Hello
I’m searching for plug connection for communication cable of Deckel FP4MA.
Greetings
Kickinger
Hello
I’m searching for plug connection for communication cable of Deckel FP4MA.
Greetings
Kickinger
HAAS VF7 - BJ2008<br />HAAS ST20<br />HAAS ST10 mit Stangenlader<br />HAAS Mikron VCE1000<br />EMCO 365<br /><br />www.KDC-Technik.at
Hello Mr. Kickinger
Which controller is it? Dialog4 or Contour3?
Pin
2 - TD
3 - RD
4 - RTS
5 - CTS
7 - Ground
What device do you have as a remote station? A PC with 9-pole gateway or another adapter?
Regards
Andreas Poggel
Andreas Poggel - industrielle IT<br />Wuppertal<br /><a href='http://www.industrielle-it.com' target='_blank'>www.industrielle-it.com</a><br />
Deckel FP 4 A with Dialog 11 at 9-pole.
I would additionally connect
25 - 9
4 - 8
5 - 7
To make a hardware handshake possible.
This cable would be for standard connection at PC (9-pole/DTE)
I always connected RTS/CTS (7 and 8 for 9 pol. SubD).