What you are concerned about is now that you have galvanic isolation between pri and sec you have no earth protection?
If the resultant DC supply from the secondary is referenced to earth ground, then if you connected the sec. (AC) winding to earth you would blow the DC power supply.
So, in most cases, either the AC sec. OR the DC supply common from that sec. can be earth grounded, (not both), if anything, it is usually the DC common that is grounded.
All earth grounds will preferably go back to a star point ground connection together with the service ground.
BTW, if using a P.C. the P.S. common is usually connected to earth GND in the P.C.