I bought a VMC 800 22 with a TNC370 control. It had problems with the toolchanger. I found the cause was a bad output from the control. I edited the PLC to use another output and rewired the relay to it. Now it all works great... except I had to change parameter mp4010 to 1 so i can run the PLC from RAM.
This is the first time Ive used this control, so Im not sure how this part really works. But I've been using this technical manual for the tnc 360 https://www.yumpu.com/en/document/vi...n-dr-johannes- .
It walked me through everything else but it says running the PLC from RAM is only for testing and it should be transferred to eprom when you are done. It says to do that you will need a pc and "MEGA PROMMER software (version 2.12 or later)" . I'm not sure where to find that, I contacted Heidenhain and they say they cant help me.
Anyone know anything about MEGA PROMMER or how to write to the eprom on this control? Or failing that does anyone know what problems running the PLC from RAM might cause? I shut the power off overnight and it remembered my changes so it must have a battery somewhere.
Thanks