    Earthing spindle on Yuhuan VFD

    Hi folks,
    I am finally getting around to installing my Yuhuan VFD to my chinese, 1.5kW, water cooled spindle.

    I have watched numerable YouTube tutorials on the subject but still feel uneasy with the installation. In all of the tutorials that I have seen, the spindle has 4 terminals but mine has just 3 on the Aviation plug at the spindle.

    I am aware that the power to the spindle must be through screened cable and I have the requisite length of 3 core cable with a braided screening layer over it. I have checked that there is no electrical connection between the phase pins on the 'Aviation' plug fitted (which is good) and that there is continuity between the Aviation socket and the spindle body.

    What I had in mind was to fit a 3 pin aviation plug into the base of the VFD with the pins connected to the three phase connections on the VFD wiring panel and the ground terminal to be connected to the body of the Aviation socket. Then, ground the braiding of the cable to the plug using the cable clamp fixture on the plug.

    What I need to know is should I also ground the braid at the spindle end too, or would this give me problems with a 'ground loop' bearing in mind that the body of the spindle would also be grounded by this method?

    Perhaps I am looking at it from the wrong perspective and hope that one of you more knowledgeable types can give me guidance.

    Thanks in anticipation.

  2. #2
    Join Date
    Dec 2003
    Posts
    24220

    Re: Earthing spindle on Yuhuan VFD

    If you have good earth bonding of the various machine sections, for e.g. earth wire from a moving gantry back to the star point etc.
    In all the years of fitting VFD's I have never used screened cable, in fact when VFD's first came on the scene there was no such thing aimed at this application.
    I have always used flexible metalic conduit to the spindle which by its nature is grounded both ends, the MTW/TEW wiring used was three conductors twisted together with the earth conductor ran along side them.
    This has never ever been a problem for me.
    You should find a point on the motor frame in order to use a ground wire point if non is supplied by the manuf..
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Mar 2003
    Posts
    35538

    Re: Earthing spindle on Yuhuan VFD

    Flexible metallic conduit is not an option on a machine where the spindle moves, which is 99% of the machines using these spindles.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  4. #4
    Join Date
    Dec 2003
    Posts
    24220

    Re: Earthing spindle on Yuhuan VFD

    One of the points i was making though is that
    What I need to know is should I also ground the braid at the spindle end too, or would this give me problems with a 'ground loop' bearing in mind that the body of the spindle would also be grounded by this method?
    is the chance of ground loop is removed by a suitable earth wire to motor frame, then both ends of any shielding can be connected to earth..
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Jan 2005
    Posts
    15362

    Re: Earthing spindle on Yuhuan VFD

    Quote Originally Posted by Pader View Post
    Hi folks,
    I am finally getting around to installing my Yuhuan VFD to my chinese, 1.5kW, water cooled spindle.

    I have watched numerable YouTube tutorials on the subject but still feel uneasy with the installation. In all of the tutorials that I have seen, the spindle has 4 terminals but mine has just 3 on the Aviation plug at the spindle.

    I am aware that the power to the spindle must be through screened cable and I have the requisite length of 3 core cable with a braided screening layer over it. I have checked that there is no electrical connection between the phase pins on the 'Aviation' plug fitted (which is good) and that there is continuity between the Aviation socket and the spindle body.

    What I had in mind was to fit a 3 pin aviation plug into the base of the VFD with the pins connected to the three phase connections on the VFD wiring panel and the ground terminal to be connected to the body of the Aviation socket. Then, ground the braiding of the cable to the plug using the cable clamp fixture on the plug.

    What I need to know is should I also ground the braid at the spindle end too, or would this give me problems with a 'ground loop' bearing in mind that the body of the spindle would also be grounded by this method?

    Perhaps I am looking at it from the wrong perspective and hope that one of you more knowledgeable types can give me guidance.

    Thanks in anticipation.
    What you where planning to do would work well, just make sure the exposed Ground wire is as short as possible, at the spindle end, if that's what you are going to do, Braid on the outside of the cable is not recommended, and you need a 4 core any way 3 Hot and Ground Plus shield, IGUS is an ideal place to get good cable, there part number is

    You can not create a Ground loop if you wire everything correctly

    https://www.igus.co.uk/

    This is 16 Gauge Numbers you can use 18 Gauge for your 1.5Kw Spindle

    CF35-15-04

    CF31-15-04
    Mactec54

  6. #6
    Join Date
    Jul 2010
    Posts
    22

    Re: Earthing spindle on Yuhuan VFD

    Quote Originally Posted by mactec54 View Post
    What you where planning to do would work well, just make sure the exposed Ground wire is as short as possible, at the spindle end, if that's what you are going to do, Braid on the outside of the cable is not recommended, and you need a 4 core any way 3 Hot and Ground Plus shield, IGUS is an ideal place to get good cable, there part number is

    You can not create a Ground loop if you wire everything correctly

    https://www.igus.co.uk/

    This is 16 Gauge Numbers you can use 18 Gauge for your 1.5Kw Spindle

    CF35-15-04

    CF31-15-04
    The picture shows the connection end of my spindle with just 3 pins in the Aviation connector. The black metal cap, body of the spindle and the aviation connector body all have electrical continuity and so I cannot see where a 4th conductor would connect.

    In one of the videos that I watched, the maker chose not to connect the ground wire to the motor and the motor functioned perfectly. Am I correct in thinking that the spindle motor is a brushless motor similar in design to those used in model aircraft and do not have a ground connection?

    The cable that I have has 3 cores enclosed in a pvc sheath with a closely wound steel wire braiding about it. The whole cable originally had a heavy pvc sheath around it but this I removed because it considerably stiffened the cable making it too stiff for use even inside the cable chains that I am using on my machine for all wiring. I am considering coating the braid with silicone to keep the braiding in place when it flexes.

    The braiding outer diameter is just the right size to clamp tightly in the body of the aviation plug providing earth continuity from the body of the spindle all the way through to another aviation plug/socket at the VFD with the body of the socket connected directly to earth on the VFD main panel block.

  7. #7
    Join Date
    Jul 2010
    Posts
    22

    Re: Earthing spindle on Yuhuan VFD

    I am thinking that what you advocate is functionally achieved by what I have written in reply to Mactech54 above. Am I correct?

  8. #8
    Join Date
    Jul 2010
    Posts
    22

    Re: Earthing spindle on Yuhuan VFD

    I would not dream of using flexible conduit in the circumstances that you suggest. I do use it to route cabling on non-moving parts but if they were required to flex often, would result in the spiral casing unravelling. What I am suggesting for use is 3 core flex with a steel wire braiding completely about the cable which will enable sufficient flexure.

  9. #9
    Join Date
    Jul 2010
    Posts
    22

    Re: Earthing spindle on Yuhuan VFD

    Quote Originally Posted by Al_The_Man View Post
    If you have good earth bonding of the various machine sections, for e.g. earth wire from a moving gantry back to the star point etc.
    In all the years of fitting VFD's I have never used screened cable, in fact when VFD's first came on the scene there was no such thing aimed at this application.
    I have always used flexible metalic conduit to the spindle which by its nature is grounded both ends, the MTW/TEW wiring used was three conductors twisted together with the earth conductor ran along side them.
    This has never ever been a problem for me.
    You should find a point on the motor frame in order to use a ground wire point if non is supplied by the manuf..
    Al.
    Shielding was recommended to me by the guy from which I have bought most of my equipment. He said it is essential to prevent RF interference to nearby equipment and that he installs it on all of his machines for sale including high end industrial machines. Thank you for your contribution though.

  10. #10
    Join Date
    Jan 2005
    Posts
    15362

    Re: Earthing spindle on Yuhuan VFD

    Quote Originally Posted by Pader View Post
    Shielding was recommended to me by the guy from which I have bought most of my equipment. He said it is essential to prevent RF interference to nearby equipment and that he installs it on all of his machines for sale including high end industrial machines. Thank you for your contribution though.
    Shielding is a no brainer, it is a code requirement in some countries

    Because you only have 3 Pin Spindle Plug, your best choice, is to remove the spindle plug, and add a cable restraint like in this photo, for this you remove the top of the spindle and wire everything direct, the shield would then be grounded by the cable restraint, and your Ground wire connected like the photo, it is important to get the correct cable restraint gland as some are not for Grounding the Shield

    Like this https://hollandshielding.com/EMI-RFI-cable-entry-glands
    Mactec54

  11. #11
    Join Date
    Jan 2005
    Posts
    15362

    Re: Earthing spindle on Yuhuan VFD

    Here is another supply for the Cable Restraint Gland, just cut and paste this and it will open as a PDF file, it was too big to down load here

    file:///D:/EMF%20Shield%20Grounding/CORD_GRIP_CATALOGUE.pdf
    Mactec54

Similar Threads

  1. Practical star earthing
    By robrollings in forum CNC Machine Related Electronics
    Replies: 5
    Last Post: 01-09-2016, 11:48 PM
  2. Insulating transformer earthing/Driver Earthing
    By Cware in forum CNC Machine Related Electronics
    Replies: 3
    Last Post: 09-27-2014, 10:47 PM
  3. Earthing rod installation
    By Simonh1959 in forum Hypertherm Plasma
    Replies: 6
    Last Post: 02-11-2013, 04:18 PM
  4. Why earthing laserengraver ?
    By froggygeorge in forum Laser Engraving / Cutting Machine General Topics
    Replies: 5
    Last Post: 02-15-2011, 11:50 AM
  5. earthing problem - help
    By neurofen in forum CNC Machine Related Electronics
    Replies: 27
    Last Post: 01-22-2011, 04:18 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •