    Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    So I just received two 400W DYN4 driver and motor sets to convert my SX3 mill from steppers. I connected everything per the manual on the bench to test it out and make sure all the wiring is correct but as soon as I power it on with the motor connected to the driver within 5 seconds the drive goes into a fault and on the program it shows it as Overcurrent. If the motor is not connected to the driver and I turn the driver on it works just fine with no faults.
    I connected both sets in all possible pairs to eliminate a potential bad component in either system but I got the same behavior from both sets.
    Again, everything is brand new with brand new cables, all ordered from CNC4PC. What am I doing wrong?
    I am connecting to single phase 220V. Tomorrow I will try with 120V but I have a feeling that is not my problem. The manual says either a bad encoder cable or an excessive load on the motor. The motors were just sitting on the bench so no load whatsoever. Both encoder cables are brand new.

    Any suggestions or ideas?

  2. #2
    Join Date
    Dec 2013
    Posts
    5716

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    What is the part numbers on your Drives and Motors?
    Jim Dawson
    Sandy, Oregon, USA

  3. #3
    Join Date
    Mar 2015
    Posts
    9

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by Jim Dawson View Post
    What is the part numbers on your Drives and Motors?
    I can't see them right now as I am not home but this is what I ordered if it helps for now: https://cnc4pc.com/dmm-dyn4-servo-kit-400w-at-200v.html

  4. #4
    Join Date
    Dec 2013
    Posts
    5716

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    It looks like the set you ordered is properly matched, but confirm that the motors are 640-DST-A6HS1 motors. I would send an email to DMM tech support. They are very responsive. [email protected]


    Jim Dawson
    Sandy, Oregon, USA

  5. #5
    Join Date
    Mar 2003
    Posts
    35538

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    When I ordered from CNC4PC, they sent me a 60V motor by mistake, so make sure you have the right motor.

    And you have to be careful when using 240V. DMM recommends a line reactor before the drives.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  6. #6
    Join Date
    Jan 2005
    Posts
    15362

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by jivkom View Post
    So I just received two 400W DYN4 driver and motor sets to convert my SX3 mill from steppers. I connected everything per the manual on the bench to test it out and make sure all the wiring is correct but as soon as I power it on with the motor connected to the driver within 5 seconds the drive goes into a fault and on the program it shows it as Overcurrent. If the motor is not connected to the driver and I turn the driver on it works just fine with no faults.
    I connected both sets in all possible pairs to eliminate a potential bad component in either system but I got the same behavior from both sets.
    Again, everything is brand new with brand new cables, all ordered from CNC4PC. What am I doing wrong?
    I am connecting to single phase 220V. Tomorrow I will try with 120V but I have a feeling that is not my problem. The manual says either a bad encoder cable or an excessive load on the motor. The motors were just sitting on the bench so no load whatsoever. Both encoder cables are brand new.

    Any suggestions or ideas?
    One thing to check is the Servo Drive, you could have the wrong one for that motor, for 400w servo motor, the Servo Drive needs to be DYN4-L01A-2-00

    If this is correct how are you running it, which software are you using and what settings are you using, you may well be over driving the motor, and this will give you this same fault
    Mactec54

  7. #7
    Join Date
    Mar 2015
    Posts
    9
    Quote Originally Posted by Jim Dawson View Post
    It looks like the set you ordered is properly matched, but confirm that the motors are 640-DST-A6HS1 motors. I would send an email to DMM tech support. They are very responsive. [email protected]


    So I just checked and the motors are PN 640-DST-A6HK1. The drivers are PN or model DYN4- L01 A2 00.

  8. #8
    Join Date
    Mar 2015
    Posts
    9
    Quote Originally Posted by mactec54 View Post
    One thing to check is the Servo Drive, you could have the wrong one for that motor, for 400w servo motor, the Servo Drive needs to be DYN4-L01A-2-00

    If this is correct how are you running it, which software are you using and what settings are you using, you may well be over driving the motor, and this will give you this same fault

    That seems to be the correct PN. I am connecting after a magnetic contractor as described in the manual.

  9. #9
    Join Date
    Dec 2013
    Posts
    5716

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    I think it's time for an email or call to DMM tech support. They'll be open in about an hour.

    http://www.dmm-tech.com/contact.html
    Jim Dawson
    Sandy, Oregon, USA

  10. #10
    Join Date
    Jan 2005
    Posts
    15362

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by jivkom View Post
    That seems to be the correct PN. I am connecting after a magnetic contractor as described in the manual.
    You should not be using a magnetic contactor, it should be a MCCB which is a Molded Case Circuit Breaker

    Do you have a line reactor to prevent the in rush over voltage plus the power filter on the Control Logic Power Circuit

    You did not say what software you are using to run the motor

    Does this happen when you go to run the Servo motor, Or does this happen on Power up
    Mactec54

  11. #11
    Join Date
    Mar 2003
    Posts
    35538

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    The manual shows an MCCB, followed by a magnetic contactor, labeled MC1.
    And it says your Estop should kill the contactor coil.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  12. #12
    Join Date
    Dec 2013
    Posts
    5716

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by mactec54 View Post
    You should not be using a magnetic contactor, it should be a MCCB which is a Molded Case Circuit Breaker
    The manual specifies both a MCCB and a mag contactor

    Here is an in-process picture of my setup. I bench tuned all four motors yesterday with no problems with the exception of a minor misunderstanding of the Enable input function wiring which was quickly resolved by tech support.

    Jim Dawson
    Sandy, Oregon, USA

  13. #13
    Join Date
    Mar 2015
    Posts
    9
    Quote Originally Posted by mactec54 View Post
    You should not be using a magnetic contactor, it should be a MCCB which is a Molded Case Circuit Breaker

    Do you have a line reactor to prevent the in rush over voltage plus the power filter on the Control Logic Power Circuit

    You did not say what software you are using to run the motor

    Does this happen when you go to run the Servo motor, Or does this happen on Power up
    I’m using the DMM software, latest version downloaded from their website last night.

    This happens within a few seconds after powering the driver when the motor is connected to the driver or within seconds of connnecting the motor to the driver of the driver is already powered. It’s definitely the connection to the motor that triggers the fault, without even trying to drive it to move.

  14. #14
    Join Date
    Mar 2015
    Posts
    9

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Just got off the phone with DMM. They said it might be a firmware mismatch. I had to email them a picture of the plates to see the serial numbers. Hopefully it's something simple to resolve.

  15. #15
    Join Date
    Jan 2005
    Posts
    15362

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by jivkom View Post
    Just got off the phone with DMM. They said it might be a firmware mismatch. I had to email them a picture of the plates to see the serial numbers. Hopefully it's something simple to resolve.
    Do you have the servo motor connected directly to the Drive, No switches or any other connections between the motor and the Drive

    It does sound like something is a not a match, and could well be the firmware in the Servo Drive is a mismatch for the Servo Motor you are using

    Disconnect the servomotor at the Drive and try a power up
    Mactec54

  16. #16
    Join Date
    Mar 2015
    Posts
    9

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by mactec54 View Post
    Do you have the servo motor connected directly to the Drive, No switches or any other connections between the motor and the Drive

    It does sound like something is a not a match, and could well be the firmware in the Servo Drive is a mismatch for the Servo Motor you are using

    Disconnect the servomotor at the Drive and try a power up
    Correct, directly connected to the drive with brand new cables from DMM.

    The drive powers up and stays on with no faults without connecting the motor to it.

  17. #17
    Join Date
    Jan 2005
    Posts
    15362

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by jivkom View Post
    Correct, directly connected to the drive with brand new cables from DMM.

    The drive powers up and stays on with no faults without connecting the motor to it.
    It seems then that it has the wrong firmware is installed or could even be just the wrong label was put on the drive

    Check the wiring A B C is correct before you try the motors again

    Just try with ( 1 ) servo motor connected, if it faults on power up, then check the other motor to see if it does the same, if it does it would be a good indication the drives are not for the motors you have

    Something else to check is the A B C connection of the servo Motor to Drive these have to be correct if ( 1 ) phase is not wired correct you can have this problem also so check there wire color spec's match the A B C connection

    Blue is A Phase

    Red is B Phase

    Black is C Phase

    These must be wired correct

    Ground connected to your Ground Plane, or Star Ground
    Mactec54

  18. #18
    Join Date
    Mar 2015
    Posts
    9

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    All resolved. Wrong firmware.

  19. #19
    Join Date
    Dec 2013
    Posts
    5716

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by jivkom View Post
    All resolved. Wrong firmware.
    Is the firmware user updatable?
    Jim Dawson
    Sandy, Oregon, USA

  20. #20
    Join Date
    Mar 2015
    Posts
    9

    Re: Brand new DYN4 400W set - goes in Overcurrent fault as soon as motor is connected

    Quote Originally Posted by Jim Dawson View Post
    Is the firmware user updatable?
    It's more configurable rather than upgradeable.

Page 1 of 2 12

Similar Threads

  1. DYN4 1.8KW Servo Motor
    By Vinnito1 in forum Dmm Technology
    Replies: 11
    Last Post: 03-25-2019, 03:11 AM
  2. DMM Dyn4 & 1KW AC Servo motor reliability & quality
    By Marty_Escarcega in forum Dmm Technology
    Replies: 3
    Last Post: 06-27-2017, 03:01 PM
  3. Eathtek 400W spindle motor
    By ProtoXNH in forum DIY CNC Router Table Machines
    Replies: 0
    Last Post: 12-04-2016, 02:52 PM
  4. AC motor connected to Raspberry Pi
    By schitale in forum Servo Motors / Drives
    Replies: 0
    Last Post: 01-02-2014, 07:55 AM
  5. What free servo controller used for brush DC motor 400W ?
    By Qwerfk in forum Open Source Controller Boards
    Replies: 7
    Last Post: 01-10-2013, 05:18 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •