    208V 3ph machine on 240V 3ph?

    I have ran 3ph 208v motors on a 240v with no problems, but what about a entire machine with all kinds of PLC's and controllers runing on 240v instead of the 208v that it was made for, Will it be ok?

    Thanks
    Dennis

  2. #2
    Join Date
    Dec 2003
    Posts
    24221
    Alot depends on the individual system, for example some switching power supplies will run on 110vac to 240vac.
    Fanuc state ±10% and I have had to fit buck transformers to satisfy this.
    Every system requires evaluation, motors, like line-operated transformers are pretty durable and rugged.
    The bottom line is that anything over the manufacturers limit has to be assessed and if used over this, is a gamble.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Aug 2005
    Posts
    828
    Thank you for the input!!