    Apparent issue with SJ200 & Leeson 3ph 2HP motor

    Hi All,

    Prior to the recent holidays, I acquired a Hitachi SJ200-022NFU (capable of accepting 1 and 3 ph line power) and a Leeson 2HP 3ph 3400RPM motor.

    I have 240 1ph service into the shop via a subpanel breakered at 60A at the main panel. Until now, the breaker feeding the subpanel has never tripped.

    I connected the line and load wiring precisly as defined in the manual (2 legs of the 240 line power going to L1 and L2 and neutral going to the N/L3 lug while the VFD to motor connection is U to U1, V to V1, and W to W1). I also have the chassis ground of the motor connected to the chassis ground of the VFD. As my line power receptacle does not currently have a ground lug, I left the line side of the VFD ungrounded. I'll get a ground wire and appropriate recptacle prior to actual install and operation.

    After double checking my connections, I plugged the power plug into the wall socket and shop immediately went black. None of the local subpanel breakers tripped, but the the 60A breaker did. This was an instantaneous, do not pass go event.

    I have since looked over everything again, and all connections seem to be preceisly as they need to be. I have checked for shorts in all of my cables and plugs--all are as prescribed. I also checked the 240 circuit and everything checks out voltage wise.

    I am stumped and unsure what to do next. I'm reluctant to plug it in again because I have changed nothing since the trip. I could sure use some advice. I am definitely out of my element here.

    Thanks,

    David

  2. #2
    Join Date
    Dec 2003
    Posts
    24220
    I have never heard of connecting a VFD up with the neutral when using 1 ph, I think if you check the manual, the L1 & L3 is used for the 240vac, you may need to jumper the L1 & L2 terminals, Also Do you have a jumper in place now?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Oct 2003
    Posts
    43
    Well... that would explain my problem wouldn't it. I feel absolutley stupid.

    There is indeed a jumper between L1 and L2 and I heartily questioned that--the idea of connecting the two legs of 240 across the jumper defied my understanding of what made sense. But the docs are quite clear that the Jumper must be in place... and I have opinions about people who blindly follow along without questioning. Duhhh...

    And indeed I did not intepret the instructions to hook the 2nd leg to N/L3. There were no examples for connecting 1ph power. I did just reread the docs and it does indeed say (in bold no less):

    "...for single phase power, terminal [S/L2] will remain unconnected." Now it makes sense.

    One final question then: Is the neutral connected to anything? Or does it just float?

    Thanks for your attention Al. You have answered hundreds if not thousands of questions here, and I'm quite certain that we all greatly appreciate the energy and knowledge you so generously share.

    Thanks!!!

    David

  4. #4
    Join Date
    Jan 2005
    Posts
    15362
    Hi you sure do have a problem you my have fryed the drive as well
    The L1 & L3 are what you have to use for your single PH 240 input
    L2 you do not connect any thing to it

    Some drives L1 can be jumpered to L3 but I'm not sure with your drive
    Yaskawa you can

    The neutral was one of your problems as you created a dead short
    and do not jumper L1 & L2 that to could be a dead short

    You can use the Neutral as a ground wire if you do not have a ground but put some green heat shrink on it

    Do not run the drive without a ground to the power source you are just
    asking for trouble or Electrocution I'm surprised that AL The Man did not say
    this by wiring this way you made your whole machine live with no Ground to
    protect you.
    Mactec54

  5. #5
    Join Date
    Oct 2003
    Posts
    43
    Mactek,

    Thanks for your response.

    Seems like what you and Al said are in contradisction. L1 and L2 have a jumper. As I said in my second post, the docs do say "L2 will remain disconnected".

    Anyone else withan SJ200 powered with 1ph?? How did you connect it???

    Thanks,

    David

  6. #6
    Join Date
    Dec 2003
    Posts
    24220
    Quote Originally Posted by mactec54 View Post
    You can use the Neutral as a ground wire if you do not have a ground but put some green heat shrink on it

    Do not run the drive without a ground to the power source you are just
    asking for trouble or Electrocution I'm surprised that AL The Man did not say
    this by wiring this way you made your whole machine live with no Ground to
    protect you.
    I did not allocate using without ground, but you do NOT use neutral as a ground wire, ever, this violates the E.Code.
    In fact you do not use neutral at all in VFD installation.
    The manual states using L1 & L3 for the 240v 1ph. The L1 & L2 are jumpered to allow a bit of extra DC capacity on 1 ph.
    The ground is connected in the usual way to the ground lug.
    By having a short circuit across the 240v, you probabally blew the breaker before any damage was done.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  7. #7
    Join Date
    Oct 2006
    Posts
    36
    Connection of the L1 and L2 with a jumper is unnecessary, it gives you no "extra capacity" since all the AC input does is provide the raw power for conversion to DC. The capacity of those 2 diodes will be greater, but the total input capacity is still dictated by the other 1/2 of the circuit anyway, so it makes no difference. They recommend making that jumper connection just to satisfy the people who insist on connecting wires to unused terminals, PRECISELY so that they are not compelled to connect the neutral! Now that you have, you most likely blew the input diodes, i.e. your drive is toast. Sorry for the bad news. The only possible saving grace is if by some miracle, the breaker cleared before the diode popped. Highly unlikely though. In that world, breakers are painfully slow.

  8. #8
    Join Date
    Oct 2003
    Posts
    43
    Thanks Al,

    Understood and thank you. I'll hook it up tomorrow and let all know if the breaker did the additional job of protecting the unit.

    Regards,

    David

  9. #9
    Join Date
    Jan 2005
    Posts
    15362
    Hi I did type it wrong and I changed it to L1 & L3 for these Hitachi drives should be connected for 240 V single PH and AL you can use any wire you want as long as it is correctly colored or marked so it is clear what that wire is, this does not Violate any codes.Also as J Raef has said you do not have
    to jumper L1 & L2 for it will have no gain

    Yaskawa VFD Drives are L1 & L2 for single PH
    Mactec54

  10. #10
    Join Date
    Dec 2003
    Posts
    24220
    The blocking action of a 3 phase bridge should cause no conduction from live to neutral if a neutral was so connected to a phase input.
    My point about the ground was that you violate the code if you use the neutral as a ground.
    The system neutral should be only grounded at source, and this applies to local supplies where a local neutral is set up.
    The only reason I mentioned the link was to quote the manual for David's information.
    It probabally does not matter what pair you use, as the input usually enters to a 3 phase bridge, the alternative is where there is a 1 phase ac control source connected to a particular pair.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  11. #11
    Join Date
    Oct 2003
    Posts
    43
    Hi all...

    I went to the shop and hooked up everything from scratch, with the two legs of my 1ph 240 to L1/L2 (jumpered) and L3. I clipped and wire-nutted the neutral wire. I also ran a dedicated wire from the VFD ground to Earth ground. The 3ph motor is hooked up as previously stated (U,V & W plus ground).

    I plugged the VFD in and... (drum roll) the breaker tripped again.

    So unless anyone has any other thoughts, I suspect I cooked the VFD. I think I'll call Hitachi tomorrow, bare my soul, and see what can be done.

    Thoughts???

    Thanks again,

    David

  12. #12
    Join Date
    Dec 2003
    Posts
    24220
    Doesn't sound good, try powering up without the motor connected, just to confirm if it is the supply input problem.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  13. #13
    Join Date
    Dec 2005
    Posts
    390
    I have exactly the same configuration as you... well except I have a real ground. Please see the attached image to see how it is configured. I did not change any jumper. There is a jumper installed but on the second row of terminals - you can see the jumper on pg 2-19 of the manual and in the picture. I hope you find there is nothing wrong with your VFD.
    Attached Thumbnails Attached Thumbnails IMG_4146a.JPG  

  14. #14
    Join Date
    Oct 2003
    Posts
    43
    Hey Wildcat and Al,

    Well, this continues to be a damnable and humbling experience. I work with tech stuff every day, and I have never so misread (maybe not read is more apt) a manual as I have this one from Hitachi.

    I was going back through the manual, looking at diagrams, and suddenly began to question what I was calling L1, L2, and N/L3.

    Then Wildcat simultaneously posted his picture and served up my second helping of humble pie in as many days.

    To make a short story as short as possible, I was using the second row of lugs, not the first. I read the schematic to mean that the 1st row was used for 3ph input and the 2nd row for 1ph input. Now, I realize that is rather lame reasoning on my part, but that is what I did. I now see that the top row is for braking. If I could find a smiley that fits in here I'd use it, but they're all way to understated to fit the situation.

    I must say though, no where does the manual say to leave the Neutral wire disconnected from the VFD. I'm happy te eat my 3rd helping if someone can show me where it is. Here's the URL to the manual:

    http://www.hitachi.us/supportingdocs...ok_NB650XA.pdf

    So, the first opportunity I have to get back to the shop, I'll hook this thing up again and see what happens. Hopefully I didn't burn something out hooking it up to the braking circuit.

    Seriously, thanks for all of your help and best wishes.

    David
    Attached Thumbnails Attached Thumbnails SJ200 Schematic.jpg  

  15. #15
    Join Date
    Dec 2005
    Posts
    390
    David - hey, just cause mine is working does not mean there were not initial problems That manual is THICK and you are right, there is not much (is there any?) information on hooking the VFD up to single phase power. Somehow I did notice the warning on the side that said to be sure to check the model number... turned out I was initially sent a -002 instead of a -022... Hmm, think a 1/4HP VFD would drive a 2HP motor? Anyway, best of luck. Be sure to go through the programmable variables and set them appropriately for your motor. VFDs are really pretty amazing beasts.

  16. #16
    Join Date
    Dec 2003
    Posts
    24220
    You are going to be very lucky if you haven't fried the Braking circuit.
    I would hook it up the CORRECT way without the motor connected and see if any fault codes come up,
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  17. #17
    Join Date
    Oct 2003
    Posts
    43
    Hi All,

    Just a quick post to bring you up to date on the status of my VFD. I connected the unit (CORRECTLY) without the motor connected (the two legs connected to L1 & L3, no neutral connection, and the ground lug connected to earth.

    The unit did not light up at all, and I got a small puff of magic smoke.

    I'm certain I've cooked this thing. I'm going to contact a repair facilty for an estimate of the cost to repair. I won't be surprized if the cost is close to the actual cost of the unit. If you have a thought on this, I'd be happy to hear it.

    I'm fairly disgusted with myself, but I'm beyond anything more than a shake of my head and writing a check for another one. Expensive lesson, but one well earned. Ha... that was supposed to be learned, but I think earned is equally apt.

    Thanks for your help and patience!!

    David

  18. #18
    Join Date
    Dec 2005
    Posts
    390
    Oh man real sorry to hear this. Good luck with the repair quote. I'd be inclined to just get another one... after holding back a tear or two. FWIW, I got mine from Automation4Less which, at least at the time, had the best deal going that I could find. Also, I am a little uncomfortable about turning the VFD on without the motor attached. I could swore I read in the manual not to do this but couldn't find it the other day. I might just be misremembering the warning about placing a switch between the VFD and motor.

    Quote Originally Posted by haysys
    I'm certain I've cooked this thing. I'm going to contact a repair facilty for an estimate of the cost to repair. I won't be surprized if the cost is close to the actual cost of the unit. If you have a thought on this, I'd be happy to hear it.

  19. #19
    Join Date
    Dec 2003
    Posts
    24220
    Quote Originally Posted by wildcat View Post
    Also, I am a little uncomfortable about turning the VFD on without the motor attached. I could swore I read in the manual not to do this but couldn't find it the other day. I might just be misremembering the warning about placing a switch between the VFD and motor.
    I think thats what you are alluding to, is that it is not recomended to remove and apply power to the motor in the motor leads.
    Its Ok If you power up a VFD as long as you do not connect a load when power is on.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  20. #20
    Join Date
    Mar 2007
    Posts
    196

    Sweating in Atlanta

    I too have a Leeson 2HP motor and an Hitachi SJ200-015NFU VFD sitting on my workbench ready to install. The description of the mistakes made has me re-reading everything in the manual and sweating bullets! Wow, these are really poor instructions for wiring with single phase 240V! Actually, there really isn't a wiring diagram at all for 1 ph.

    So if I have this right, with my 4 wire 240 line, the red(or black) goes to L1, the second hot wire goes to L3, the green to the grounding lug on the VFD chassis, and the white wire goes to NOTHING. Is this correct? Is it advisable to connect L1 and L2 with a "jumper" or not?

    Also, should the motor chassis be grounded back to the VFD chassis ground lug as well?

    Thanks,

    Bill
    Atlanta

Page 1 of 2 12

Similar Threads

  1. Issue at low power....
    By WilliamD in forum Laser Engraving / Cutting Machine General Topics
    Replies: 2
    Last Post: 12-02-2006, 06:44 AM
  2. Homing Issue
    By Moondog in forum Machines running Mach Software
    Replies: 3
    Last Post: 07-30-2006, 04:23 AM
  3. Help with selector switch wiring issue (***actually a motor issue***)
    By BEDFORD in forum Charter Oak Automation Support Forum
    Replies: 7
    Last Post: 04-07-2006, 09:19 PM
  4. Parallel Relay Board & Z-motor brake issue
    By Liv2fish2 in forum DNC Problems and Solutions
    Replies: 0
    Last Post: 02-06-2006, 06:35 PM
  5. THC Issue
    By Aldoseri in forum CamSoft Products
    Replies: 3
    Last Post: 01-31-2006, 11:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •