    Hi Guys,
    Me and my dad is building a Milling and Plasma Table.
    The milling Part works fine.
    I am running Mach3. I have connected up the relay as in photo attached but as soon as we turn on our 3 phase plasma cutter the relay blows( I test the relay by removing the signal wire and touching the ground, before the plasma blows it it clicks when touching ground, after it is blown I do the same but only the light goes on. if I power of the 5v and back up it clicks then only).
    It blows the relay and Mach3 says limit switch triggered. (I'm guessing the faulty relay causes that).
    Can you guys please help as this is our only issue left. I hope before the machine is complete.
    24221
    Re: Plasma blows relay..........!!!!WHY
    Is it the contact side that blows?
    If so it is most likely that you are overloading the contact rating or a short circuit/high load develops to blow it.
    What load are you switching?
    Max.
    Albert E.
    Mar 2018
    22
    Is there a way to check what side is bowed? I will have to check the load tommorow. We are using a 3-phase plasma machine
    24221
    You could energize the relay but disconnect the load side, and if you have a meter, see if there is continuity across the output.
    Al.
    Albert E.
    Mar 2018
    22
    Thanks, I will test. Is my wiring correct as on photo? And is the limit switch triggered error from relay blowing
    Mar 2018
    22
    Al.
    Load is to much yes, is there a bigger relay we can use on mach3 to activate the plasma
    24221
    Find out the actual load and size a relay accordingly, you may find it hard to find one rated for 5vdc coil.
    If so you could use a 2n7000 Fet and a 12v -24v relay.
    See PDF.
    Al.
    Attached Files Attached Files
    Albert E.
    Mar 2018
    22
    We spoke to the people where we are purchasing the plasma. they said the relay will be fine. I think it is another issue. I am getting 24v out of all my output ports on mach3.....is this normal? so my signal pin to turn relay on and of has 24v on. I have my V+ (on Mach3 board) running to the V+ on my power supply. Then I have V- (on mach3 board) running GND (where my wall plug runs to on power supply) because there is no V- on the power supply only a COM connection.
    When I connect up my relay with a 5 v power supply I test it by touching the int 1 pin to a GND wire then it opens. Must it not touch a V+ to open?
    24221
    The output from the PC port should be 5vdc maximum, not sure where the 24v would be coming from?
    Unless you have some external wiring mistake!
    Al.
    Albert E.
    Mar 2018
    22
    Yes we have a extra 24v power supply for limit switches and estop
    Mar 2018
    22
    This is my wiring diagram
    24221
    That would be 24v supply common, not earth ground.
    There should be a separate earth ground terminal on the input of the P.S. for the service GND.
    Al.
    Albert E.
    Mar 2018
    22
    or can I ground it on the body where all the other grounds are? It is currently on the the earth on the power supply. Any idea why my relay switches on when i touch my signal wire to the ground. As I understand it must open when i touch the 5v......but it shorts out when i touch the 5v
    Mar 2007
    2083
    is this how your machine is wired?
    Attachment 395086
    your diagram of the arduino relay does not have the "snubber " across the relay contacts (100 ohm resistor in series with 0.1uF)
    the "snubber" helps to reduce the arc as the relay opens
    assuming all of your power supplies have no connection between the output and the supply ground
    the connection shown between the work piece and the 24V negative can explain why touching a wire from the relay boards input to ground switches on the relay
    it will also explain why connecting the +5v to ground short circuits it
    John
    PS
    wiring diagram V2
    a possible alternative relay board connection
    with opto-isolator input circuit powered by USB motion card +5V
    PPS
    part of photo of relay board posted
    Attachment 395090
    when the jumper is fitted
    JD-VCC & VCC are connected together
    relay boards circuit diagram adapted from diagram found on line
Name:	OptoRelay x2 connection to BOB.jpg
    Attached Thumbnails Attached Thumbnails Wiring v2.jpg   OptoRelay x2 connection to BOB.jpg
  1. Relay for Plasma Touch Off
    By ny_racer_xxx in forum CNC Plasma / Oxy Fuel Cutting Machines
    Last Post: 08-13-2016, 06:48 PM
  2. Relay not starting plasma
    By 28arodma in forum CNC Plasma / Oxy Fuel Cutting Machines
    Last Post: 12-30-2014, 12:52 PM
  3. Relay for triggering plasma arc
    By GITRDUN in forum CNC Plasma / Oxy Fuel Cutting Machines
    Last Post: 04-28-2014, 05:31 PM
  4. plasma relay problems
    By stanglou in forum CNC Machine Related Electronics
    Last Post: 06-24-2006, 02:42 AM