    Angry 1040 Low Hydraulic Pressure

    This alarm seems to be permantly on, even on machine reset. It just started happerning. Can anyone help, its on a Fanuc 18T control.

    Machine is a hardinge Conquest T42.

    If you keep hold of reset the alarm goes, but the pump does not start up and the alarm returns on letting reset go

    pinguS

  2. #2
    Join Date
    Dec 2003
    Posts
    24216
    I would think you need to find out what is preventing the pump from comming on?
    Is it a fuse or contactor overload require resetting?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Mar 2006
    Posts
    167
    Where do I start? I am not familiar with this machine but, does the pump run? If not check fuses/breakers. If it runs, does the pressure reach the required level on the pressure gauge? If not, is the motor actually driving the pump. Often motors will shear the drive keys/splines or the pressure relief may be stuck open. If all of the above checks out ok, I would suggest that it is a problem with the pressure switch itself.

    regards, Oz

  4. #4
    Join Date
    Jun 2007
    Posts
    119
    Alarm "Low Lubr. Pressure- Cycle intrerupted" Fanuc O-TD
    If you keep hold of reset the alarm goes.Can anyone help

  5. #5
    Pingus

    check the Hyd. motor Running or not, if not running check the Electrical side first. If Motor is running check the Drive to pump & check the pump output. if pump output is ok, check the Pr. switch wires & pr. switch function.

    viorel26
    check the above sequence for Lube motor

  6. #6
    Join Date
    Dec 2003
    Posts
    24216
    Quote Originally Posted by viorel26 View Post
    Alarm "Low Lubr. Pressure- Cycle intrerupted" Fanuc O-TD
    If you keep hold of reset the alarm goes.Can anyone help
    this can depend on how the lube system is set up, some lube pumps run intermittently and are expected to trip a pressure switch within a certain time span, others run while the machine is in auto/start, so this set up would probabally require the press. sw. seen all the time.
    In both cases, check both Lube pressure and P.Switch.
    It is probabally a PMC input so it can be checked on the diag or ladder screen.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.