to undo the little screws at each end and then pop the board outwards a few millimetres.

  3. #3
    Join Date
    Jan 2013
    Posts
    27
    Hello Bloke.

    No we are NPE in Havant down in Portsmouth.

    I have reseated the board with the big grey plugs on and re-booted the machine. Calibrated ok then started the warm up cycle
    which ran for around 2 minutes and then same way lube oil low message appears. Any other suggestions?

    Thankyou.

  4. #4
    Join Date
    Jun 2008
    Posts
    1103
    It sounds like you may have a power supply issue. Does the coolant randomly come on and or low air pressure messages?

  5. #5
    Join Date
    Jun 2008
    Posts
    1103
    It may be that the float switch in the tank is playing up. There are two pairs of wires in the tank power box. One pair is 115v AC supply and the other is to the float switch. Locate the float switch pair and short them together or open the circuit to see if the fault continues. If it does, it'll isolate the fault further.

  6. #6
    Join Date
    Jan 2013
    Posts
    27
    Hello

    No the coolant does not randomly come on and we do not get any air pressure messages? Just the way lube oil low message!

    I have an electrician here at the moment who is looking at various things, but he is not familiar with milling machines.

    He is checking all the connections to the pump are ok.

    The screen now is starting to play up and keeps rebooting in a loop. It eventually gets to the correct screen, but it takes a while.
    Could there be a hard drive issue?


    Is there anything else I can get him to look at.

  7. #7
    Join Date
    Jun 2008
    Posts
    1103
    Havant. I'm going to Qinetiq on Tuesday for three days. Nice place.
    I doubt it's a hard drive problem that's causing it to re-boot. That would normally give an 'Invalid system disk' fault. Have you had the sparky check the power supply voltages?

  8. #8
    Join Date
    Jan 2013
    Posts
    27
    Hello.

    Yes Quinetiq are about 10 mins away from us. We are really struggling here to solve this. The sparky is not really
    into these machines and is more of a mate just doing a favour. And I think he wishes he never bothered!!!

    If your in the area maybe you could pop in for a cup of tea!!

    Thanks

  9. #9
    Join Date
    Jun 2008
    Posts
    1103
    If you need to check the power supply, the test points are under the aluminium cover for the control box. There is a small board on the side that has five test points - one on its own which is 0v and then there are four together. Moving away from the 0v test point, they are -12v, 5v, 12v & 24v.

  10. #10
    Join Date
    Jun 2008
    Posts
    1103
    Thanks for the offer of a cuppa but I'm going to be really short on time - I have to retrofit a Nikken 4th & 5th axis to an older machine they have on site. It's going to be a tad manic finishing and getting back for my nipper's birthday on thursday.

  11. #11
    Join Date
    Jan 2013
    Posts
    27
    Hello

    The sparky has buggered off now. But before he left us he checked the voltage in the tank and it was 24v. But this was with the
    machine on, but the console not booted up. He traced the wires into the cabinet to a box whic has a blue "switch" that can be pushed
    in and out. When this is in the voltage measured 115v as you suggested. It seems to push itself out randomly and when it does the
    voltage drops. Could this be the problem that is causing the error message and screen booting problems?

    Thanks

  12. #12
    Join Date
    Jun 2008
    Posts
    1103
    No, I think the button you are pressing is on a contactor that supplies the servo drives. A thought, you mention that this has only started after powering it back up after a break. Is it quite cold in your shop? It may need the cabinet running back up to temperature to expel condensation if it's been left a while. If you have a fan heater, point it into the cabinet for ten minutes with the power off and try it again.

  13. #13
    Join Date
    Jan 2013
    Posts
    27
    Yes our factory is very cold, and we dont normally switch the machines off! as it causes problems!!!

    I have put the fan heater on as suggested. The machine fired up first time with no reboots. And I have performed 2 warm up cycles.
    I will keep testing the machine for a few hours and let you know the outcome.

    Thankyou very much for your help so far, especially at the weekend!

  14. #14
    Join Date
    Jun 2008
    Posts
    1103
    No probs, fella. Have a good weekend.

  15. #15
    Join Date
    Jan 2013
    Posts
    27
    Hello Bloke

    The machine is running back to normal now, and touch wood it will stay that way. Thankyou very much for
    all of your help and knowledge it is really appreciated. We are only a small business and just having one machine
    down can cause us delays, so thanks and I hope it goes well at quinetiq.

    Mark Newton

  16. #16
    Join Date
    Jun 2008
    Posts
    1103
    Glad it's stayed working.
    Just tickling the first pint of the night at the Premier inn/pub combo in Gosport. Qinetiq is going well so far...

Similar Threads

  1. "master encoder state error" AB ultra100 error message
    By ShapeShaver in forum Servo Motors / Drives
    Replies: 3
    Last Post: 07-31-2013, 04:09 PM
  2. Bridgeport Ez Trak SX - "No Cable" Error Message
    By sullivnc in forum Bridgeport / Hardinge Mills
    Replies: 3
    Last Post: 04-10-2013, 12:03 AM
  3. Replies: 2
    Last Post: 02-17-2013, 02:49 PM
  4. Replies: 3
    Last Post: 03-04-2012, 10:42 PM