    Question problem with Huanyang 4kw vfd

    Hi
    i have a problem with my 4kw VFD with is a 4kw 18000rpm spindle
    i can fine get the spindel to 18000 rpm and 300hz
    but if i set the mach3 to 9000 rpm the the vfd is showing 174.5hz and not 150hz
    and i have measured the pwm signal to 5v

    now i have use two days and i cant find the error

    /kenneth

  2. #2
    Join Date
    Jan 2005
    Posts
    15362

    Re: problem with Huanyang 4kw vfd

    Quote Originally Posted by tkoc View Post
    Hi
    i have a problem with my 4kw VFD with is a 4kw 18000rpm spindle
    i can fine get the spindel to 18000 rpm and 300hz
    but if i set the mach3 to 9000 rpm the the vfd is showing 174.5hz and not 150hz
    and i have measured the pwm signal to 5v

    now i have use two days and i cant find the error

    /kenneth
    What Parameters have you set in the VFD Drive

    What is your spindle spec's

    Max RPM=
    Amps=
    Voltage=
    Max Hz=
    Mactec54

  3. #3
    Join Date
    May 2010
    Posts
    2

    Re: problem with Huanyang 4kw vfd

    spindle
    Voltage: 220VAC
    Current: 10A
    Frequency: 0-300Hz
    Speed: 0-18000rpm

    PD001=1
    PD003=300
    PD004=300
    PD005=300

    PD007=20

    PD008=220
    PD009=15
    PD010=8
    PD011=40
    PD014 Accel=12
    PD015 Deccl=12
    PD141=220 ( Motor Rated Voltage )
    PD142=10
    PD143=2
    PD144=3000

  4. #4
    Join Date
    Jan 2005
    Posts
    15362

    Re: problem with Huanyang 4kw vfd

    Quote Originally Posted by tkoc View Post
    spindle
    Voltage: 220VAC
    Current: 10A
    Frequency: 0-300Hz
    Speed: 0-18000rpm

    PD001=1
    PD003=300
    PD004=300
    PD005=300

    PD007=20

    PD008=220
    PD009=15
    PD010=8
    PD011=40
    PD014 Accel=12
    PD015 Deccl=12
    PD141=220 ( Motor Rated Voltage )
    PD142=10
    PD143=2
    PD144=3000
    Is your Spindle Air cooled or Water Cooled ???


    PD014= you seem to have a high setting for this normally you can go as low as 3 so anywhere from 3 and up should work fine

    PD015= you seem to have a high setting for this normally you can go as low as 3 so anywhere from 3 and up should work fine


    Jumper J1 also must be set for Remote Control This is located next to the Terminal Block


    PD002=1

    PD011=120 Not 40 this is below the minimum speed for your spindle

    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )

    PD72=300

    PD73=120

    PD120=120 (Stall Prevention )

    PD174=?? ? ( Your VFD Drives Max Amp Output Rating )
    Mactec54

  5. #5

    Re: problem with Huanyang 4kw vfd

    Way pd 144 =3000 ist this max rpm of motor?

  6. #6
    Join Date
    Jan 2005
    Posts
    15362

    Re: problem with Huanyang 4kw vfd

    Quote Originally Posted by Velikivrh View Post
    Way pd 144 =3000 ist this max rpm of motor?
    Yes that is the max setting for that Parameter PD144=3000=Max Spindle RPM what ever it is
    Mactec54

Similar Threads

  1. Huanyang inverter problem cooling fan does not run
    By tenmetalman in forum Spindles / VFD
    Replies: 2
    Last Post: 12-27-2015, 05:51 PM
  2. 10hp huanyang VFD problem
    By 78sharpshooter in forum Spindles / VFD
    Replies: 3
    Last Post: 04-16-2015, 07:44 PM
  3. Huanyang Inverter Problem
    By icanoe in forum Community Club House
    Replies: 0
    Last Post: 03-15-2013, 01:35 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •