    Post Sizing a circuit breaker for my servo drive.

    Hi,

    This is a newbie question about sizing my circuit breaker.

    I have a servo drive I need to size a circuit breaker for.
    The information on the side of the servo drive is:

    Rated current: 3.8 A rms
    Instantaneous Max current: 12.2 A rms

    Which size circuit breaker should I choose for it?

    Thank you so much in advance.

  2. #2
    Join Date
    Mar 2007
    Posts
    2083

    Re: Sizing a circuit breaker for my servo drive.

    you need to ask a local electrician but

    I would expect a 4A MCB is too close to the 3.8A and would choose a 6A breaker
    to avoid nuisance tripping use a type C or possibly type D breakers instead of the more usual type B

    Click image for larger version. 

Name:	Protecta - Type B Distribution Boards.pdf 
Views:	0 
Size:	291.0 KB 
ID:	383894

    John

  3. #3
    Join Date
    Mar 2017
    Posts
    411

    Re: Sizing a circuit breaker for my servo drive.

    You might think about using a fuse instead of a breaker. An inline slow blow fuse could be a better choice than a breaker. They are smaller, and you can more readily make changes to the size or type of fuse. I would recommend starting with a 3 Amp Slow blow fuse. If that blows then change the fuse.

    Also, it would be a good idea to measure the amount of current that is drawn under load. The numbers printed on the servo are probably worst case and, depending on your design, you may not want to put that much power into the servo. Only put as much power into the system as the weakest link. For example, you may be driving your load through a coupler with a tiny shaft diameter and secured with a small setscrew. If you load up the system and then apply maximum power you will surely spin the coupler on the shaft and the setscrew will carve a nice groove all the way around.

    Finally consider voltage. Make sure that your circuit protection is rated at or above the maximum voltage.

    Good luck.

Similar Threads

  1. YASKAWA AC SERVO and SERVOPACKS circuit breaker sizing and IP44 cable
    By graupnerhansen in forum CNC Machine Related Electronics
    Replies: 0
    Last Post: 04-17-2017, 09:56 AM
  2. ac servo drive sizing
    By suppermaxxin in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 11-23-2015, 04:00 PM
  3. alarm 24 circuit breaker on a FR-SF drive
    By Captdave in forum Mazak, Mitsubishi, Mazatrol
    Replies: 1
    Last Post: 06-06-2013, 12:45 PM
  4. Servo Drive Sizing
    By GEMorris in forum Servo Motors / Drives
    Replies: 14
    Last Post: 07-20-2006, 01:00 AM
  5. Help with Sizing a servo drive.
    By Fabric8r in forum CNC Machine Related Electronics
    Replies: 2
    Last Post: 10-28-2005, 07:56 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •