    Am I Wiring this right? i have pictures.

    I'm Excited to use my new VFD. although I'm stuck at something that might be very simple.
    there is no ground wire on the UVW side of my VFD. the manual says this for the grounding section.

    3.2.2.6 : Grounding Terminal : " Do not share the grounding terminal with zero line of power supply."

    i have no idea what that means so im scared to share the ground thats going in on my single phase power side.

    i have some images. any help would be appreciated. Thanks!


    Attached Thumbnails Attached Thumbnails IMG_1030.jpg   IMG_1032.jpg  

  2. #2
    Join Date
    Dec 2003
    Posts
    24220

    Re: Am I Wiring this right? i have pictures.

    You should ground the frame of the motor to the service ground provided, this should be the same as the earth terminal on the power entry point.
    The +/PB is a brake resistor terminal.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Jan 2016
    Posts
    33

    Re: Am I Wiring this right? i have pictures.

    thanks i will try it.

  4. #4
    Join Date
    Jan 2005
    Posts
    15362

    Re: Am I Wiring this right? i have pictures.

    Quote Originally Posted by a3dcreator View Post
    I'm Excited to use my new VFD. although I'm stuck at something that might be very simple.
    there is no ground wire on the UVW side of my VFD. the manual says this for the grounding section.

    3.2.2.6 : Grounding Terminal : " Do not share the grounding terminal with zero line of power supply."

    i have no idea what that means so im scared to share the ground thats going in on my single phase power side.



    i have some images. any help would be appreciated. Thanks!


    In this case the ( 2 ) Grounds can connect to the same Ground Terminal, or if you can find a place on the Heat sink of the VFD that has a place to mount the Ground wire, this can even be on the mounting foot of the VFD, just make sure it has a good contact, if you did it this way, remove paint or any anodizing from the Heat sink, set your parameters correct for your spindle
    Mactec54

Similar Threads

  1. wiring check please. parallel wiring to maximum current to servo motors
    By Novett in forum CNC Machine Related Electronics
    Replies: 3
    Last Post: 10-11-2014, 07:54 PM
  2. g0704 wiring pictures
    By kuyote in forum Benchtop Machines
    Replies: 9
    Last Post: 01-26-2014, 07:42 PM
  3. SX2/SC2 LMS Spindle Control Board Wiring (with pictures)
    By Nine8Six in forum Benchtop Machines
    Replies: 1
    Last Post: 08-24-2012, 05:38 PM
  4. Electronics Enclosure pictures/wiring and fusing
    By ahaidet in forum Benchtop Machines
    Replies: 8
    Last Post: 11-16-2011, 02:52 PM
  5. Need help wiring motor to driver and controller - pictures included
    By ltovey in forum DIY CNC Router Table Machines
    Replies: 2
    Last Post: 06-09-2011, 08:53 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •